earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Products: AS-B, MP-C, MP-V, AS-P, RP-C, RP-V
Functionalities: BACnet/IP devices
Product version: 2022
11/27/2023

MS/TP DIP Switches

You must configure the DIP switches as part of the commissioning process for RP controllers that support MS/TP communications.

For more information, see BACnet MS/TP Network Communications .

Tip:

Use only switches 1-7. Switch 8 in unused.

See the table and graphic that follows for more information on the switches and their ON values.

Table: DIP Switch ON Values

Switch

ON value

1

1

2

2

3

4

4

8

5

16

6

32

7

64

 
action_zoom_plus_stroke Address DIP switches
Figure: Address DIP switches

For example, to configure address 6, configure DIP switches 2 and 3 to ON and switches 1, 4, 5, 6 and 7 to OFF.

For more information, see Configuring the MS/TP Address .

  • BACnet MS/TP Network Communications
  • Configuring the MS/TP Address