You must configure the DIP switches as part of the commissioning process for the RP and MP controllers and RP-IO modules that only support MS/TP communications.
For more information, see BACnet MS/TP Network Communications .
Use only switches 1-7. Switch 8 is unused.
See the table and graphic that follows for more information on the switches and their ON values.
|
Switch |
ON value |
|
1 |
1 |
|
2 |
2 |
|
3 |
4 |
|
4 |
8 |
|
5 |
16 |
|
6 |
32 |
|
7 |
64 |
For example, to configure address 6, configure DIP switches 2 and 3 to ON and switches 1, 4, 5, 6 and 7 to OFF.