SpaceLogic™ UI-16 Central IO module is a universal input, 16-channel I/O module.
The universal inputs are ideal for any mix of temperature, pressure, flow, status points, and similar point types in a building control system.
The universal inputs can be configured to read several different types of inputs:
Digital
Counter
Supervised
Voltage
Current
Temperature
Resistive
As counter inputs they are commonly used in energy metering applications. As supervised inputs they are used for security applications where it is critical to know whether or not a wire has been cut or shorted. These events provide a separate indication of alarms and trouble conditions to the system.
The modules are part of a modular system that delivers power and communications on a common bus. Connecting modules is a one-step process: just slide the modules together using the built-in connectors.
Each module can be separated from its terminal base to allow the site to be wired prior to the installation of the electronics. The patented locking mechanism serves as handles for removing the module from its base. All critical components have a protective cover that permits convection cooling to occur.
Because critical applications require 24-hour operation, Schneider Electric designed the Central IO modules for hot-connection of terminal bases and hot-swapping of the modules to their bases. This design ensures continuous power and communication during service operations.
The auto-addressing feature automatically assigns device addresses without the need to set DIP switches or press commission buttons. Each device automatically knows its order in the chain and assigns itself accordingly – significantly reducing engineering and maintenance time.
Fasteners easily snap into a locked position for panel installation. The fastener has a quick-release feature for easy DIN-rail removal.
The Central IO module terminals are clearly labeled and protected by transparent covers. The terminals are at the top and bottom of each module and are accessible for maintenance without removing the module. The EcoStruxure Building Operation WorkStation software can generate custom as-built labels for each module. Pre-perforated letter and A4 size label sheets are available as an accessory.
The SpaceLogic devices use built-in connectors for single row connectivity, side by side. If a panel size requires multiple rows, extension cords are available.
The Central IO module has a status indicator that denotes the health and status of the module.
Each input channel has a dedicated two color status LED. The LED can be configured to display either red or green for each input state.
Protection components on the inputs protect against high-voltage short-duration transient events.
The current inputs are protected against over current.
Input channels
|
16
|
DC input supply power
|
1.8 W
|
DC input supply voltage
|
24 VDC
|
| Environment | |
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
Ambient temperature, storage
|
-20 to +70 °C (-4 to +158 °F)
|
Maximum humidity
|
95 % RH non-condensing
|
| Material | |
Plastic flame rating
|
UL94-5VB
|
Enclosure
|
PC/ABS
|
Ingress protection rating
|
IP 20
|
| Mechanical | |
Dimensions including terminal base
|
90 W x 114 H x 64 D mm (3.6 W x 4.5 H x 2.5 D in.)
|
|
|
Weight including terminal base TB-IO-W1
|
0.269 kg (0.59 lb)
|
Weight including terminal base TB-IO-W1-2
|
0.299 kg (0.66 lb)
|
Weight excluding terminal base
|
0.146 kg (0.32 lb)
|
Terminal base
|
TB-IO-W1
|
TB-IO-W1-2
|
|
| Agency compliances | |
Emission
|
RCM; BS/EN 61000-6-3; FCC Part 15, Sub-part B, Class B
|
Immunity
|
BS/EN 61000-6-2
|
Safety standards
|
BS/EN 61010-1; UL 916 C-UL US Listed
|
Product
|
BS/EN 61326-1
|
Smoke control product safety
|
UL 864
|
| Part numbers | |
UI-16, Central IO module
|
|
16 universal inputs
|
SXWUI16XX10001
|
TB-IO-W1, terminal base for Central IO module
a
|
|
(Required for each Central IO module)
|
SXWTBIOW110001
|
| a) The Central IO modules are compatible with TB-IO-W1 (SXWTBIOW110001) and TB-IO-W1-2 (SXWTBIOW110002). TB-IO-W1 is UL 864 certified. UL 864 certification for TB-IO-W1-2 is currently pending. | |
TB-IO-W1-2, terminal base for Central IO module
a
|
|
(Required for each Central IO module)
|
SXWTBIOW110002
|
| a) The Central IO modules are compatible with TB-IO-W1 (SXWTBIOW110001) and TB-IO-W1-2 (SXWTBIOW110002). TB-IO-W1 is UL 864 certified. UL 864 certification for TB-IO-W1-2 is currently pending. | |
| Accessory part numbers | |
DIN-RAIL-CLIP, DIN-rail end clip
|
|
package of 25 pieces
|
SXWDINEND10001
|
PRINTOUT-A4-W1, printout sheets for terminal labels
|
|
A4 sheet size, 100 sheets, 18 labels per sheet
|
SXWTERLBL10011
|
PRINTOUT-LTR-W1, printout sheets for terminal labels
|
|
Letter sheet size, 100 sheets, 16 labels per sheet
|
SXWTERLBL10012
|
S-CABLE-L, S-cable extension cord for the I/O bus, L shaped connectors
|
|
1.5 m
|
SXWSCABLE10002
|
S-CABLE-L, S-cable extension cord for the I/O bus, L shaped connectors
|
|
0.75 m
|
SXWSCABLE10003
|
| Universal inputs | |
|
|
Absolute maximum ratings
|
-0.5 to +24 VDC
|
A/D converter resolution
|
12 bits
|
| Digital | |
Range
|
Dry contact switch closure or open collector/open drain, 24 VDC, 2.4 mA
|
Minimum pulse width
|
120 ms
|
LED polarity
|
Software selectable, if the LED is activated when the input is high or low
|
LED color
|
Red or green, software selectable
|
| Counter | |
Range
|
Dry contact switch closure or open collector/open drain, 24 VDC, 2.4 mA
|
Minimum pulse width
|
20 ms
|
Maximum frequency
|
25 Hz
|
LED polarity
|
Software selectable, if the LED is activated when the input is high or low
|
LED color
|
Red or green, software selectable
|
| Supervised | |
5 V circuit, 1 or 2 resistors
|
|
Monitored switch combinations
|
Series only, parallel only, and series and parallel
|
Resistor range
|
1 to 10 kohm
|
| For a 2-resistor configuration, each resistor must have the same value +/- 5 % | |
| Voltage | |
Range
|
0 to 10 VDC
|
Accuracy
|
+/-(7 mV + 0.2 % of reading)
|
Resolution
|
2.7 mV
|
Impedance
|
100 kohm
|
Reliability check
|
Yes
|
| Current | |
Range
|
0 to 20 mA
|
Accuracy
|
+/-(0.03 mA + 0.4 % of reading)
|
Resolution
|
5.6 μA
|
Impedance
|
47 ohm
|
Reliability check
|
Yes
|
| Resistive | |
10 ohm to 10 kohm accuracy
|
+/-(7 + 4 x 10
-3
x R) ohm
|
| R = Resistance in ohm | |
10 kohm to 60 kohm accuracy
|
+/-(4 x 10
-3
x R + 7 x 10
-8
x R
2
) ohm
|
| R = Resistance in ohm | |
Reliability check
|
Yes
|
| Temperature | |
Range
|
-50 to +150 °C (-58 to +302 °F)
|
Reliability check
|
Yes
|
| Supported thermistors | |
Honeywell
|
20 kohm
|
Type I (Continuum)
|
10 kohm
|
Type II (I/NET)
|
10 kohm
|
Type III (Satchwell)
|
10 kohm
|
Type IV (FD)
|
10 kohm
|
Type V (FD w/ 11k shunt)
|
Linearized 10 kohm
|
Satchwell D?T
|
Linearized 10 kohm
|
Johnson Controls
|
2.2 kohm
|
Xenta
|
1.8 kohm
|
Balco
|
1 kohm
|
| Measurement accuracy | |
20 kohm, 10 kohm, 2.2 kohm, and 1.8 kohm
|
-50 to -30 °C: +/-1.5 °C (-58 to -22 °F: +/-2.7 °F)
|
-30 to 0 °C: +/-0.5 °C (-22 to +32 °F: +/-0.9 °F)
|
|
0 to 50 °C: +/-0.2 °C (32 to 122 °F: +/-0.4 °F)
|
|
50 to 100 °C: +/-0.5 °C (122 to 212 °F: +/-0.9 °F)
|
|
100 to 150 °C: +/-1.5 °C (212 to 302 °F: +/-2.7 °F)
|
|
Linearized 10 kohm
|
-50 to -30 °C: +/-3.0 °C (-58 to -22 °F: +/-5.4 °F)
|
-30 to 0 °C: +/-1.0 °C (-22 to +32 °F: +/-1.8 °F)
|
|
0 to 50 °C: +/-0.3 °C (32 to 122 °F: +/-0.5 °F)
|
|
50 to 100 °C: +/-0.5 °C (122 to 212 °F: +/-0.9 °F)
|
|
100 to 150 °C: +/-2.0 °C (212 to 302 °F: +/-3.6 °F)
|
|
1 kohm
|
-50 to +150 °C: +/-1.5 °C (-58 to +302° F: +/-2.7 °F)
|