earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
How to

How to


Products: Automation Server, AS-B, Enterprise Server, AS-P, Virtual Project Servers
Functionalities: Trends
Product version: 1.9
5/4/2017

Configuring a Change of Value Trend Log

You configure the properties of a change of value trend log to meet the unique needs of your site.

Show More
action_close

​The change of value trend log records the variable each time the difference between the current value and the last log value exceeds the delta. Use the change of value trend log to, for example, record a variable that has an unequal oscillation.

Note:
  • The change of value trend log is limited to 10 records per second.

  • Do not set the delta too small since this can quickly fill up the trend log.

For example, in the figure below, the change of value trend log records a variable every time the variable exceeds or falls below the delta of 3. The records are printed in a trend chart. Notice that the change of value trend log records the values without any time perspective between the records.

 
action_zoom_plus_stroke Change of value trend log schematic.
Figure: Change of value trend log schematic.

The change of value trend log, which is not a variable triggered trend log, has the function to start log records according to a given start condition. For more information, see Trend Log Activation .

You can configure the maximum log interval in a change of value trend log. The maximum log interval is the maximum time that can elapse between two recordings regardless of whether the value has changed or not. The maximum log interval is calculated from the last actual recording. When the maximum log interval is configured, it bypasses the delta and the recording is triggered when the configured time period has elapsed.

To configure a change of value trend log
  1. In WorkStation, in the System Tree pane, click the change of value trend log you want to configure.

     
    action_zoom_plus_stroke
  2. Edit the properties:

    Table: Change of Value Trend Log Properties - Basic Tab

    Property

    Description

    Status

    Displays the status of the trend log.

    Enabled

    Displays True if the trend log is enabled.

    Logged variable

    Enter the variable that you want to log.

    Delta

    Select the minimum value change that triggers a new record.

    Activation variable

    Enter the variable that makes the trend log start recording values when the variable is True .

    For more information, see Trend Log Activation .

    Activation time

    Specify the time when the trend log is to start recording values.

    For more information, see Trend Log Activation .

    Maximum log interval

    Select the maximum time that can pass between two recordings regardless if the delta value has been exceeded or not.

    Log size

    Select the number of records to store before old records are overwritten, including internal records generated by the trend log.

    For more information, see Log Record Storage .

    Clear when enabled

    Select True to clear the trend log when it is enabled.

  3. Click the Save button

     
    action_zoom_plus_stroke
    .

  • Change of Value Trend Logs
  • Change of Value Trend Log Properties
  • Configure Dialog Box – Configuration Tab
  • Trend Log Activation
  • Configure Dialog Box – Operation Tab
  • Log Record Storage
  • Trend Log Does Not Start Record Due to the Start Condition
  • Missing Trend Log Records