The RP-C-EXT-REL-4 relay module connects to the RP-C room controllers and enables power supply and control of lights.
The relay module is part of the RP controller expansion modules for connected room solution and can be combined with other modules from this product range.
The RP-C-EXT-REL-4 relay module has four Relay outputs, which are designed for power supply and control of lights.
Mer information finns i Relay Outputs on RP-C-EXT-REL-4 .
The RP controller expansion modules have digital inputs that can be used for sensing of dry contacts:
The light modules, blind modules, and the RP-C-EXT-REL-4 relay module have four digital inputs, which can be used in applications such as interfacing with light switches and window contacts.
The CRS-HH-REL-10 relay module has 12 digital inputs suitable for dry contact monitoring of switches and push buttons used for lighting control, window and door positions, and other functions in the hotel room.
Mer information finns i RP Controller Expansion Module Digital Inputs .
RP controller expansion modules with power distribution capability support energy metering, which means that the module can measure the electrical energy consumption and power demand for the equipment connected to and supplied by the module.
Mer information finns i RP Controller Expansion Module Energy Metering .
RP controller expansion modules and multi-sensor have two types of memory, flash memory and RAM.
Mer information finns i RP Controller Expansion Module and Multi-sensor Memory .
The RP controller expansion modules and multi-sensors have two room bus ports (RJ45 receptacles), which enable connection to the RP-C controller and other expansion modules and multi-sensors on the room bus through a daisy-chain configuration.
Mer information finns i RP-C Room Bus .
Each RP controller expansion module and multi-sensor has a rotary switch, which is used to give the device a unique address on the room bus.
Mer information finns i RP-C Room Bus .
The RP-C room bus allows RP controller expansion modules and multi-sensors to be connected to the controller for motion detection, luminosity measurements, communication with remote control (RP-C-RC-BLE), and control of electric lights and window blinds.
Mer information finns i RP-C Room Bus .
The RP controller expansion modules have PCB mounted connectors for the power input, outputs, and digital inputs. The PCB mounted connectors mate with pluggable connectors:
The light modules, blind modules, and the RP-C-EXT-REL-4 relay module have mechanically keyed and color-coded connectors, which allows the matching external connectors to be plugged in on site quickly and easily.
The CRS-HH-REL-10 relay module has PCB header connectors for pluggable screw terminal blocks, which are easy to install and remove from the device.
Mer information finns i RP Controller Expansion Module Pluggable Connectors .
There is one or more LEDs on the front panel of the RP controller expansion modules.
Mer information finns i RP Controller Expansion Module LEDs .
All RP controller expansion modules have a Set button on the front. The Set button is reserved for future use.
Mer information finns i RP Controller Expansion Module Set Button .
The RP controller expansion module can be installed on a DIN rail or other flat surface inside a cabinet. The device is recommended to be installed in a cabinet, unless local regulations allow an exception.
Mer information finns i RP Controller Expansion Module Device Installation .
The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, BACnet/IP devices, RP controller expansion modules, and Operator Display.
Mer information finns i Wiring .
The RP controller expansion modules and multi-sensors support different modes that can be used for maintenance purposes.
Mer information finns i RP Controller Expansion Module and Multi-sensor Maintenance Modes .
Using WorkStation, you can update the firmware of multiple BACnet/IP devices and their attached SpaceLogic Sensor devices and RP controller expansion modules at the same time with minimum downtime. In particular, the universal upgrade package simplifies the update process and requires minimal user involvement and coordination.
SpaceLogic Sensor devices and RP controller expansion modules are supported by the RP controller.
Mer information finns i BACnet/IP Device Firmware Management .
This section provides information on regulatory compliance and approvals for the RP controller expansion modules.
Mer information finns i RP Controller Expansion Modules Regulatory Compliance and Approvals .
Electrical | |
Nominal voltage
|
100 to 277 VAC
|
Operating voltage range
|
+/-10 %
|
Frequency
|
50/60 Hz
|
Maximum current consumption
|
10 A
|
Room bus power consumption
|
0.3 W (24 VDC)
|
Protection
|
Maximum 16 A external fuse (circuit breaker) is needed
|
Overvoltage category
|
III
|
Environment | |
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
Ambient temperature, storage
|
-20 to +70 °C (-4 to +158 °F)
|
Humidity
|
20 to 90 % RH non-condensing
|
Pollution degree
|
2
|
Material | |
Plastic flame rating
|
UL94 V-0
|
Ingress protection rating
|
IP 20
|
Mechanical | |
Dimensions
|
198 W x 110 H x 64 D mm (7.8 W x 4.3 H x 2.5 D in.)
|
|
|
Weight
|
0.378 kg (0.833 lb)
|
Recommended installation
|
DIN rail or flat surface in a cabinet
a
|
a) It is recommended to install the device in an enclosure (cabinet), unless local regulations allow an exception. | |
Connectors
|
Power input: 1 x 3-pin Wieland GST15i3 connector
|
Relay outputs: 4 x 3-pin Wieland GST15i3 connector
|
|
Digital inputs: 4 x 2-pin Wieland GST15i2 connector
|
|
Communication ports | |
Room bus
|
RS-485
|
Dual RJ45 ports for daisy-chain configurations
|
|
Use a Cat 5 (or higher) cable
|
|
Maximum total length of the room bus: 72 m (236 ft)
|
|
Room bus protection
|
Transient voltage suppressors on communication and power signals
|
Hardware | |
CPU type
|
ARM Cortex-M4 single-core
|
Frequency
|
80 MHz
|
SRAM (embedded)
|
320 KB
|
Flash memory (embedded)
|
512 KB
|
NOR flash memory
|
16 MB
|
Status indicator
|
LED (green and red) that shows the status of the device
|
Relay status indicator
|
One status LED (green) for each output
|
Address switch
|
Rotary switch 0 to 9
|
Set button
|
Push-button switch
|
Energy metering | |
Energy consumption measurement | |
The energy consumption is measured in Wh, shared by the four outputs. | |
Voltage range
|
230 to 277 VAC +/-10 %
|
Accuracy class (according to IEC 61557-12)
|
Active energy measurement: Class 1
|
Typical measurement accuracy at room temperature
|
20 to 100 W: 5%
|
100 to 3000 W: 1%
|
|
Relay outputs | |
Relay outputs for lights powered by 100 to 277 VAC. | |
Outputs
|
4, Relay 1 to Relay 4
|
Output terminals
|
N, PE, and L
|
Power distribution
|
100 to 277 VAC (same voltage as power supply)
|
Maximum 5 A load per output
|
|
Maximum 10 A total load for the 4 outputs
|
|
Maximum 165 A inrush current (<20 ms) per output
|
|
Maximum 800 A inrush current (<200 µs) per output
|
|
Digital inputs | |
Inputs
|
4, DI1 to DI4
|
Range
|
Dry contact, 0 to 5.0 VDC, 2.2 mA, SELV (Safety Extra-Low Voltage)
|
The RP-C-EXT-REL-4 internal configuration with regards to the signal ground is shown in the following figure.