The RP-C-EXT-ZB-0-10V Zigbee 0-10V module communicates with the RP-C room controller over the Zigbee TM wireless protocol and provides I/O expansion for 0-10V lighting control.
The Zigbee 0-10V module enables dimming of different types of lights equipped with electrical ballasts for 220–240 VAC line voltage. The Zigbee 0-10V module can distribute power (220–240 VAC) from an external power supply to the lights.
The Zigbee 0-10V module has one 0-10V analog output for control (dimming) of lights with electronic ballasts, LED drivers, and other 0-10V compatible control gear and one power output for power distribution to the control gear.
Более подробную информацию см. Zigbee 0-10V Light Output and Power Output .
The RP controller expansion Zigbee modules have power distribution capability, which means that the module distributes the AC mains voltage (220–240 VAC) from the Power Input terminals to the light control gear connected to the Power Output terminals.
Более подробную информацию см. Zigbee Modules Power Distribution .
RP controller expansion Zigbee modules can measure and monitor the power consumption for the loads connected to the module.
Более подробную информацию см. Zigbee Modules Power Consumption Monitoring .
RP controller expansion Zigbee modules have two types of memory, flash memory and RAM.
Более подробную информацию см. Zigbee Modules Memory .
The Zigbee 0-10V module supports 0-10 V lighting control according to the current sinking standards.
The RP controller expansion Zigbee modules are Zigbee Certified Products. The Zigbee modules' wireless connectivity option is used for connecting to and communicating with the RP controller.
Более подробную информацию см. Zigbee Modules Wireless Connectivity .
The RP controller expansion Zigbee modules have fixed screw terminals for the power input, power output, and light output.
Более подробную информацию см. Zigbee Modules Screw Terminals .
There is one LED on the front panel of the RP controller expansion Zigbee modules.
Более подробную информацию см. Zigbee Modules LED .
The RP controller expansion Zigbee modules have a Reset button on the front.
Более подробную информацию см. Zigbee Modules Reset Button .
The RP controller expansion Zigbee modules are designed to be installed on a flat surface on a ceiling.
Более подробную информацию см. Zigbee Modules Device Installation .
The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, BACnet/IP devices, RP controller expansion modules, and Operator Display.
Более подробную информацию см. Wiring .
Using WorkStation, you can update the firmware of multiple BACnet/IP devices and their attached SpaceLogic Sensor devices and RP controller expansion modules at the same time with minimum downtime. In particular, the universal upgrade package simplifies the update process and requires minimal user involvement and coordination.
SpaceLogic Sensor devices and RP controller expansion modules are supported by the RP controller.
Более подробную информацию см. BACnet/IP Device Firmware Management .
This section provides information on regulatory compliance and approvals for the RP controller expansion Zigbee modules.
Более подробную информацию см. Zigbee Modules Regulatory Compliance and Approvals .
AC input | |||||||
Nominal voltage
|
230 VAC
|
||||||
Rated voltage range
|
220 to 240 VAC
|
||||||
Frequency
|
50/60 Hz
|
||||||
Maximum load current
|
5 A
|
||||||
Maximum power consumption
|
<1 W
|
||||||
Power input protection
|
MOV suppression and internal fuse
|
||||||
AC output | |||||||
Rated voltage range
|
220 to 240 VAC (same as power supply)
|
||||||
Maximum load current
|
5 A
|
||||||
Maximum inrush current
|
30 A (<5 ms)
|
||||||
Wireless connectivity | |||||||
Communication protocol
|
Zigbee 3.0
|
||||||
Frequency band
|
2.4 GHz (ISM band), compliant with IEEE Standard 802.15.4
|
||||||
Maximum output power
|
7 dBm
|
||||||
Effective indoor radio signal range
|
30 m (98 ft)
|
||||||
Antenna
|
Integrated antenna
|
||||||
Environment | |||||||
Ambient temperature, operating
|
-20 °C to +50 °C (-4 °F to +122 °F)
|
||||||
Case temperature, maximum
|
75 °C (167 °F)
|
||||||
Ambient temperature, storage
|
-30 to +65 °C (-22 to +149 °F)
|
||||||
Humidity
|
Maximum 85 % RH non-condensing
|
||||||
Material | |||||||
Plastic flame rating
|
UL94 V-0
|
||||||
Ingress protection rating
|
IP 20
|
||||||
Mechanical | |||||||
Dimensions
|
155 W x 44 H x 30 D mm (6.1 W x 1.7 H x 1.2 D in.)
|
||||||
Weight
|
0.126 kg (0.278 lb)
|
||||||
Installation
|
Ceiling
|
||||||
Indoor use only
|
|||||||
Output terminals
|
Fixed
|
||||||
Left side: 1 x 6-pin terminal block
|
|||||||
Right side: 1 x 2-pin terminal block
|
|||||||
Hardware | |||||||
CPU type
|
ARM Cortex-M4 single-core
|
||||||
Frequency
|
40 MHz
|
||||||
SRAM (embedded)
|
64 KB
|
||||||
Flash memory (embedded)
|
512 KB
|
||||||
NOR flash memory
|
1 MB
|
||||||
Status indicator
|
LED (green and red) that shows the status of the device
|
||||||
Reset button
|
Push-button switch
|
||||||
Energy metering | |||||||
Measurement accuracy
|
See table below.
|
||||||
|
|||||||
0-10V light output | |||||||
Outputs
|
1, terminals 0-10V AO and COM
|
||||||
Output voltage
|
0 to 10 VDC
|
||||||
Sink current
|
40 mA
|