earth_america
user_standard Anmelden
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Benutzeroberfläche

Benutzeroberfläche


Produkte: AS-B, Enterprise Central, Enterprise Server, AS-P, Project Configuration Tool
Funktionen: Alarme
Produktversion: 3.2, 3.3, 2022
15.10.2020

Create Out of Reference Range Alarm Wizard – Alarm Trigger Page

Use the Alarm Trigge r page to configure the trigger settings of the out of reference range alarm.

 
action_zoom_plus_stroke Out of reference range alarm trigger page
Abbildung: Out of reference range alarm trigger page

Tabelle: Out of Reference Range Alarm Trigger Page

Component

Description

Upper deviation limit

​Enter the upper limit the monitored variable is allowed to deviate from the reference variable before the alarm is triggered.

Lower deviation limit

​Enter the lower limit the monitored variable is allowed to deviate from the reference variable before the alarm is triggered.

Deadband

​Enter the range the monitored variable has to pass within the normal range before the alarm is reset.

Monitored variable

​Enter the path to the variable that is monitored by the alarm.

Disable alarm

Select to disable the alarm, for example, before deployment.

Reference variable

​Enter the reference variable that is compared with the monitored variable.

Alarm delay

​Enter the time, in seconds, the alarm has to be within the alarm criteria before the alarm is triggered.

Reset delay

​Enter the time, in seconds, the alarm has to be within the reset criteria before the alarm state is changed from alarm to reset.

Shunt variable 1

​Enter the shunt variable that is used to enable or disable the alarm. Für weitere Informationen siehe Shunt Variables .

Invert

Select to invert the shunt value, that is, enable the alarm when the shunt value is active and disable the alarm when the shunt value is inactive. Für weitere Informationen siehe Shunt Variables .

Operator

Select AND or OR to add logic between the first and the second shunt variable. Für weitere Informationen siehe Shunt Variables .

Shunt variable 2

​Enter the second shunt variable that is used to enable or disable the alarm. Für weitere Informationen siehe Shunt Variables .

Invert

Select to invert the shunt value, that is, enable the alarm when the shunt value is active and disable the alarm when the shunt value is inactive. Für weitere Informationen siehe Shunt Variables .

 
action_zoom_plus_stroke

Set u nit

​Enter the unit of the alarm.

  • Out of Reference Range Alarms
  • Create Alarm Wizard – Presentation Page
  • Create Alarm Wizard – User Action Page
  • Create Alarm Wizard – Attachment Page
  • Out of Reference Range Alarm Properties – Basic Tab
  • Create Object Dialog – Naming the Object Page