The RP-V-5C-M model has five I/O points and the controller is equipped with 11 fixed screw terminals and a 3-position removable screw terminal block.
Recommended screw tightening torque for fixed screw terminal blocks: 0.56 to 0.79 Nm (5 to 7 lbf.in)
Recommended screw tightening torque for removable screw terminal block : 0.5 Nm (4.5 lbf.in)
The 11 fixed screw terminals are used as follows:
Two screw terminals for the power input
One screw terminal for earth ground input
Four screw terminals for the two universal inputs/outputs of type Ub
Four screw terminals for the three solid-state relay (SSR) outputs
The 3-position removable screw terminal block is used for connection to the BACnet MS/TP (RS-485) network.
|
Terminal number |
Designation |
Usage |
|
Power input |
|
|
|
1 |
L |
Line (L) lead, 24 VAC, 50/60 Hz, 11 VA |
|
2 |
N |
Neutral (N) lead, 24 VAC, 50/60 Hz, 11 VA |
|
3 |
|
Earth ground Internally connected to signal ground and all RET terminals |
|
Universal inputs/outputs |
|
|
|
4 |
Ub1 |
Universal input/output, type Ub |
|
5 |
RET |
Internally connected to all earth ground and RET terminals |
|
6 |
Ub2 |
Universal input/output, type Ub |
|
7 |
RET |
Internally connected to all earth ground and RET terminals |
|
Solid-state relay (SSR) outputs |
|
|
|
8 |
COM |
Common connection for DO1, DO2, and DO3 The COM terminal can be connected to 0 to 24 VAC or -30 VDC to +30 VDC. |
|
9 |
DO1 |
SSR output |
|
10 |
DO2 |
SSR output |
|
11 |
DO3 |
SSR output |
|
RS-485 terminals |
|
|
|
12 |
Shield |
Convenience terminal to interconnect two shield drain wires (incoming and outgoing). There is no electrical connection in the device. The shield should be connected to ground at only one location and that is recommended to be at the automation server. The shield should not be connected directly to the RET terminal on the automation server. The transient energy on the drain wire should be conducted to ground and not through the automation server. |
|
13 |
RS-485– |
Connection to TX/RX– (RS-485–) signal in the BACnet MS/TP (RS-485) network. |
|
14 |
RS-485+ |
Connection to TX/RX+ (RS-485+) signal in the BACnet MS/TP (RS-485) network. |