The RP-V controllers support BACnet MS/TP communication. The BACnet MS/TP configuration differs between the RP-V models. The BACnet/IP enabled RP-V controllers can be reconfigured to communicate with automation servers based on the BACnet MS/TP protocol, instead of the BACnet/IP protocol. An adapter is required for converting the controller RS-485 Com port with RJ45 interface to screw terminals. There is also an RP-V model designed for connection to a BACnet MS/TP (RS-485) network and this model can only communicate via MS/TP.
Regarding the differences in the BACnet protocol support, the RP-V controller models can be divided into the following two categories:
RP-V controllers supporting both BACnet/IP and MS/TP
RP-V controllers only supporting BACnet MS/TP
This category of BACnet/IP enabled RP-V controllers needs to be reconfigured to communicate using BACnet MS/TP, instead BACnet/IP. The category consists of the following RP-V models:
RP-V-4A
RP-V-5A
For more information, see RP-V Models .
The support for connecting RP controllers to a BACnet MS/TP (RS-485) network for communication with an automation server (AS-P or AS-B) enables retrofitting of MNB and b3 BACnet devices on the network while reusing parts of the existing cabling and equipment. For more information, see RS-485 Communications .The support for both BACnet IP and BACnet MS/TP protocols also facilitates a transition from a BACnet MS/TP (RS-485) network to an IP based network. The controller can be configured to use either protocol.
“MNB BACnet devices” refers to Schneider Electric (TAC I/A Series) MicroNet BACnet (MNB) zone controllers.
“b3 BACnet devices” refers to Schneider Electric (Andover Continuum) b3 BACnet zone controllers.
An RJ45 to screw terminal block adapter and a separate connection cable is required to connect the RP controllers to the BACnet MS/TP (RS-485) network. For more information, see RS-485 Adapters .
The RS-485 adapters are available in two models:
Isolated RS-485 Adapter (SXWISORS48510001)
Non-isolated RS-485 Adapter (SXWNISORS48510001)
The RS-485 adapters can be ordered from Schneider Electric using the above part numbers.
The isolated adapter is designed to be used when connecting RP controllers to a BACnet MS/TP (RS-485) network with MNB devices.
The non-isolated adapter is designed to be used when connecting RP controllers to a BACnet MS/TP (RS-485) network with b3 BACnet devices.
The cable is not included and needs to be purchased separately.
To connect the adapter, it is recommended to use a Cat 5 (or higher) unshielded, straight-through wired cable with eight conductors (four twisted pairs) and RJ45 connectors. The recommended maximum cable length is 0.3 m (12 inches). The wire size (cross-sectional area) should be 22 to 26 AWG (0.34 to 0.14 mm²). When RP controllers are installed in a space that handles conditioned air or return air, the BACnet MS/TP (RS-485) network cables and IP network cables frequently must be plenum-rated to meet applicable building codes.
For more information, see Wiring .
You need to configure which RS-485 (RJ45) port on the RP-V controller to use for connection to the automation server BACnet MS/TP (RS-485) network. You can configure to use either the RS-485 Com A or Com B port, with the following restrictions:
RS-485 Com B can either be used for connection of an isolated adapter or a non-isolated adapter
RS-485 Com A can only be used for connection of a non-isolated adapter
For more information, see Communication Ports on RP-V-4A and -5A .
For more information, see Allocating Flexible Ports .
As part of the commissioning process for the device, you also need to configure the baud rate for the automation server BACnet MS/TP (RS-485) bus. For more information, see MS/TP Communications Baud Rate .
 
    In retrofit projects with MNB devices, the RP-V controllers can be mixed with MNB devices on the BACnet MS/TP (RS-485) network.
The isolated RS-485 adapter is used for connection of the RP-V controller.
The isolated RS-485 adapter must be connected to the RS-485 Com B port on the RP-V controller.
 
    In retrofit projects with b3 BACnet devices, the RP-V controllers can be mixed with b3 BACnet devices on the BACnet MS/TP (RS-485) network.
The non-isolated RS-485 adapter is used for connection of the RP-V controller.
The non-isolated RS-485 adapter can be connected to either the RS-485 Com A or Com B port on the RP-V controller.
 
    This category of RP-V controllers only supports connection to an BACnet MS/TP (RS-485) network. The category consists of the RP-V model with “-M” in the product name:
RP-V-5C-M
For more information, see RP-V Models .
The RP-V controllers have an RS-485 port with a 3-pole removable screw terminal block that is used for connection to the BACnet MS/TP (RS-485) network and MS/TP communication with the automation server (AS-P or AS-B). Connecting to an IP network is not supported as this RP-V model does not have Ethernet ports. For more information, see Communication Ports on RP-V-5C-M .
You need to configure a unique MS/TP address for the device during installation using the address DIP switches on the device. For more information, see MS/TP DIP Switches .
As part of the commissioning process for the device, you also need to configure the baud rate for the automation server BACnet MS/TP (RS-485) bus. For more information, see MS/TP Communications Baud Rate .
 
    The RP-V controllers can be mixed with b3 BACnet devices on the BACnet MS/TP (RS-485) network. For more information, see RS-485 Communications .
RP-V-5C-M is not isolated and connection of the device to a network comprised of isolated RS-485 interfaces is not recommended. The RS-485 application guidelines provide additional details. For more information, see RS-485 Communications .