earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Products: Operator Display
Functionalities: Hardware
Product version: 3.3, 2022, 2023, 2024
3/30/2023

Operator Display

SpaceLogic™ Operator Display is a touch-screen Human Machine Interface (HMI) for SpaceLogic controllers and servers, designed for local monitoring of building controllers in small and medium-sized buildings, as well as in large buildings with comprehensive building management systems. Operator Display is specifically designed for equipment rooms and it simplifies operations, service, and troubleshooting for System Integrators and Service Engineers, as well as for non-technical users (notably Facility Managers and Janitors).

The simplified user interface and the intuitive touch-screen navigation make it easy to operate and maintain the system. Operator Display communicates quickly over BACnet/IP open protocol with a direct connection to SpaceLogic MP or RP controllers, IP-IO modules, AS-B or AS-P servers. Only one Operator Display is required per cabinet in the equipment room, so there is no need for more displays when a controller is added (up to seven controllers). The operator can view and acknowledge alarms, edit schedules, and adjust setpoint temperatures. Authorized operators can also view and override inputs, outputs, and other virtual points.

 
action_zoom_plus_stroke HMIST6400SL

HMIST6400SL

Operator Display Bundle

Operator Display is delivered in a bundle, which includes an installation gasket, installation fasteners, screws, and a DC power supply connector. The USB transfer cable is ordered separately from Schneider Electric.

Operator Display Safety Information

This section provides safety information specific to Operator Display. Carefully read the instructions before trying to install, operate, service, or maintain the equipment.

For more information, see Operator Display Safety Information .

Operator Display LED

There is one LED on the front of Operator Display.

For more information, see Operator Display LED .

Operator Display Communication Ports

Operator Display has a status LED, a battery slot, a hook, Ethernet ports, serial interface ports, a power plug connector, and USB ports.

For more information, see Operator Display Communication Ports .

Operator Display Hardening

There are specific security hardening recommendations to follow when installing Operator Display.

For more information, see Operator Display Hardening .

Operator Display Installation

Operator Display is panel-mounted in equipment rooms using installation fasteners.

For more information, see Operator Display Installation .

Wiring

The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, BACnet/IP devices, RP controller expansion modules, and Operator Display.

For more information, see Wiring .

Operator Display Regulatory Compliance and Approvals

This section provides information on regulatory and agency compliance and approvals for the SpaceLogic Operator Display.

For more information, see Operator Display Regulatory and Agency Compliance and Approvals .

Specifications

DC input
Nominal voltage
24 VDC
Operating voltage range
+/- 20 %
Inrush current
30 A or less
Maximum power consumption
9 W
Immunity to microbreaks
5 ms
Environment
Physical environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +60 °C (-4 to +140 °F)
Humidity
10 to 90 % RH non-condensing
Pollution degree
2
Operating altitude
800 to 1,114 hPa (2,000 m (6,561 ft) or lower)
Mechanical environment
Vibration resistance
IEC/BS/EN 61131-2 compliant
  
5 to 9 Hz Single amplitude 3.5 mm (0.14 in)
  
9 to 150 Hz Fixed acceleration: 9.8 m/s 2
  
X, Y, Z directions for 10 cycles (approximately 100 minutes)
Shock resistance
IEC/BS/EN 61131-2 compliant: 147 m/s 2 , X, Y, Z directions for 3 times
Electrical environment
Electrical fast transient/burst
IEC/BS/EN 61000-4-4, 2 kV: Power port (display unit), 1 kV: Signal ports
Electrostatic discharge immunity
IEC/BS/EN 61000-4-2 Level 3, Contact discharge method: 6 kV, Air discharge method: 8 kV
Material
Enclosure
Polycarbonate (PC)
Front
Aluminum
Display
Polyethylene Terephthalate (PET)
Ingress protection rating
IP 65 (front of product that is exposed, on panel-mounted installation)
NEMA rating
NEMA 4 (front, indoor use)
  
NEMA 13 (front, in enclosure)
Plastic flame rating
UL94 V-0
Mechanical
Dimensions (W x H x D)
208 x 153 x 45 mm (8.19 x 6.02 x 1.77 in.)
See drawing below:
 
action_zoom_plus_stroke
Weight
0.8 kg (1.8 lb)
Installation
Mounted to the panel using 4 screws (included), conforming to UL 61010-1, CSA C22.2 No 61010-1, UL 61010-2-201, CSA C22.2 No 61010-2-201 (1.6 to 5 mm (0.1 to 0.2 in) thick panel), BS/EN 61131-2, and BS/EN 61000-6-2
Real-time clock
Power
Battery (CR2032)
Accuracy
+/- 20 ppm
Battery lifetime
5 years at room temperature a
Communication ports
Ethernet
Dual 10/100BASE-TX (RJ45) a
USB
1 USB 2.0 host port (type-A), 5 VDC, 2.5 W
  
1 USB 2.0 device port (micro-B)
RS-232C
1 COM1 (D-Sub, 9-pin, female) - Inactive
RS-485
1 COM2 (RJ45, female) - Inactive
Hardware
CPU type
ARM Cortex-A8 single-core
Frequency
800 MHz
Device memory (NAND Flash)
1 GB (including 180 MB for user data)
Backup memory (MRAM)
512 KB
Status indicator
LED (green, orange, and red)
  
Buzzer (not used)
Display
Display resolution
800 x 480 pixels (WVGA)
Display aspect ratio
16:10
Display size
7 inches (178 mm)
Display type
TFT LCD, touchscreen
  
Single touch analog resistive panel
Color
16 million colors
Display languages
Czech, Danish, English, Finnish, French, German, Italian, Norwegian, Polish, Portuguese, Russian, Slovak, Spanish, Swedish
Brightness control
400 cd/m 2
  
16 levels
LED lifetime a
50,000 hours
  • Operator Display Safety Information
  • Operator Display LED
  • Operator Display Communication Ports
  • Operator Display Hardening
  • Operator Display Installation
  • Wiring
  • Operator Display Regulatory and Agency Compliance and Approvals