The RP-IO module provides I/O expansion to your HVAC application over BACnet MS/TP. The I/O module can share its I/O resources across applications running in automation servers, RP and MP controllers, or third-party systems. With the support of local alarms and local trend logs, the I/O module avoids unnecessary traffic over the network while being able to log important information locally. The I/O module can be installed near facilities in the field, away from the automation server or the RP or MP controller.
The RP-IO module is an I/O module that allows for flexible control solutions due to the versatile mix of universal inputs/outputs and solid-state relay (SSR) outputs.
When RP-IO modules are part of an EcoStruxure BMS, you can take full advantage of the existing EcoStruxure Building Operation engineering tools.
The RP-IO module is available in two models that only support BACnet MS/TP communication. These two models offer two different combinations (sets) of the number and types of I/O points. Both models support 24 VAC/VDC input power.
For more information, see RP-IO Models .
The RP-IO module models provide 12 or 16 I/O points, consisting of two different sets of I/O point types. The versatile mix of I/O point types match a wide variety of applications. The universal inputs/outputs are highly flexible and can be configured as either inputs or outputs.
For more information, see RP-IO Onboard I/O .
The RP-IO module has a built-in power supply designed to accommodate a nominal operating voltage of 24 VAC at 50/60 Hz or 24 to 30 VDC input power.
For more information, see RP-IO Module Built-in Power Supply .
RP and MP controllers and I/O modules are devices that have three types of memory:
Flash memory: for boot loader, operating system, application software, and configuration storage
RAM: for runtime operation
FRAM non-volatile memory: for data retention in the case of power outage
For more information, see Memory in RP and MP Controllers and I/O Modules .
One of the cornerstones of the EcoStruxure BMS is support for open standards. As a result, the RP-IO module complies with the BACnet open standard, one of the most popular standards for buildings.
For more information, see RP-IO Module Supported Building Standards .
The RP-IO module provides the following communication port:
One RS-485 port with terminal block
For more information, see RP-IO Module Communication Port .
The RP-IO modules are designed for connection to a BACnet MS/TP (RS-485) network and can only communicate with automation servers using the BACnet MS/TP protocol.
For more information, see RP-IO BACnet MS/TP Support .
You must configure the DIP switches as part of the commissioning process for the RP and MP controllers and RP-IO modules that only support MS/TP communications.
For more information, see MS/TP DIP Switches .
The RP-IO module has fixed screw terminals for the power input, SSR outputs, and universal inputs/outputs and a removable screw terminal block for connection to the BACnet MS/TP (RS-485) network.
For more information, see RP-IO Screw Terminals .
There is one LED on the front panel of the RP-IO module.
For more information, see RP-IO Module LED .
You can reset and restart the RP-IO module in different ways depending on how long you press the reset button. The resets and restarts can affect the retention of values after restart based on the retain levels configured for the variables.
For more information, see IP-IO and RP-IO Module Reset Modes .
The RP-IO module can be installed on a DIN rail or other flat surface inside a cabinet. The device is recommended to be installed in a cabinet, unless local regulations allow an exception.
For more information, see RP-IO Module Device Installation .
The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, RP and MP controllers, IP-IO and RP-IO modules, RP controller expansion modules, and Operator Display.
For more information, see Wiring .
Using WorkStation, you can update the firmware of multiple RP-IO IO modules at the same time with minimum downtime. In particular, the universal upgrade package simplifies the update process and requires minimal user involvement and coordination.
For more information, see RP-IO Module Firmware Management .
This section provides information on regulatory compliance and approvals for the RP-IO modules.
For more information, see RP-IO Module Regulatory Compliance and Approvals .
| AC input | |
Nominal voltage
|
24 VAC
|
Operating voltage range
|
+/-15 %
|
Frequency
|
50/60 Hz
|
Maximum power consumption
|
7 VA
|
Power input protection
|
MOV suppression and internal fuse
|
| DC input | |
Nominal voltage
|
24 to 30 VDC
|
Operating voltage range
|
21 to 33 VDC
|
Maximum power consumption
|
3 W
|
Power input protection
|
MOV suppression and internal fuse
|
| Environment | |
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
Ambient temperature, storage
|
-40 to +70 °C (-40 to +158 °F)
|
Maximum humidity
|
95 % RH non-condensing
|
| Material | |
Plastic flame rating
|
UL94 V-0
|
Ingress protection rating
|
IP 20
|
Plenum rating
|
UL 2043
|
| Mechanical | |
Dimensions
|
180 W x 110 H x 64 D mm (7.1 W x 4.3 H x 2.5 D in.)
|
|
|
Weight, RP-IO-12A-M-24V
|
0.336 kg (0.741 lb)
|
Weight, RP-IO-16E-M-24V
|
0.334 kg (0.736 lb)
|
Recommended installation
|
DIN rail or flat surface in a cabinet
a
|
| a) It is recommended to install the device in an enclosure (cabinet), unless local regulations allow an exception. | |
Terminal blocks
|
Power and I/O: Fixed
|
BACnet MS/TP communications: Removable
|
|
| Optional covers | |
Dimensions
|
181 W x 164 H x 64 D mm (7.1 W x 6.5 H x 2.5 D in.)
|
|
|
Weight, optional covers
|
0.070 kg (0.154 lb)
|
| Communication ports | |
RS-485 port
|
RS-485 (3-pole screw terminal block)
|
Transient voltage suppressors on communication signals
|
|
| RS-485 transceiver characteristics | |
| All device models | |
Transceiver type
|
Failsafe
|
Non-isolated
|
|
External biasing
|
None required
|
Total Unit Load (UL) per device
|
Maximum 0.5 UL
|
| Communications | |
BACnet
|
BACnet MS/TP, maximum bus length: 1200 m (4000 ft), maximum baud rate: 76800
|
BTL B-ASC (BACnet Application Specific Controller)
a
|
|
| a) See the BTL Product Catalog for up-to-date details on BTL listed firmware revisions on BACnet International's home page. | |
| CPU | |
Frequency
|
500 MHz
|
Type
|
ARM Cortex-A7 single-core
|
Internal SRAM
|
6 MB
|
NOR flash memory
|
32 MB
|
Memory backup
|
128 kB
a
, FRAM, non-volatile
|
| a) RP-IO-12A-M-24V with hardware version earlier than 01 and RP-IO-16E-M-24V with hardware version earlier than 03 have a FRAM memory with a size of 8 kB. For these hardware versions, the use of Script programs is recommended to save FRAM memory space. | |