RP-C-16B-F-24V Screw Terminals

The RP-C-16B-F-24V model has 16 I/O points and the controller is equipped with 30 fixed screw terminals.

Pericolo Pericolo

HAZARD OF ELECTRIC SHOCK, EXPLOSION, OR ARC FLASH

Disconnect the power supply and other high voltage equipment before wiring.

Failure to follow these instructions will result in death or serious injury.

Recommended screw tightening torque: 0.56 to 0.79 Nm (5 to 7 lbf.in)

 
action_zoom_plus_stroke Screw terminals and other connectors, RP-C-16B-F-24V
Figura: Screw terminals and other connectors, RP-C-16B-F-24V

The 30 screw terminals are used as follows:

  • Three screw terminals for the power input

  • Two screw terminals for the return (RET) terminals 4 and 5

  • Six screw terminals for the four solid-state relay (SSR) outputs

  • Four screw terminals for the three relay outputs

  • Three screw terminals for the high power relay output

  • 12 screw terminals for the eight universal inputs/outputs of type Ub

Tabella: Screw Terminals, RP-C-16B-F-24V

Terminal number

Designation

Usage

Power input

1

 
action_zoom_plus_stroke
/+

G – 24 VAC, 50/60 Hz, 23 VA

Positive lead (+) when operating the device from 24-30 VDC, 14 W

2

 
action_zoom_plus_stroke
/–

G0 – Earth ground lead of 24 VAC transformer connects to terminal 2.

Terminals 2 and 3 are internally connected.

Negative (–) lead when operating the device from 24-30 VDC, 14 W

3

RET

 
action_zoom_plus_stroke

Terminal 3 is provided for convenience to connect to protective earth ground (optional).

Terminals 2 and 3 are internally connected.

Return terminals

4

RET

Internally connected to all earth ground and RET terminals

5

RET

Internally connected to all earth ground and RET terminals

Solid-state relay (SSR) outputs

6

DO1

SSR output

7

COM1

Common connection for DO1 and DO2

The COM terminal can be connected to 0 to 24 VAC or -30 VDC to +30 VDC.

8

DO2

SSR output

9

DO3

SSR output

10

COM2

Common connection for DO3 and DO4

The COM terminal can be connected to 0 to 24 VAC or -30 VDC to +30 VDC.

11

DO4

SSR output

Relay outputs

12

COM3

Common connection for DO1, DO2, and DO3

13

DO1

Relay output, type Form A

14

DO2

Relay output, type Form A

15

DO3

Relay output, type Form A

High power relay outputs

16

NC

Normally Closed terminal. High power relay output, type Form C.

17

DO4

Common terminal. High power relay output, type Form C.

18

NO

Normally Open terminal. High power relay output, type Form C.

Universal inputs/outputs

19

Ub1

Universal input/output, type Ub

20

RET

Internally connected to all earth ground and RET terminals

21

Ub2

Universal input/output, type Ub

22

Ub3

Universal input/output, type Ub

23

RET

Internally connected to all earth ground and RET terminals

24

Ub4

Universal input/output, type Ub

25

Ub5

Universal input/output, type Ub

26

RET

Internally connected to all earth ground and RET terminals

27

Ub6

Universal input/output, type Ub

28

Ub7

Universal input/output, type Ub

29

RET

Internally connected to all earth ground and RET terminals

30

Ub8

Universal input/output, type Ub