earth_america
user_standard Iniciar sesión
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Explicación de procesos

Explicación de procesos


Productos AS-B, MP-C, MP-V, AS-P, RP-C, RP-IO , RP-V
Funcionalidades: Dispositivos SmartX IP Controller
Versión del producto: 2023, 2024, 7.0
24/03/2023

Configuring the MS/TP Address

You must configure a unique MS/TP address for the RP and MP controllers and RP-IO modules that only support MS/TP communications. You do so during installation by using position 1-7 on the address DIP switch.

Aviso

MAC address 0 is a valid address for MP or RP controllers. You cannot use this address, however, if another device on the bus uses address 0.

In many installations, the automation server uses address 0. If this is the case, be sure to avoid using the address when configuring MS/TP communications in MP and RP controllers.

Mostrar más
action_close

You must configure the DIP switches as part of the commissioning process for the RP and MP controllers and RP-IO modules that only support MS/TP communications.

Para obtener más información, consulte BACnet MS/TP Network Communications .

Para obtener más información, consulte EasyLogic RP-IO .

Aviso

Use only switches 1-7. Switch 8 is unused.

See the table and graphic that follows for more information on the switches and their ON values.

Tabla: DIP Switch ON Values

Switch

ON value

1

1

2

2

3

4

4

8

5

16

6

32

7

64

 
action_zoom_plus_stroke Address DIP switches
Figura: Address DIP switches

For example, to configure address 6, configure DIP switches 2 and 3 to ON and switches 1, 4, 5, 6 and 7 to OFF.

Para obtener más información, consulte Configuring the MS/TP Address .

Configuring the MS/TP address
  1. In the RP or MP controller or RP-IO module, locate the address DIP switch.

  2. Use position 1-7 to configure the address.

    Position 1-7 represent the binary values 1, 2, 4, 8, 16, 32, and 64.

    Aviso

    Position 8 is not valid.

  3. Activate the switch at the numbered position by moving the switch down (ON) and then deactivate it by moving the switch up (OFF).

  • MS/TP DIP Switches
  • EasyLogic RP-IO