Use the Alarm Trigge r page to configure the trigger settings of the out of reference range alarm.
Component |
Description |
Upper deviation limit |
Enter the upper limit the monitored variable is allowed to deviate from the reference variable before the alarm is triggered. |
Lower deviation limit |
Enter the lower limit the monitored variable is allowed to deviate from the reference variable before the alarm is triggered. |
Deadband |
Enter the range the monitored variable has to pass within the normal range before the alarm is reset. |
Monitored variable |
Enter the path to the variable that is monitored by the alarm. |
Disable alarm |
Select to disable the alarm, for example, before deployment. |
Reference variable |
Enter the reference variable that is compared with the monitored variable. |
Alarm delay |
Enter the time, in seconds, the alarm has to be within the alarm criteria before the alarm is triggered. |
Reset delay |
Enter the time, in seconds, the alarm has to be within the reset criteria before the alarm state is changed from alarm to reset. |
Shunt variable 1 |
Enter the shunt variable that is used to enable or disable the alarm. Mer information finns i Shunt Variables . |
Invert |
Select to invert the shunt value, that is, enable the alarm when the shunt value is active and disable the alarm when the shunt value is inactive. Mer information finns i Shunt Variables . |
Operator |
Select AND or OR to add logic between the first and the second shunt variable. Mer information finns i Shunt Variables . |
Shunt variable 2 |
Enter the second shunt variable that is used to enable or disable the alarm. Mer information finns i Shunt Variables . |
Invert |
Select to invert the shunt value, that is, enable the alarm when the shunt value is active and disable the alarm when the shunt value is inactive. Mer information finns i Shunt Variables . |
|
Set u nit Enter the unit of the alarm. |