The RP-IO-16E-M-24V model has 16 I/O points and the controller is equipped with 30 fixed screw terminals and a 3-position removable screw terminal block.
Recommended screw tightening torque: 0.56 to 0.79 Nm (5 to 7 lbf.in)
The 30 fixed screw terminals are used as follows:
Two screw terminals for the power input
One screw terminal for ground input
Two screw terminals for the return (RET) terminals 4 and 5
25 screw terminals for the eight universal inputs/outputs of type Ub
The 3-position removable screw terminal block is used for connection to the BACnet MS/TP (RS-485) network.
Terminal number |
Designation |
Usage |
Power input |
|
|
1 |
|
24 VAC, 50/60 Hz, 7 VA Positive lead (+) when operating the device from 24-30 VDC, 3 W |
2 |
|
The other output from the 24 VAC transformer connects to terminal 2. Negative (–) lead when operating the device from 24-30 VDC, 3 W |
3 |
RET |
Terminal 3 is provided for convenience to connect to protective earth ground. |
Return terminals |
|
|
4 |
RET |
Internally connected to all earth ground and RET terminals |
5 |
RET |
Internally connected to all earth ground and RET terminals |
RS-485 terminals |
|
|
6 |
RS-485+ |
Connection to TX/RX+ (RS-485+) signal in the BACnet MS/TP (RS-485) network. |
7 |
RS-485– |
Connection to TX/RX– (RS-485–) signal in the BACnet MS/TP (RS-485) network. |
8 |
SHIELD |
Convenience terminal to interconnect two shield drain wires (incoming and outgoing). There is no electrical connection in the device. The shield should be connected to ground at only one location and that is recommended to be at the automation server. The shield should not be connected directly to the RET terminal on the automation server. The transient energy on the drain wire should be conducted to ground and not through the automation server. |
Universal inputs/outputs |
|
|
9 |
Ub9 |
Universal input/output, type Ub |
10 |
RET |
Internally connected to all earth ground and RET terminals2 |
11 |
Ub10 |
Universal input/output, type Ub |
12 |
Ub11 |
Universal input/output, type Ub |
13 |
RET |
Internally connected to all earth ground and RET terminals |
14 |
Ub12 |
Universal input/output, type Ub |
15 |
Ub13 |
Universal input/output, type Ub |
16 |
RET |
Internally connected to all earth ground and RET terminals |
17 |
Ub14 |
Universal input/output, type Ub |
18 |
RET |
Internally connected to all earth ground and RET terminals |
19 |
Ub15 |
Universal input/output, type Ub |
20 |
RET |
Internally connected to all earth ground and RET terminals |
21 |
Ub16 |
Universal input/output, type Ub |
Universal inputs/outputs |
|
|
22 |
Ub1 |
Universal input/output, type Ub |
23 |
RET |
Internally connected to all earth ground and RET terminals |
24 |
Ub2 |
Universal input/output, type Ub |
25 |
Ub3 |
Universal input/output, type Ub |
26 |
RET |
Internally connected to all earth ground and RET terminals |
27 |
Ub4 |
Universal input/output, type Ub |
28 |
Ub5 |
Universal input/output, type Ub |
29 |
RET |
Internally connected to all earth ground and RET terminals |
30 |
Ub6 |
Universal input/output, type Ub |
31 |
Ub7 |
Universal input/output, type Ub |
32 |
RET |
Internally connected to all earth ground and RET terminals |
33 |
Ub8 |
Universal input/output, type Ub |