The PS-24V is mounted on the Terminal Base model TB-PS-W1. The TB-PS-W1 appears similar to the TB-AS-W1 terminal base as seen in the figures in the section that follows. Per maggior informazioni, consulta AS-P Installation .
They differ in the printed circuit board function provided in each.
There may be multiple PS-24V modules on an I/O bus, but there must be one located in the first, leftmost position on the bus (directly to the left of the Automation Server, or AS-P). The connector extending from the right side of the first TB-PS-W1 base is the beginning of the I/O bus. The TB-AS-W1 terminal base (holding the Automation Server (AS-SMK)), or the TB-ASP-W1 (holding the AS-P (AS-P-SMK)) is located adjacent and to the right of the first PS-24V. The TB-AS-W1 base slides to the left on the DIN rail to receive and mate with the connector extending from the TB-PS-W1 base.
The PS-24V receives input power in the form of 24 VAC +/-20% (60VA max) and delivers a 24 VDC +/-1V (30W) to the terminal base backplane. In smoke control applications, the 24-30 VDC power input capability is not used. The terminal base is typically wired before plugging in electronic module (the PS-24V). Only terminals 1, 2 and 4 are used in the power supply terminal base for power input. The following diagram shows the terminations.
You connect a PS-24V power supply module as follows:
Connect a 24 VAC source (from one of the transformers listed in this guide) to terminals 1 and 2 on the terminal base using 18 AWG (or larger) wire
Per maggior informazioni, consulta Transformers .
Connect terminal 4 to the Earth or Signal ground rail in the enclosure using 16 AWG (or larger) wire
Use the power budget table to determine how many and what type of I/O modules you can power from this PS-24V module. You must also use the table to determine where you must install another PS-24V module to power additional I/O modules.
Per maggior informazioni, consulta Power Rating .
You must connect the additional PS-24V modules to 24 VAC input power as shown.
The specifications for the PS-24V are as follows:
Power Input |
|
AC Input Voltage |
24VAC Class 2 |
AC Input Range |
+/- 20% 50/50Hz |
Maximum Current |
2.5 A rms |
Transformer Size |
60VA or larger |
Power Output |
|
DC Output |
24VDC +/- 1VDC |
Maximum Power |
30W |
Environment |
|
Op. Temperature |
0 to 50 o C 32 to 122 o F |
Humidity |
95% Max. nonCondensing |
Mechanical |
|
Housing Rating |
IP20 |
Plastic Rating |
UL94-5VB |
The PS-24V Status LED indicates the condition of the device as follows:
LED Patterns |
Condition of the PS-24V |
Green, constant |
Output voltage and load OK |
Red/green, flashing |
Output slightly overloaded |
Red, constant |
Output overloaded |
No light |
No input power |
The Main Power LED is illuminated when the module receives 24 VAC power.
The LEDs provided on the PS-24V, the Smoke Control Servers and all of the I/O modules are intended to support diagnostic and service functions for the modules. Per maggior informazioni, consulta Module Status LEDs .