The Schneider Electric EasyLogic and SpaceLogic hardware devices for the EcoStruxure BMS include terminal bases, PS-24V power supplies, Central IO modules, automation servers such as AS-P and AS-B servers, MP-C, MP-V, RP-C, and RP-V controllers, IP-IO and RP-IO I/O modules, RP controller expansion modules, remote control, KNX Modbus gateway, Bluetooth adapter, Wireless Adapter - Advanced, SpaceLogic Sensor devices, Advanced Display devices, and Operator Display devices.
The terminal bases are used for SpaceLogic devices that are based on the patented two-piece design. The terminal base provides the I/O bus to the electronics module installed on the terminal base as well as to the SpaceLogic device installed to the right (next terminal base in the chain).
Per maggior informazioni, consulta Terminal Bases .
PS-24V is the power supply for the AS-P servers and Central IO modules. The PS-24V power supply requires an input voltage of either 24 VAC +/–20 % or 24–30 VDC.
Per maggior informazioni, consulta PS-24V Power Supplies .
The AS-P server offers enhanced processor performance, increased memory size, dual Ethernet ports, and high-speed USB interfaces. The AS-P server is a Schneider Electric manufactured embedded device that generally serves as the lowest tier EcoStruxure BMS server within the EcoStruxure BMS. The AS-P controls and supervises equipment, typically HVAC equipment. AS-P servers use Central IO module with connected field devices, such as sensors and actuators, to do that.
Per maggior informazioni, consulta AS-P Servers .
By adding a variety of Central IO and power supply modules, you can use the AS-P server to tailor the Intelligent Building Management System to your unique requirements.
Per maggior informazioni, consulta Central IO Modules .
An AS-B server is a powerful automation server that features both onboard I/O and built-in power supply. Like the other automation servers, the AS-B server is a Schneider Electric manufactured embedded device that generally serves as the lowest tier EcoStruxure BMS server within the EcoStruxure BMS. The automation server controls and supervises equipment, typically HVAC equipment. The AS-B server uses its onboard I/O with connected field devices, such as sensors and actuators, to do that.
Per maggior informazioni, consulta AS-B Servers .
The MP-C controller is a multi-purpose, fully programmable, IP based field controller. The MP-C models offer a flexible mix of I/O point types that suits a wide range of HVAC applications. The MP-C can either be used as a standalone BACnet field controller or as part of an EcoStruxure BMS with an automation server or Enterprise Server as the parent server.
Per maggior informazioni, consulta MP-C Controllers .
The MP-V controller is a multi-purpose, fully programmable, IP based field controller dedicated for VAV applications. MP-V integrates a controller, a damper actuator, and an air flow sensor in a single unit for ease of installation. The MP-V can either be used as a standalone BACnet field controller or as part of an EcoStruxure BMS with an automation server or Enterprise Server as the parent server. MP-V can also be reconfigured through the EcoStruxure Building Operation software to use BACnet MS/TP, instead of BACnet/IP.
Per maggior informazioni, consulta MP-V Controllers .
The IP-IO module provides I/O expansion to your HVAC application over BACnet/IP and can share their I/O resources across applications running in automation servers, BACnet/IP controllers, or third-party systems. The IP-IO module can be installed near facilities in the field, away from the automation server or the BACnet/IP controller.
Per maggior informazioni, consulta IP-IO Modules .
The RP-C controller is a room-purpose, fully programmable, IP based field controller. The RP-C models offer a flexible mix of I/O point types that suit a wide range of HVAC applications. The RP-C can either be used as a standalone BACnet field controller or as part of an EcoStruxure BMS with an automation server or Enterprise Server as the parent server. The BACnet/IP enabled RP-C controller can also be reconfigured through the EcoStruxure Building Operation software to support BACnet MS/TP, instead of BACnet/IP. The RP-C features a wireless chip that allows a mobile device running the Commission mobile application to connect directly to the controller.
Per maggior informazioni, consulta RP-C Controllers .
The RP-V controller is a room-purpose, fully programmable, IP based field controller dedicated for VAV cooling and Heating applications. RP-V integrates a controller, a damper actuator, and an air flow sensor in a single compact unit for ease of installation. The controller can either be used as a standalone BACnet field controller or as part of an EcoStruxure BMS with an automation server or an Enterprise Server as the parent server. The BACnet/IP enabled RP-V controller can also be reconfigured through the EcoStruxure Building Operation software to support BACnet MS/TP, instead of BACnet/IP. The RP-V features a wireless chip that allows a mobile device running the Commission mobile application to connect directly to the controller.
Per maggior informazioni, consulta RP-V Controllers .
The RP-IO module provides I/O expansion to your HVAC application over BACnet MS/TP. The I/O module can share its I/O resources across applications running in automation servers, RP and MP controllers, or third-party systems. With the support of local alarms and local trend logs, the I/O module avoids unnecessary traffic over the network while being able to log important information locally. The I/O module can be installed near facilities in the field, away from the automation server or the RP or MP controller.
Per maggior informazioni, consulta RP-IO Modules .
The RP controller expansion modules provide a range of devices that can be combined to form a connected room solution. The RP controller expansion modules are connected to the RP controller room bus and provide the RP controllers with I/O expansion and sensors that enable lighting and blind control.
Per maggior informazioni, consulta RP Controller Expansion Modules .
The RP controller expansion Zigbee modules provide devices that can be used to form a connected room solution. The RP controller expansion Zigbee modules are connected to the RP-C room controllers through the Zigbee TM wireless protocol and provide the controllers with I/O expansion that enable lighting control.
Per maggior informazioni, consulta RP Controller Expansion Zigbee Modules .
The RP-C-RC-BLE remote control connects wirelessly to the RP controller expansion sensor modules, such as the Multi-sensor and Insight-Sensor, and enables the occupants of modern office buildings to control the comfort level of their space.
Per maggior informazioni, consulta RP-C-RC-BLE .
The KNX Modbus gateway RP-C-EXT-KNX connects to the RP-C controllers and provides an interface between the controller and KNX devices such as push-buttons, sensors, and control units for lights, blinds, and room temperature.
Per maggior informazioni, consulta KNX Modbus Gateway RP-C-EXT-KNX .
SpaceLogic Sensors are a family of living space sensors designed for BACnet/IP controllers using the EcoStruxure Building Operation user interface. These sensors use an RJ-45 sensor bus that provides communication and power from the BACnet/IP controller.
Per maggior informazioni, consulta SpaceLogic Sensors .
The SpaceLogic Bluetooth Adapter is plugged into a SpaceLogic Sensor to provide a wireless Bluetooth connection to the BACnet/IP controller (Sensor Bus compliant controller) for commissioning, maintenance, and troubleshooting of the controller and the sensor.
Per maggior informazioni, consulta SpaceLogic Bluetooth Adapter .
Wireless Adapter - Advanced is a USB-based wireless adapter that enables Zigbee TM wireless connectivity with an RP-C controller, AS-P server, or AS-B server, extending the controller's or server's point count and bringing flexibility in retrofit applications.
Per maggior informazioni, consulta Wireless Adapter - Advanced .
AD v1 provides a Human Machine Interface (HMI) for local access to the EcoStruxure BMS servers.
Per maggior informazioni, consulta AD v1 .
AD v2 is the successor to AD v1, and offers several improvements such as higher display resolution, enhanced processor performance, and increased memory size. Like AD v1, AD v2 provides a Human Machine Interface (HMI) for local access to the EcoStruxure BMS servers.
Per maggior informazioni, consulta AD v2 .
Advanced Display v3 (AD v3) is the successor to AD v2. AD v3 provides an industrial grade Human Machine Interface (HMI), with battery-free power supply, for local access to the EcoStruxure BMS servers.
Per maggior informazioni, consulta AD v3 .
SpaceLogic™ Operator Display is a touch-screen Human Machine Interface (HMI) for SpaceLogic controllers and servers, designed for local monitoring of building controllers in small and medium-sized buildings, as well as in large buildings with comprehensive building management systems. Operator Display is specifically designed for equipment rooms and it simplifies operations, service, and troubleshooting for System Integrators and Service Engineers, as well as for non-technical users (notably Facility Managers and Janitors).
Per maggior informazioni, consulta Operator Display .
The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, RP and MP controllers, IP-IO and RP-IO modules, RP controller expansion modules, and Operator Display.
Per maggior informazioni, consulta Wiring .