Our site will be unavailable from October 29-30 due to scheduled maintenance.
Thank you for your patience.
This section provides recommendations on wires sizes and lengths for the RP-C 230 V controller models.
This applies to the following RP-C 230 V controller models:
RP-C-16A-F-230V, RP-C-16B-F-230V, and RP-C-16C-F-230V
For more information, see RP-C Models .
The recommendations are for guidance only. Other wire sizes and lengths may be used, depending on wiring rules and when appropriate.
Screw terminal number 3 differs between different hardware versions of the controller model RP-C-16A-F-230V. For more information, see Differences Between RP-C Hardware Versions .
|
Terminals |
Minimum Cross-sectional Area |
Maximum Cable Length |
|
Power input terminals (1, 2) |
0.75 mm² (18 AWG) a or larger according to local wiring rules |
According to local wiring rules |
|
Protective earth ground terminal (3) |
0.75 mm² (18 AWG) a or larger according to local wiring rules |
According to local wiring rules |
|
24 VAC output terminals (4, 5) b |
0.5 mm² (20 AWG) |
According to local wiring rules |
|
External (EXT) input c |
0.5 mm² (20 AWG) |
According to local wiring rules |
|
Universal inputs/outputs as digital d inputs |
0.34 mm² (22 AWG) |
200 m (650 ft) |
|
Universal inputs/outputs as analog e inputs |
0.34 mm² (22 AWG) |
100 m (330 ft) |
|
Universal inputs/outputs as temperature (thermistor) inputs, up to 75 °C (167 °F) |
0.75 mm² (18 AWG) |
75 m (250 ft) |
|
Universal inputs/outputs as temperature (thermistor) inputs, up to 75 °C (167 °F) |
1.5 mm² (15 AWG) |
150 m (500 ft) |
|
Universal inputs/outputs as temperature (thermistor) inputs, up to 150 °C (302 °F) |
1.5 mm² (15 AWG) |
75 m (250 ft) |
|
Universal inputs/outputs, for actuators and transmitters powered from the same transformer as the RP-C |
0.75 mm² (18 AWG) |
20 m (65 ft) |
|
Universal inputs/outputs, for actuators and transmitters powered from their own transformer (external or internal) |
0.34 mm² (22 AWG) |
200 m (650 ft) |
|
Universal inputs/outputs as voltage outputs, for actuators powered via their own transformer (external or internal) or when the outputs have isolated converters |
0.34 mm² (22 AWG) |
200 m (650 ft) |
|
Relay outputs b |
According to local wiring rules f |
According to local wiring rules f |
|
High power relay output b |
According to local wiring rules f |
According to local wiring rules f |
|
Solid-state relay (SSR) outputs |
0.5 mm² (20 AWG) f |
According to local wiring rules f |