The Flow Balance function of the eCommission SmartX Controllers mobile application is used to air balance terminal boxes controlled by MP-V controllers. This function automates most of the air balance procedure but it also allows you to manually check out the flow balance by driving the damper to a specified position, a flow setpoint, or a flow value.
Flow balancing, also known as air balancing, is the process you use to calibrate an installed VAV terminal unit so that the airflow indicated by the VAV controller is accurate, relative to the true airflow delivered by the VAV terminal unit.
After the Electrician installs, wires, and powers the MP-V, the controller automatically calibrates the damper stroke. Upon start-up, the MP-V will automatically perform a damper stroke angle calibration where the damper rotates to each mechanical end stop. After the MP-V has completed this process, it is ready to be accessed from the eCommission application to perform flow balancing.
When you select an MP-V from the eCommission application, a Variable Air Volume Data object is automatically created in the controller. This object has values that read the Airflow Sensor terminal and values that configure the Damper Control 1 of the MP-V. The MP-V also contains logic to assist in the flow balancing calibration.
For more information, see eCommission SmartX Controllers Mobile Application Overview
.
Note:
The eCommission application supports flow balancing for MP-Vs with the data object
Variable Air Volume
only. The eCommission application does not support flow balancing for MP-Vs with custom balancing programs.
Flow Balancing Workflow
Use this workflow to perform flow balance on a single MP-V controller, using the eCommission SmartX Controllers mobile application. Related information can be found in the section after the flowchart.
For more information, see Flow Balancer Workflow
.
Configure Setpoints
You configure the MP-V controller setpoints to prepare the parameters by which the controller is balanced. These setpoints include the maximum flow setpoint, selected by default, and the intermediate and minimum flow setpoints, which are optional.
For more information, see Configuring MP-V Controller Setpoints
.
Perform Manual Checkout
After completing the automated flow balancing process, you can use manual checkout to verify and command the air flow values for one or multiple MP-V controllers.
For more information, see Performing Manual Checkout of Air Flow
.
Flow Balance Reports
The eCommission SmarX Controllers mobile application provides the user with a means to generate a flow balance report that documents several values:
Box capacity at 1 inch H20 (249 Pa)
Box measured flow
Hood measured flow for each setpoint used during balancing
Actuator stroke and rotation
Flow balance time and date
Any comments
Using the eCommission application, you can create, append, and delete flow balance reports. Flow balance reports are stored on the eCommission application mobile device and can be retrieved and shared using the file and e-mail applications of that mobile device or Windows 10 laptop.
For more information, see Flow Balance Reports
.