Wiring the Screw Terminals on an RS-485 Power Adapter for Connection of an External 24 VDC Supply

You wire the screw terminals on an RS-485 Power Adapter to connect the adapter to an external 24 VDC power supply. Always use the recommended wires (or wires with larger cross-sectional area).

Mostra di più
action_close

The RS-485 Power Adapter can be used for injecting 24 VDC from an external 24 VDC power supply to an RS-485 based network such as Room Bus or Sensor Bus. This is useful, for example, in applications where you want to extend the RS-485 bus by connecting (daisy-chaining) additional devices, which the RP or MP controller would otherwise not be able to power. The external power supply is connected to the bus via the adapter.

Avviso

Before use, check the required ratings for the external 24 VDC power supply. Per maggior informazioni, consulta RS-485 Power Adapter .

Examples

This section gives an example of how the adapter can be used to inject 24 VDC to an RS-485 bus for extension of the bus when more devices than the allowed limit need to be connected:

  • Example with Sensor Bus for an MP-V controller

Example with Sensor Bus for an MP-V controller

The following figure shows an example of how an RS-485 Power Adapter is used to inject 24 VDC from an external 24 VDC power supply to an MP-V controller Sensor Bus so that the maximum number of SpaceLogic Sensor devices with sensor bases with CO 2 option can be increased from two to four devices. Per maggior informazioni, consulta MP-V Sensor Bus .The adapter is typically placed after the second device on the bus where it is used to power the third and fourth devices. The adapter is connected to the Sensor Bus by means of two Cat 5 (or higher) UTP cables (not included). The isolated, non-grounded (floating) 24 VDC output from the external power supply is connected to the screw terminals marked 24 VDC and GND on the adapter.

 
action_zoom_plus_stroke Example with an RS-485 Power Adapter and an external 24 VDC power supply used to extend an MP-V controller Sensor Bus to four SpaceLogic Sensors with CO
Figura: Example with an RS-485 Power Adapter and an external 24 VDC power supply used to extend an MP-V controller Sensor Bus to four SpaceLogic Sensors with CO

 
action_zoom_plus_stroke
The negative terminal (–) on the external 24 VDC power supply should not be connected to local ground. The isolated (floating) 24 VDC output from the power supply should be connected to the GND (–) and 24 VDC (+) terminals on the adapter.

Connection of RJ45 Ports to RP or MP Controller RS-485 Com Port and RS-485 Bus

Separate connection cables are required to connect the two RJ45 ports on the RS-485 Power Adapter to the RS-485 Com port (RJ45) on the RP or MP controller and to other daisy-chained devices with RJ45 interface on the RS-485 bus. The cables are not included and need to be purchased separately.

Use a Cat 5 (or higher) unshielded, straight-through wired cable with eight conductors (four twisted pairs) and RJ45 connectors. Use a cable with the wire size (cross-sectional area) 22 to 26 AWG (0.34 to 0.14 mm²), and a rating that meets the requirements of the target environment. For example, when devices are installed in a space that handles conditioned air or return air, the cables typically need to be plenum-rated.

Avviso

LOSS OF COMMUNICATION

Use a Cat 5 or higher unshielded twisted pair cable with eight conductors (four twisted pairs), a cross-sectional area of 22 to 26 AWG (0.34 to 0.14 mm 2 ), and a rating that meets the requirements of the target environment.

Failure to follow these instructions can result in loss of communication.

Avviso

LOSS OF COMMUNICATION

Ensure that the total length of the RS-485 bus does not exceed the following limits:

  • Room Bus and Modbus: 72 m (236 ft)

  • Sensor Bus: 61 m (200 ft)

Failure to follow these instructions can result in loss of communication.

Per maggior informazioni, consulta Connecting an RS-485 Power Adapter to an External Power Supply to Inject 24 VDC to an RS-485 Bus .

Per maggior informazioni, consulta Communication Port Wiring .

Per maggior informazioni, consulta RJ45 Pinout for the RS-485 Port(s) of the RP-C Controllers .

Per maggior informazioni, consulta RJ45 Pinout for the RS-485 Port of the MP-V Controller .

Wiring of Screw Terminals for Connection to External 24 VDC Power Supply

Avviso

The external power supply should have an isolated, non-grounded (floating) 24 VDC output.

Avviso

It is recommended to move the slide switch on the adapter to the EXT (External) position before connecting the external 24 VDC power supply.

The four screw terminals are wired and connected to an external 24 VDC power supply as described in the following table.

Recommended screw tightening torque: 0.5 Nm (4.5 lbf.in)

Tabella: Screw Terminals, RS-485 Power Adapter, Connection to External 24 VDC Power Supply

Terminal

Usage

24 VDC

Connection to positive terminal (+) on the external 24 VDC power supply.

TX/RX+

Not connected.

TX/RX–

Not connected.

GND

Connection to negative terminal (–) on the external 24 VDC power supply.

The negative terminal (–) on the power supply should not be connected to local ground.

Per maggior informazioni, consulta Wiring the Screw Terminals on an RS-485 Power Adapter for Connection of an External 24 VDC Supply .

Per maggior informazioni, consulta RS-485 Communications .

Avviso

Before use, check the required ratings for the external 24 VDC power supply. Per maggior informazioni, consulta RS-485 Power Adapter .

To wire the screw terminals on an RS-485 Power Adapter for connection of an external 24 VDC Supply
  1. Move the slide switch on the adapter to the 24 VDC EXT position.

     
    action_zoom_plus_stroke
  2. Loosen the screw of the terminal.

  3. Strip approximately 7 mm (0.3 inch) of the insulation from the end of each wire.

  4. Insert the end of the wire fully into its intended terminal. Ensure that no bare wire strands extend from the terminal.

  5. Tighten the screw using a small flat-blade screwdriver. Ensure that the screw is fully tightened. Use the following recommended screw tightening torque: 0.5 Nm (4.5 lbf.in).

  6. Repeat steps 2 to 5 until all screw terminals on the adapter are correctly wired. Per maggior informazioni, consulta Enable Injection of 24 VDC from an External Power Supply to an RS-485 Bus .

    Avviso

    The external power supply should have an isolated, non-grounded (floating) 24 VDC output.

     
    action_zoom_plus_stroke
  7. Use appropriate cable strain relief methods, to help prevent any load applied to the cable from being transferred to conductor terminations.

    You can use the anchor points on the adapter enclosure and cable ties to fasten and fix the cables.

     
    action_zoom_plus_stroke
  • RS-485 Power Adapter
  • Enable Injection of 24 VDC from an External Power Supply to an RS-485 Bus
  • Connecting an RS-485 Power Adapter to an External Power Supply to Inject 24 VDC to an RS-485 Bus
  • Installing an RS-485 Power Adapter
  • Wiring
  • RS-485 Communications