earth_america
user_standard Iniciar sesión
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concepto

Concepto


Productos AS-B, MP-C, MP-V, AS-P, RP-C, RP-IO , RP-V
Funcionalidades: Dispositivos SmartX IP Controller
Versión del producto: 2023, 2024, 7.0
27/11/2023

MS/TP DIP Switches

You must configure the DIP switches as part of the commissioning process for the RP and MP controllers and RP-IO modules that only support MS/TP communications.

Para obtener más información, consulte BACnet MS/TP Network Communications .

Para obtener más información, consulte EasyLogic RP-IO .

Aviso

Use only switches 1-7. Switch 8 is unused.

See the table and graphic that follows for more information on the switches and their ON values.

Tabla: DIP Switch ON Values

Switch

ON value

1

1

2

2

3

4

4

8

5

16

6

32

7

64

 
action_zoom_plus_stroke Address DIP switches
Figura: Address DIP switches

For example, to configure address 6, configure DIP switches 2 and 3 to ON and switches 1, 4, 5, 6 and 7 to OFF.

Para obtener más información, consulte Configuring the MS/TP Address .

  • EasyLogic RP-IO
  • BACnet MS/TP Network Communications
  • Configuring the MS/TP Address