Concept

Concept


Products: Automation Server, AS-B, Enterprise Server, AS-P, Project Configuration Server, Virtual Project Servers
Functionalities: Alarms
Product version: 1.8
10/13/2016

Alarm Types

arrow1_rotationChange of State Alarms arrow1_rotationOut of Range Alarms arrow1_rotationOut of Reference Range Alarms arrow1_rotationMultistate Alarms arrow1_rotationMatching Text String Alarms arrow1_rotationVariable Status Alarms arrow1_rotationSum Alarms arrow1_rotationEnumeration Alarms arrow1_rotationSystem Alarms arrow1_rotationEcoStruxure Web Service Alarm Item

An alarm compares the value from a monitored variable with the conditions of the alarm. Different types of alarms handle different types of variables and different forms of evaluation.

Alarms can monitor values from external sources, such as LonWorks and BACnet devices, as well as values from SmartStruxure servers. Some alarms are also based on system information, such as device restart or network status.

Change of State Alarms

The change of state alarm monitors the state changes of digital variables. You configure the alarm ​to trigger when the variable changes its state to true or to false.

For more information, see Change of State Alarms .

Out of Range Alarms

​When setting up an out of range alarm, you configure the normal range of the monitored variable. If the variable goes below the lower limit or above the upper limit of the normal range, the alarm is triggered.

For more information, see Out of Range Alarms .

Out of Reference Range Alarms

​The out of reference range alarm monitors variable movements comparing to a reference variable. By setting an upper deviation limit and lower deviation limit, you configure the tolerance the monitored variable can vary from the reference variable before the alarm is triggered. The upper alarm limit of the monitored variable is equal to the reference point current value plus the upper deviation limit. The lower alarm limit of the monitored variable is equal to the reference point current value minus the lower deviation limit.

For more information, see Out of Reference Range Alarms .

Multistate Alarms

​The multistate alarm monitors a variable and triggers the alarm if the variable is between the configured alarm range or equal to a single value. You can add several ranges or single values to trigger the alarm.

For more information, see Multistate Alarms .

Matching Text String Alarms

​A matching text string alarm evaluates if the monitored value equals the given text strings.

For more information, see Matching Text String Alarms .

Variable Status Alarms

The variable status alarm monitors the status of a variable. The alarm is triggered when the value of the monitored variable is either forced or overridden. If you configure the alarm to trigger on both force and override, the alarm is triggered immediately when the variable changes to one of the two statuses.

For more information, see Variable Status Alarms .

Sum Alarms

​A sum alarm can be seen as a collection of alarms that have one or several common denominators. The conditions you use to filter out which alarms the sum alarm monitors are the same conditions you use to filter the Alarms pane or an Alarm View. You can use wildcards when setting up filter conditions. For more information, see Filter Condition Wildcards .

For more information, see Sum Alarms .

Enumeration Alarms

​An enumeration is a variable with labeled values; different variables have different enumerations. When configuring an enumeration alarm, you configure the variable and its enumerations to monitor.

For more information, see Enumeration Alarms .

System Alarms

​System alarms monitor system entities, such as online status for SmartStruxure server devices or field devices. The system alarms are generated by Building Operation. Users cannot create new system alarms. The possible causes of a system alarm are gathered in an enumeration called System alarm ID. When a system alarm is triggered, the cause of the alarm is indicated in the System alarm ID column in the Alarms pane or Alarm View. Some system alarms have additional information in the Alarm text column.

For more information, see System Alarms .

EcoStruxure Web Service Alarm Item

The EcoStruxure Web Service alarm item is a representation of an alarm on an EcoStruxure Web Service. The alarm item is automatically created when you host an EcoStruxure Web Service alarm on your system.

For more information, see EcoStruxure Web Service Alarm Item .

  • Mass Creating Alarms
  • Mass Creating Alarms Using the Search Method
  • Change of State Alarms
  • Out of Range Alarms
  • Out of Reference Range Alarms
  • Multistate Alarms
  • Matching Text String Alarms
  • Sum Alarms
  • Enumeration Alarms
  • System Alarms
  • Alarms Overview
  • Variable Status Alarms
  • EcoStruxure Web Service Alarm Item
  • Configuring the Description of an Alarm