The RP controller Modbus RTU (RS-485) subnetwork allows standard Modbus devices and the KNX Modbus gateway (RP-C-EXT-KNX) to be connected to the controller.
For the KNX Modbus gateway, the RP-C controller provides both 24 VDC power supply and communications through the Modbus network connection.
For standard Modbus devices, a separate power supply unit (PSU) is needed to power the Modbus devices on the network.
The Modbus RTU protocol is used for the communication. The RP-C controller acts the Modbus master and the connected devices act as slaves.
The Modbus communication parameters can be freely configured regardless of which RS-485 port on the RP-C controller that is used for the Modbus network. Mer information finns i RP-C Communication Ports .
The maximum total length of the Modbus (RS-485) network is 72 m (236 ft). The Modbus network uses a Cat 5 (or higher) unshielded, straight-through wired cable with eight conductors (four twisted pairs) and RJ45 connectors. The wire size (cross-sectional area) should be 22 to 26 AWG (0.34 to 0.14 mm²). When the RP-C controller is installed in a space that handles conditioned air or return air, the Modbus network cables and IP network cables frequently must be plenum-rated to meet applicable building codes. Mer information finns i Wiring .
You need to configure which RS-485 (RJ45) port on the RP-C controller to use for the Modbus network. You can configure to use either the Sensor Bus port (RS-485 Com A) or Room Bus port (RS-485 Com B). Mer information finns i RP-C Communication Ports .
The maximum number of Modbus devices that can be connected to an RP-C controller depends on the type of Modbus device and the number of Modbus registers.
The maximum number of Modbus registers that can be connected to and managed by an RP-C controller depends on the communication capacity of the controller's Modbus network.
The RP-C Modbus network supports up to 10 connected Modbus devices with the following restrictions:
Maximum of one KNX Modbus gateway (RP-C-EXT-KNX)
Maximum of 250 Modbus registers per network
The RP controller Modbus network does not support 64-bit Modbus registers.
The KNX Modbus gateway has the default Modbus address 1. The address can be configured through the ETS. Mer information finns i Configuring the Modbus Device Settings in the KNX Modbus Gateway .