Configuring the MS/TP Address

You must configure a unique MS/TP address for the RP controllers that support MS/TP communications. You do so during installation by using position 1-7 on the address DIP switch.

Uwaga

MAC address 0 is a valid address for MP or RP controllers. You cannot use this address, however, if another device on the bus uses address 0.

In many installations, the automation server uses address 0. If this is the case, be sure to avoid using the address when configuring MS/TP communications in MP and RP controllers.

Pokaż więcej
action_close

You must configure the DIP switches as part of the commissioning process for RP controllers that support MS/TP communications.

Więcej informacji zawiera BACnet MS/TP Network Communications .

Uwaga

Use only switches 1-7. Switch 8 in unused.

See the table and graphic that follows for more information on the switches and their ON values.

Tabela: DIP Switch ON Values

Switch

ON value

1

1

2

2

3

4

4

8

5

16

6

32

7

64

 
action_zoom_plus_stroke Address DIP switches
Rysunek: Address DIP switches

For example, to configure address 6, configure DIP switches 2 and 3 to ON and switches 1, 4, 5, 6 and 7 to OFF.

Więcej informacji zawiera Configuring the MS/TP Address .

Configuring the MS/TP address
  1. In the RP or MP controller, locate the address DIP switch.

  2. Use position 1-7 to configure the address.

    Position 1-7 represent the binary values 1, 2, 4, 8, 16, 32, and 64.

    Uwaga

    Position 8 is not valid.

  3. Activate the switch at the numbered position by moving the switch down (ON) and then deactivate it by moving the switch up (OFF).