Manually Verifying the Direction of Damper Rotation

You can manually verify the direction of the damper rotation of a VAV controller to verify that the actuator rotates clockwise or counterclockwise to open.

Pokaż więcej
action_close

The Flow Balance function of the Commission mobile application is used to air balance terminal boxes controlled by a VAV controller. This function automates most of the air balance procedure but it also allows you to manually check out the flow balance by driving the damper to a specified position, a flow setpoint, or a flow value.

Flow balancing, also known as air balancing, is the process you use to calibrate an installed VAV terminal unit so that the airflow indicated by the VAV controller is accurate, relative to the true airflow delivered by the VAV terminal unit.

After the Electrician installs, wires, and powers the VAV controller, the controller automatically calibrates the damper stroke. Upon start-up, the VAV controller will automatically perform a damper stroke angle calibration where the damper rotates to each mechanical end stop. After the VAV controller has completed this process, it is ready to be accessed from the Commission mobile application to perform flow balancing.

When you select an VAV controller from the Commission mobile application, a Variable Air Volume Data object is automatically created in the controller. This object has values that read the Airflow Sensor terminal and values that configure the Damper Control 1 of the VAV controller. The VAV controller also contains logic to assist in the flow balancing calibration.

Więcej informacji zawiera Commission Mobile Application Overview .

Uwaga

The Commission mobile application supports flow balancing for VAV controllers with the data object Variable Air Volume only. The Commission mobile application does not support flow balancing for VAV controllers with custom balancing programs.

Flow Balancing Workflow

Use this workflow to perform flow balance on a single VAV controller controller, using the Commission mobile application. Related information can be found in the section after the flowchart. Więcej informacji zawiera Flow Balancer Workflow .

Configure Setpoints

You configure the VAV controller controller setpoints to prepare the parameters by which the controller is balanced. These setpoints include the maximum flow setpoint, selected by default, and the intermediate and minimum flow setpoints, which are optional. Więcej informacji zawiera Configuring MP-V Controller Setpoints .

Flow Balance at Setpoints

Using the Commission mobile application, you flow balance a VAV unit at each designated setpoint to achieve the desired air flow.

Więcej informacji zawiera Flow Balancing at Minimum, Intermediate, or Maximum Flow Setpoint .

Perform Manual Checkout

After completing the automated flow balancing process, you can use manual checkout to verify and command the air flow values for one or multiple VAV controllers.

Więcej informacji zawiera Performing Manual Checkout of Air Flow .

Verify Damper Rotation

You can manually verify the direction of the damper rotation of an VAV controller to verify that the actuator rotates clockwise or counterclockwise to open.

Więcej informacji zawiera Manually Verifying the Direction of Damper Rotation .

Flow Balance Reports

The Commission mobile application provides the user with a means to generate a flow balance report that documents several values:

  • Box capacity at 1 inch H20 (249 Pa)

  • Box measured flow

  • Hood measured flow for each setpoint used during balancing

  • Actuator stroke and rotation

  • Flow balance time and date

  • Any comments

Using the Commission mobile application, you can create, append, and delete flow balance reports. Flow balance reports are stored on the Commission mobile application mobile device and can be retrieved and shared using the file and e-mail applications of that mobile device or Windows 10 laptop.

Więcej informacji zawiera Flow Balance Reports .

To manually verify the direction of damper rotation
  1. In the Commission mobile application, in the Device List view, select the MP-V controller to be checked.

    Uwaga

    Flow Balancers are automatically brought to the Verify rotation page after Flow Balancing is complete.

  2. In the Menu , select Flow Balance .

  3. In the Air Balancing menu, select Verify rotation .

  4. To monitor the rotation in the Current Status pane, select the information icon

     
    action_zoom_plus_stroke
    .

  5. If an error message is displayed during rotation check, perform a manual check.

    Więcej informacji zawiera Error Message is Displayed During Rotation Check of MP-V Controller .

  6. Upon completing the manual checks, repeat steps 2 and 3.

The MP-V controller's rotation direction to open the damper is manually verified. Next, on the Manual checkout view, you continue manual checkout as needed

  • Flow Balancer Workflow
  • Flow Balancing
  • Error Message is Displayed During Rotation Check of MP-V Controller
  • Performing Manual Checkout of Air Flow