The MP-C-24A-M model has 24 I/O points and the controller is equipped with 41 fixed screw terminals and a 3-position removable screw terminal block.
Recommended screw tightening torque: 0.56 Nm (5 lbf.in)
The 41 fixed screw terminals are used as follows:
Three screw terminals for the power input
Eight screw terminals for the four relay outputs
30 screw terminals for the 20 universal inputs/outputs of type Ub
The 3-position removable screw terminal block is used for connection to the BACnet MS/TP (RS-485) network.
Terminal number |
Designation |
Usage |
Power input |
|
|
1 |
24 VAC/DC |
24 VAC, 50/60 Hz, 10 VA Positive lead (+) when operating the device from 24-30 VDC, 5 W |
2 |
![]() |
Earth ground lead of 24 VAC transformer connects to terminals 2 or 3. Terminals 2 and 3 are internally connected. Negative (–) lead when operating the device from 24-30 VDC, 5 W |
3 |
![]() |
Terminal 3 is provided for convenience to connect to protective earth ground (optional). Terminals 2 and 3 are internally connected. |
RS-485 terminals |
|
|
4 |
RS-485+ |
Connection to TX/RX+ (RS-485+) signal in the BACnet MS/TP (RS-485) network. |
5 |
RS-485– |
Connection to TX/RX– (RS-485–) signal in the BACnet MS/TP (RS-485) network. |
6 |
SHIELD |
Convenience terminal to interconnect two shield drain wires (incoming and outgoing). There is no electrical connection in the device. The shield should be connected to ground at only one location and that is recommended to be at the automation server. The shield should not be connected directly to the RET terminal on the automation server. The transient energy on the drain wire should be conducted to ground and not through the automation server. |
Universal inputs/outputs |
|
|
7 |
Ub17 |
Universal input/output, type Ub |
8 |
RET |
Internally connected to all earth ground and RET terminals |
9 |
Ub18 |
Universal input/output, type Ub |
10 |
Ub19 |
Universal input/output, type Ub |
11 |
RET |
Internally connected to all earth ground and RET terminals |
12 |
Ub20 |
Universal input/output, type Ub |
Relay outputs |
|
|
19 |
DO1 |
Relay output, type Form A |
20 |
DO1 |
Relay output, type Form A |
21 |
DO2 |
Relay output, type Form A |
22 |
DO2 |
Relay output, type Form A |
23 |
DO3 |
Relay output, type Form A |
24 |
DO3 |
Relay output, type Form A |
25 |
DO4 |
Relay output, type Form A |
26 |
DO4 |
Relay output, type Form A |
Universal inputs/outputs |
|
|
35 |
Ub1 |
Universal input/output, type Ub |
36 |
RET |
Internally connected to all earth ground and RET terminals |
37 |
Ub2 |
Universal input/output, type Ub |
38 |
Ub3 |
Universal input/output, type Ub |
39 |
RET |
Internally connected to all earth ground and RET terminals |
40 |
Ub4 |
Universal input/output, type Ub |
41 |
Ub5 |
Universal input/output, type Ub |
42 |
RET |
Internally connected to all earth ground and RET terminals |
43 |
Ub6 |
Universal input/output, type Ub |
44 |
Ub7 |
Universal input/output, type Ub |
45 |
RET |
Internally connected to all earth ground and RET terminals |
46 |
Ub8 |
Universal input/output, type Ub |
47 |
Ub9 |
Universal input/output, type Ub |
48 |
RET |
Internally connected to all earth ground and RET terminals |
49 |
Ub10 |
Universal input/output, type Ub |
50 |
Ub11 |
Universal input/output, type Ub |
51 |
RET |
Internally connected to all earth ground and RET terminals |
52 |
Ub12 |
Universal input/output, type Ub |
53 |
Ub13 |
Universal input/output, type Ub |
54 |
RET |
Internally connected to all earth ground and RET terminals |
55 |
Ub14 |
Universal input/output, type Ub |
56 |
Ub15 |
Universal input/output, type Ub |
57 |
RET |
Internally connected to all earth ground and RET terminals |
58 |
Ub16 |
Universal input/output, type Ub |