The Zigbee 0-10V module has one 0-10V analog output for control (dimming) of lights with electronic ballasts, LED drivers, and other 0-10V compatible control gear and one power output for power distribution to the control gear.
The Zigbee 0-10V module supports:
0-10V lighting control
Power distribution (220–240 VAC)
The 0-10V light output has two screw terminals for 0-10V lighting control:
0-10V AO (Analog Output)
COM (Common)
The control signal is a DC voltage that varies between 0 V and 10 V. The Zigbee 0-10V module supports the current sinking standard.
The maximum number of control gear devices per module and per output is determined by the module's power distribution limitations. For more information, see section “Specifications”.
The power distribution capability means that the module distributes the AC mains voltage (220–240 VAC) from the Power Input to the control gear connected to the Power Output. Więcej informacji zawiera Zigbee Modules Power Distribution .
The Power Output has three screw terminals for power distribution:
N (out) – Neutral
L (out) – Line
The module uses a relay to control the power distribution, by connecting or disconnecting the AC mains voltage to the Power Output's L (out) terminal. In the figure above, the relay is named K1.
The module's AC mains voltage side and low-voltage side (SELV side) are galvanically separated by means of isolation circuitry.
The module's energy metering circuitry is reserved for future use (power consumption monitoring).
0-10V light output | |
Outputs
|
1, terminals 0-10V AO and COM
|
Output voltage
|
0 to 10 VDC
|
Sink current
|
40 mA
|
Power input | |
Nominal voltage
|
230 VAC
|
Rated voltage range
|
220 to 240 VAC
|
Frequency
|
50/60 Hz
|
Maximum load current
|
5 A
|
Maximum power consumption
|
<1 W
|
Power input protection
|
MOV suppression and internal fuse
|
Power output | |
Rated voltage range
|
220 to 240 VAC (same as power supply)
|
Maximum load current
|
5 A
|
Maximum inrush current
|
30 A (<5 ms)
|