How to


Products: AO-8, AO-V-8, DI-16, DO-FA-12, DO-FC-8, AS-P, PS-24V, RTD-DI-16, UI-16, UI-16 v2, UI-8/AO-4, UI-8/AO-4 v2, UI-8/AO-V-4, UI-8/AO-V-4 v2, UI-8/DO-FC-4, UI-8/DO-FC-4 v2
Functionalities: Hardware
Product version: 3.2, 3.3, 2022, 2023, 2024
6/24/2026

Connecting Terminal Bases

You connect terminal bases together to provide continuity of the power supply and the address bus.

Show More
action_close

The SpaceLogic devices with the two-piece design are designed for installation on DIN rails in a cabinet.

Consider a simple example:

 
action_zoom_plus_stroke SpaceLogic devices: a power supply, an automation server, and two Central IO modules
Figure: SpaceLogic devices: a power supply, an automation server, and two Central IO modules

Two-piece design

Each device consists of two parts:

  • Terminal base

  • Electronics module

 
action_zoom_plus_stroke A hardware device: the electronics module and the terminal base
Figure: A hardware device: the electronics module and the terminal base

A separate terminal base means the terminal base can be installed and wired before the electronics module with the application program and data is supplied.

The electronics module is easily plugged in to the terminal base and firmly locked by pushing the handles in place.

Replacing an electronics module is done in seconds because no terminal wiring is affected.

Installation orientation restrictions

Notice

REDUCED LIFE SPAN OF ELECTRONICS MODULE

Follow the installation orientation restrictions that apply to the device.

Failure to follow these instructions can result in reduced life span of the electronics module.

The terminal base must be installed horizontally with the backplane board device label text in the upright position reading left to right. Any other installation orientations may exceed the electronics module's thermal specifications, which can reduce the life span of the electronics module.

 
action_zoom_plus_stroke Installation orientation restrictions
Figure: Installation orientation restrictions

Installation on a DIN rail

Notice

REDUCED LIFE SPAN OF ELECTRONICS MODULE

Always install the terminal base on a horizontal DIN rail to provide sufficient cooling air flow through the electronics module.

Failure to follow these instructions can result in reduced life span of the electronics module.

A DIN rail is a common and convenient technique for installing a SpaceLogic device along with other associated control and monitoring devices. The most efficient ventilation is achieved with the wall-mounted DIN rail oriented horizontally and with adequate space provided between the SpaceLogic device rail and adjacent rails or other panel-mounted devices.

The terminal base must be installed on a horizontal DIN rail (going from left to right), with the device label text and the text “UP” (indicated by an arrow) in the upright position reading left to right.

Installing the terminal base on a horizontal DIN rail provides sufficient cooling air flow through the electronics module. Installing the terminal base on a vertical DIN rail can reduce the life span of the electronics module.

 
action_zoom_plus_stroke Installing a terminal base on a horizontal DIN rail
Figure: Installing a terminal base on a horizontal DIN rail

The terminal base is recommended to be installed on a DIN rail, but it can also be mounted directly on the wall.

DIN rail end clip

To prevent the modules from sliding sideways on the DIN rail, fix an end clamp for DIN 35 (part number SXWDINEND10001) tightly against the rightmost device on the rail. The end clamp is easily removed if you bend the snap lock open with a screwdriver.

 
action_zoom_plus_stroke End clamp for DIN 35 fixed across the DIN rail
Figure: End clamp for DIN 35 fixed across the DIN rail

Installation in a cabinet

Install the terminal bases horizontally in the cabinet with ample space between the DIN rails and devices for sufficient cooling air flow through the electronics modules.

 
action_zoom_plus_stroke Power supply, automation server, and terminal bases for Central IO modules installed on horizontal DIN rails in a cabinet
Figure: Power supply, automation server, and terminal bases for Central IO modules installed on horizontal DIN rails in a cabinet

Installation of electronics modules on terminal bases

Warning Warning

HAZARD OF ELECTRIC SHOCK OR EQUIPMENT DAMAGE

Install only the module type that is indicated on the label on the terminal base backplane.

Failure to follow these instructions can result in death, serious injury, or equipment damage.

To ensure that the correct electronics module is used with the correct terminal base, you must always check that the warning label on the terminal base backplane indicates which module type is to be connected. Write the intended module type, if it is not already printed, on the label.

 
action_zoom_plus_stroke Terminal base with label for intended module type
Figure: Terminal base with label for intended module type

Install only the module type that is indicated on the label on the terminal base backplane. A mismatch can cause electric shock and damage the electronics module.

If the label does not indicate the intended module type, consult the control panel documentation to determine the intended module type.

The electronics module is easily plugged in to the terminal base and firmly locked by pushing the handles in place.

 
action_zoom_plus_stroke Installing an electronics module on a terminal base
Figure: Installing an electronics module on a terminal base

Connection of the next terminal base on the I/O bus

The terminal bases are connected to each other by sliding the terminal bases together using the built-in connectors.

 
action_zoom_plus_stroke Connecting terminal bases
Figure: Connecting terminal bases
S-cables

The chain of devices can be split on multiple DIN rails (rows) by using an extension cord called S-cable. Maximum five S-cables are allowed per system. The S-cable connects the last (rightmost) device on one DIN rail with the first (leftmost) device on the next DIN rail.

The complete chain of devices must remain within one cabinet for EMC reasons. When the I/O bus size or quantity of I/O modules exceeds the capacity of a single cabinet, you can extend the I/O bus using an S-cable to a second, adjacent cabinet. Both cabinets must be securely fastened together and electrically connected to function as a single unit. This ensures continuous electromagnetic compatibility (EMC) protection, equivalent to that of a single cabinet. Mechanical bonding involves securely fastening the cabinets together, while electrical bonding ensures a common grounding and shielding system, minimizing electromagnetic interference and maintaining signal integrity.

The following figure shows an example of how you can use an S-cable to connect devices that are installed on separate DIN rails in a cabinet. For sufficient cooling air flow through the devices, the DIN rails and the devices are installed horizontally in the cabinet.

 
action_zoom_plus_stroke Devices installed on separate, horizontal rails and connected using an S-cable
Figure: Devices installed on separate, horizontal rails and connected using an S-cable

The S-cable is available with right angle connectors and in 1.5 m (5 ft) and 0.75 m (2 ft 5 in) lengths. You can serially connect up to two S-cables to extend the length.

The following image shows the minimum space required for plugging/unplugging the S-cable from the device but also provides information on the minimum bend radius required to reduce the stress of the cable. The S-cable with straight connectors is a discontinued product, which can no longer be ordered from Schneider Electric.

 
action_zoom_plus_stroke S-cable connecting devices on separate rails
Figure: S-cable connecting devices on separate rails

Device order

The order in which the devices are installed in the chain (I/O bus) is important. The devices should be installed in the following order:

  • Position 1 (leftmost): Power supply (mandatory)

  • Position 2: AS-P server (mandatory)

  • Position 3 to 32: Central IO modules and extra power supplies as needed based on power budget. One power supply can supply power for loads up to 30 W. For more information, see Power Budget .

Note:

There is a limit of one automation server per I/O bus.

The rules are summarized in the following illustration.

 
action_zoom_plus_stroke Order of devices on the I/O bus
Figure: Order of devices on the I/O bus

To connect terminal bases
  1. Ensure that each terminal base is clipped to the DIN-rail.

  2. Push each terminal base firmly against its neighbor to the left, ensuring that the power supply and address bus connector is properly mated.

     
    action_zoom_plus_stroke
  3. On the backplane label of each terminal base, write the type of module to be connected to that terminal base.

You can now wire the terminal base.

  • Device Installation
  • Wiring a Terminal Base