User Interface

User Interface


Products: AS-B, Enterprise Central, Enterprise Server, AS-P, Virtual Project Servers
Functionalities: Alarms
Product version: 3.2, 3.3, 2022
10/15/2020

Create Change of State Alarm Wizard – Alarm Trigger Page

Use the Alarm Trigger page to configure the trigger settings of the change of state alarm.

 
action_zoom_plus_stroke Change of state alarm trigger page
Figure: Change of state alarm trigger page

Table: Change of State Alarm Trigger Page

Component

Description

True

Select to trigger the alarm when the monitored variable is equal to true.

False

Select to trigger the alarm when the monitored variable is equal to false.

Monitored variable

​Enter the path to the variable that is monitored by the alarm.

Disable alarm

Select to disable the alarm, for example, before deployment.

Alarm delay

​Enter the time, in seconds, the alarm has to be within the reset criteria before the alarm state is changed from alarm to reset.

Reset delay

​Enter the time, in seconds, the alarm has to be within the alarm criteria before the alarm is triggered.

Shunt variable 1

​Enter the shunt variable that is used to enable or disable the alarm. For more information, see Shunt Variables .

Invert

Select to invert the shunt value, that is, enable the alarm when the shunt value is active and disable the alarm when the shunt value is inactive. For more information, see Shunt Variables .

Operator

Select AND or OR to add logic between the first and the second shunt variable. For more information, see Shunt Variables .

Shunt variable 2

​Enter the second shunt variable that is used to enable or disable the alarm. For more information, see Shunt Variables .

Invert

Select to invert the shunt value, that is, enable the alarm when the shunt value is active and disable the alarm when the shunt value is inactive. For more information, see Shunt Variables .