This section provides recommendations on wire sizes and lengths for the AS-B servers.
For more information, see AS-B Servers .
The recommendations are for guidance only. Other wire sizes and lengths may be used, depending on wiring rules and when appropriate.
| Terminals | Minimum Cross-sectional Area | Maximum Cable Length | 
| Power input terminals (1, 2) | 0.75 mm² (18 AWG) a | According to local wiring rules | 
| Earth ground terminal (3) | 0.75 mm² (18 AWG) a | According to local wiring rules | 
| Return (RET) terminals (4, 5), connected to ground rail | 1.3 mm² (16 AWG) | As short as possible within the same panel, maximum 1.5 m (4.8 ft). | 
| RS-485 terminals (6, 7, 8, 9) | For more information, see RS-485 Communications . | For more information, see RS-485 Communications . | 
| Digital inputs and universal inputs/outputs as digital b inputs | 0.34 mm² (22 AWG) | 200 m (650 ft) | 
| Universal inputs/outputs as analog c inputs | 0.34 mm² (22 AWG) | 100 m (330 ft) | 
| Universal inputs/outputs as temperature (thermistor) inputs, up to 75 °C (167 °F) | 0.75 mm² (18 AWG) | 75 m (250 ft) | 
| Universal inputs/outputs as temperature (thermistor) inputs, up to 75 °C (167 °F) | 1.5 mm² (15 AWG) | 150 m (500 ft) | 
| Universal inputs/outputs as temperature (thermistor) inputs, up to 150 °C (302 °F) | 1.5 mm² (15 AWG) | 75 m (250 ft) | 
| Universal inputs/outputs, for actuators and transmitters powered from the same transformer as the AS-B sever | 0.75 mm² (18 AWG) | 20 m (65 ft) | 
| Universal inputs/outputs, for actuators and transmitters powered from their own transformer (external or internal) | 0.34 mm² (22 AWG) | 200 m (650 ft) | 
| Universal inputs/outputs as voltage outputs, for actuators powered from their own transformer (external or internal) or when the outputs have isolated converters | 0.34 mm² (22 AWG) | 200 m (650 ft) | 
| Relay outputs | According to local wiring rules d | According to local wiring rules d | 
| Triac outputs | 0.5 mm² (20 AWG) d | According to local wiring rules d |