SpaceLogic™ Operator Display is a touch-screen Human Machine Interface (HMI) for SpaceLogic controllers and servers, designed for local monitoring of building controllers in small and medium-sized buildings, as well as in large buildings with comprehensive building management systems. Operator Display is specifically designed for equipment rooms and it simplifies operations, service, and troubleshooting for System Integrators and Service Engineers, as well as for non-technical users (notably Facility Managers and Janitors).
The simplified user interface and the intuitive touch-screen navigation make it easy to operate and maintain the system. Operator Display communicates quickly over BACnet/IP open protocol with a direct connection to SpaceLogic MP or RP controllers, IP-IO modules, AS-B or AS-P servers. Only one Operator Display is required per cabinet in the equipment room, so there is no need for more displays when a controller is added (up to seven controllers). The operator can view and acknowledge alarms, edit schedules, and adjust setpoint temperatures. Authorized operators can also view and override inputs, outputs, and other virtual points.
Operator Display is delivered in a bundle, which includes an installation gasket, installation fasteners, screws, and a DC power supply connector. The USB transfer cable is ordered separately from Schneider Electric.
This section provides safety information specific to Operator Display. Carefully read the instructions before trying to install, operate, service, or maintain the equipment.
Per maggior informazioni, consulta Operator Display Safety Information .
There is one LED on the front of Operator Display.
Per maggior informazioni, consulta Operator Display LED .
Operator Display has a status LED, a battery slot, a hook, Ethernet ports, serial interface ports, a power plug connector, and USB ports.
Per maggior informazioni, consulta Operator Display Communication Ports .
There are specific security hardening recommendations to follow when installing Operator Display.
Per maggior informazioni, consulta Operator Display Hardening .
Operator Display is panel-mounted in equipment rooms using installation fasteners.
Per maggior informazioni, consulta Operator Display Installation .
The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, BACnet/IP devices, RP controller expansion modules, and Operator Display.
Per maggior informazioni, consulta Wiring .
This section provides information on regulatory and agency compliance and approvals for the SpaceLogic Operator Display.
Per maggior informazioni, consulta Operator Display Regulatory and Agency Compliance and Approvals .
DC input | |
Nominal voltage
|
24 VDC
|
Operating voltage range
|
+/- 20 %
|
Inrush current
|
30 A or less
|
Maximum power consumption
|
9 W
|
Immunity to microbreaks
|
5 ms
|
Environment | |
Physical environment | |
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
Ambient temperature, storage
|
-20 to +60 °C (-4 to +140 °F)
|
Humidity
|
10 to 90 % RH non-condensing
|
Pollution degree
|
2
|
Operating altitude
|
800 to 1,114 hPa (2,000 m (6,561 ft) or lower)
|
Mechanical environment | |
Vibration resistance
|
IEC/BS/EN 61131-2 compliant
|
5 to 9 Hz Single amplitude 3.5 mm (0.14 in)
|
|
9 to 150 Hz Fixed acceleration: 9.8 m/s
2
|
|
X, Y, Z directions for 10 cycles (approximately 100 minutes)
|
|
Shock resistance
|
IEC/BS/EN 61131-2 compliant: 147 m/s
2
, X, Y, Z directions for 3 times
|
Electrical environment | |
Electrical fast transient/burst
|
IEC/BS/EN 61000-4-4, 2 kV: Power port (display unit), 1 kV: Signal ports
|
Electrostatic discharge immunity
|
IEC/BS/EN 61000-4-2 Level 3, Contact discharge method: 6 kV, Air discharge method: 8 kV
|
Material | |
Enclosure
|
Polycarbonate (PC)
|
Front
|
Aluminum
|
Display
|
Polyethylene Terephthalate (PET)
|
Ingress protection rating
|
IP 65 (front of product that is exposed, on panel-mounted installation)
|
NEMA rating
|
NEMA 4 (front, indoor use)
|
NEMA 13 (front, in enclosure)
|
|
Plastic flame rating
|
UL94 V-0
|
Mechanical | |
Dimensions (W x H x D)
|
208 x 153 x 45 mm (8.19 x 6.02 x 1.77 in.)
|
See drawing below: | |
![]() |
|
Weight
|
0.8 kg (1.8 lb)
|
Installation
|
Mounted to the panel using 4 screws (included), conforming to UL 61010-1, CSA C22.2 No 61010-1, UL 61010-2-201, CSA C22.2 No 61010-2-201 (1.6 to 5 mm (0.1 to 0.2 in) thick panel), BS/EN 61131-2, and BS/EN 61000-6-2
|
Real-time clock | |
Power
|
Battery (CR2032)
|
Accuracy
|
+/- 20 ppm
|
Battery lifetime
|
5 years at room temperature
a
|
a) The lifetime of the battery may vary depending on different applications and environments. | |
Communication ports | |
Ethernet
|
Dual 10/100BASE-TX (RJ45)
a
|
a) Only one port is used; the second one is inactive. | |
USB
|
1 USB 2.0 host port (type-A), 5 VDC, 2.5 W
|
1 USB 2.0 device port (micro-B)
|
|
RS-232C
|
1 COM1 (D-Sub, 9-pin, female) - Inactive
|
RS-485
|
1 COM2 (RJ45, female) - Inactive
|
Hardware | |
CPU type
|
ARM Cortex-A8 single-core
|
Frequency
|
800 MHz
|
Device memory (NAND Flash)
|
1 GB (including 180 MB for user data)
|
Backup memory (MRAM)
|
512 KB
|
Status indicator
|
LED (green, orange, and red)
|
Buzzer (not used)
|
|
Display | |
Display resolution
|
800 x 480 pixels (WVGA)
|
Display aspect ratio
|
16:10
|
Display size
|
7 inches (178 mm)
|
Display type
|
TFT LCD, touchscreen
|
Single touch analog resistive panel
|
|
Color
|
16 million colors
|
Display languages
|
Czech, Danish, English, Finnish, French, German, Italian, Norwegian, Polish, Portuguese, Russian, Slovak, Spanish, Swedish
|
Brightness control
|
400 cd/m
2
|
16 levels
|
|
LED lifetime
a
|
50,000 hours
|
a) The LED lifetime is defined as the time when the LED continues to operate at the ambient temperature 25 °C +/-2 °C (77 °F +/- 3.6 °F) until the brightness is reduced to 25% of its original value. |