earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Products: MP-C
Functionalities: Hardware
Product version: 2023, 2024, 7.0
6/20/2023

MP-C BACnet MS/TP Support

The support for BACnet MS/TP communication differs between the MP-C controller models. Only MP-C models with “-M” in the product name support BACnet MS/TP. These MP-C models are designed for connection to a BACnet MS/TP (RS-485) network and can only communicate with automation servers using the BACnet MS/TP protocol.

This category of MP-C controllers (with “-M” in the product name) consists of the following models:

  • MP-C-24A-M and MP-C-36A-M

Note:

The MP-C models without “-M” in the product name are designed for connection to an IP network and can only communicate with automation servers using the BACnet/IP protocol.

For more information, see MP-C Models .

The MP-C controllers with “-M” in the product name have an RS-485 port with a 3-pole removable screw terminal block that is used for connection to the BACnet MS/TP (RS-485) network and MS/TP communication with the automation server (AS-P or AS-B). Connecting to an IP network is not supported as these MP-C controllers do not have Ethernet ports. For more information, see Communication Ports on MP-C-24A-M and -36A-M .

You need to configure a unique MS/TP address for the device during installation using the address DIP switches on the device. For more information, see MS/TP DIP Switches .

As part of the commissioning process for the device, you also need to configure the baud rate for the automation server BACnet MS/TP (RS-485) bus. For more information, see MS/TP Communications Baud Rate .

 
action_zoom_plus_stroke Location of the RS-485 screw terminal block on the MP-C controllers with “-M” in the product name
Figure: Location of the RS-485 screw terminal block on the MP-C controllers with “-M” in the product name
Automation Server BACnet MS/TP (RS-485) Network with b3 BACnet devices

The MP-C controllers can be mixed with b3 BACnet devices on the BACnet MS/TP (RS-485) network. For more information, see RS-485 Communications .

Note:

The MP-C controller models with “-M” in the product name are not isolated and connection of the controllers to a network comprised of isolated RS-485 interfaces is not recommended. The RS-485 application guidelines provide additional details. For more information, see RS-485 Communications .

A mix of up to 50 devices per RS-485 Com port can be connected to an automation server.

 
action_zoom_plus_stroke Examples of automation server BACnet MS/TP (RS-485) networks mixing MP-C controllers (models with “-M” in the product name) with b3 BACnet devices
Figure: Examples of automation server BACnet MS/TP (RS-485) networks mixing MP-C controllers (models with “-M” in the product name) with b3 BACnet devices
  • Hardware Overview
  • MP-C Controllers
  • MP-C Models
  • RS-485 Communications
  • Wiring
  • Communication Ports on MP-C-24A-M and -36A-M
  • MS/TP Communications Baud Rate
  • BACnet MS/TP Network Communications
  • Configuring MS/TP Network Settings
  • MS/TP DIP Switches
  • Configuring the MS/TP Address