Power Rating

Using the power rating for each of the modules (listed in the following table), accumulate the power consumed by the Smoke Control Server and I/O modules. The PS-24V can supply up to 30W (~1.25A at 24 VDC). The 24 VDC from the PS-24V is delivered to all modules connecting on the bus on the right side of the PS-24V up to the next power supply module. You must add another PS-24V on the I/O bus to keep the load on the previous power supply at 30W or below.

Tabella: Power Budget Table

Device

Power (W)

AS-P

10.0

Automation Server

7.0

AO-8

4.9

AO-8-H

4.9

AO-V-8

0.7

AO-V-8-H

0.7

DI-16

1.6

DO-FA-12

1.8

DO-FA-12-H

1.8

DO-FC-8

2.2

DO-FC-8-H

2.2

RTD-DI-16

1.6

UI-16

1.8

UI-8-DO-FC-4

1.9

UI-8-DO-FC-4-H

1.9

UI-8-AO-4

3.2

UI-8-AO-4-H

3.2

UI-8-AO-V-4

1.0

UI-8-AO-V-4-H

1.0