Use this workflow to perform flow balance on a single MP-V controller, using the Commission mobile application. Related information can be found in the section after the flowchart.
Więcej informacji zawiera Flow Balancing .
Start the Commission mobile application and log in as either a Technician or Flow Balancer.
Więcej informacji zawiera Downloading and Starting the eCommission SmartX Controllers Mobile Application .
Discover controllers on the site, and connect to a single MP-V.
Więcej informacji zawiera Device Connection .
You configure the MP-V controller setpoints to set up the parameters by which the controller is flow balanced. These setpoints include the maximum flow setpoint, selected by default, and the intermediate and minimum flow setpoints, which are optional.
Więcej informacji zawiera Configuring MP-V Controller Setpoints .
Once the setpoints are configured and before the flow balance is started, the damper is forced closed to obtain an average reading of the zero flow threshold before continuing to balance for each setpoint. You can either apply these changes, or ignore once the calculation is completed.
Więcej informacji zawiera VAV Objects Provided for the Commission Mobile Application .
Więcej informacji zawiera VAV Controller Automatic Velocity Pressure Offset Calibration .
Using the Commission mobile application, you flow balance a VAV unit at each designated setpoint to achieve the desired air flow.
Więcej informacji zawiera Flow Balancing at Minimum, Intermediate, or Maximum Flow Setpoint .
After flow balancing the MP-V controller, you can perform manual checkout on two components of the MP-V:
Verify direction of rotation to open
You can manually verify the direction of damper rotation to determine whether the actuator rotates clockwise or counterclockwise to open.
Więcej informacji zawiera Manually Verifying the Direction of Damper Rotation .
Manual checkouts of air flow
After completing the automated flow balancing process, you can optionally verify and command the air flow values by performing manual checkout.
Więcej informacji zawiera Performing Manual Checkout of Air Flow .
After completing flow balancing, you can use the Commission mobile application to create, append, view, or delete flow balance reports. Więcej informacji zawiera Managing Flow Balance Reports .