2022-03-11

RP-C-EXT-ZB-0-10V

The RP-C-EXT-ZB-0-10V Zigbee 0-10V module communicates with the RP-C room controller over the Zigbee TM wireless protocol and provides I/O expansion for 0-10V lighting control.

The Zigbee 0-10V module enables dimming of different types of lights equipped with electrical ballasts for 220–240 VAC line voltage. The Zigbee 0-10V module can distribute power (220–240 VAC) from an external power supply to the lights.

 
action_zoom_plus_stroke RP-C-EXT-ZB-0-10V – Zigbee 0-10V module
Rysunek: RP-C-EXT-ZB-0-10V – Zigbee 0-10V module

Zigbee 0-10V Light Output

The Zigbee 0-10V module has one 0-10V analog output for control (dimming) of lights with electronic ballasts, LED drivers, and other 0-10V compatible control gear and one power output for power distribution to the control gear.

Więcej informacji zawiera Zigbee 0-10V Light Output and Power Output .

Zigbee Modules Power Distribution

The RP controller expansion Zigbee modules have power distribution capability, which means that the module distributes the AC mains voltage (220–240 VAC) from the Power Input terminals to the light control gear connected to the Power Output terminals.

Więcej informacji zawiera Zigbee Modules Power Distribution .

Zigbee Modules Memory

RP controller expansion Zigbee modules have two types of memory, flash memory and RAM.

Więcej informacji zawiera Zigbee Modules Memory .

Zigbee 0-10V Module Supported Building Standards

The Zigbee 0-10V module supports 0-10 V lighting control according to the current sinking standards.

Zigbee Modules Wireless Connectivity

The RP controller expansion Zigbee modules are Zigbee Certified Products. The Zigbee modules' wireless connectivity option is used for connecting to and communicating with the RP controller.

Więcej informacji zawiera Zigbee Modules Wireless Connectivity .

Zigbee Modules Screw Terminals

The RP controller expansion Zigbee modules have fixed screw terminals for the power input, power output, and light output.

Więcej informacji zawiera Zigbee Modules Screw Terminals .

Zigbee Modules LED

There is one LED on the front panel of the RP controller expansion Zigbee modules.

Więcej informacji zawiera Zigbee Modules LED .

Zigbee Modules Reset Button

The RP controller expansion Zigbee modules have a Reset button on the front.

Więcej informacji zawiera Zigbee Modules Reset Button .

Zigbee Modules Device Installation

The RP controller expansion Zigbee modules are designed to be installed on a flat surface on a ceiling.

Więcej informacji zawiera Zigbee Modules Device Installation .

Wiring

The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, BACnet/IP devices, RP controller expansion modules, and Operator Display.

Więcej informacji zawiera Wiring .

BACnet/IP Device Firmware Management

Using WorkStation, you can update the firmware of multiple BACnet/IP devices and their attached SpaceLogic Sensor devices and RP controller expansion modules at the same time with minimum downtime. In particular, the universal upgrade package simplifies the update process and requires minimal user involvement and coordination.

Uwaga

SpaceLogic Sensor devices and RP controller expansion modules are supported by the RP controller.

Więcej informacji zawiera BACnet/IP Device Firmware Management .

Zigbee Modules Regulatory Compliance and Approvals

This section provides information on regulatory compliance and approvals for the RP controller expansion Zigbee modules.

Więcej informacji zawiera Zigbee Modules Regulatory Compliance and Approvals .

Dane techniczne

AC input
Nominal voltage
230 VAC
Rated voltage range
220 to 240 VAC
Frequency
50/60 Hz
Maximum load current
5 A
Maximum power consumption
<1 W
Power input protection
MOV suppression and internal fuse
AC output
Rated voltage range
220 to 240 VAC (same as power supply)
Maximum load current
5 A
Maximum inrush current
30 A (<5 ms)
Wireless connectivity
Communication protocol
Zigbee 3.0
Frequency band
2.4 GHz (ISM band), compliant with IEEE Standard 802.15.4
Maximum output power
7 dBm
Effective indoor radio signal range
30 m (98 ft)
Antenna
Integrated antenna
Environment
Ambient temperature, operating
-20 °C to +50 °C (-4 °F to +122 °F)
Case temperature, maximum
75 °C (167 °F)
Ambient temperature, storage
-30 to +65 °C (-22 to +149 °F)
Humidity
Maximum 85 % RH non-condensing
Material
Plastic flame rating
UL94 V-0
Ingress protection rating
IP 20
Mechanical
Dimensions
155 W x 44 H x 30 D mm (6.1 W x 1.7 H x 1.2 D in.)
Weight
0.126 kg (0.278 lb)
Installation
Ceiling
  
Indoor use only
Output terminals
Fixed
  
Left side: 1 x 6-pin terminal block
  
Right side: 1 x 2-pin terminal block
Hardware
CPU type
ARM Cortex-M4 single-core
Frequency
40 MHz
SRAM (embedded)
64 KB
Flash memory (embedded)
512 KB
NOR flash memory
1 MB
Status indicator
LED (green and red) that shows the status of the device
Reset button
Push-button switch
0-10V light output
Outputs
1, terminals 0-10V AO and COM
Output voltage
0 to 10 VDC
Sink current
40 mA
  • Hardware Overview
  • RP Controller Expansion Zigbee Modules
  • Zigbee 0-10V Light Output and Power Output
  • Zigbee Modules Power Distribution
  • Zigbee Modules Memory
  • Zigbee Modules Wireless Connectivity
  • Zigbee Modules Screw Terminals
  • Zigbee Modules LED
  • Zigbee Modules Reset Button
  • Zigbee Modules Device Installation
  • Wiring
  • BACnet/IP Device Firmware Management
  • Zigbee Modules Regulatory Compliance and Approvals