The AS-P-L-3 model has four removable screw terminal blocks, one for the power input and two for RS-485 serial communications, and one for LonWorks communications.
Recommended screw tightening torque: 0.56 Nm (5 lbf.in)
    The removable screw terminal blocks are used as follows:
One 3-position terminal block for the power input
One 4-position terminal block for the RS-485 Com A port
One 3-position terminal block for the RS-485 Com B port
One 3-position terminal block for the LON TP/FT port
| 
 Terminal number  | 
 Designation  | 
 Usage  | 
| 
 Power input  | 
 
  | 
 
  | 
| 
 1  | 
 L/+  | 
 Line (L) lead when operating the device from 24 VAC  
    Positive (+) lead when operating the device from 24-30 VDC  
     | 
| 
 2  | 
 N/–  | 
 Neutral (N) lead when operating the device from 24 VAC  
    Negative (–) lead when operating the device from 24-30 VDC  
     | 
| 
 3  | 
 
  
     | 
 Functional earth ground  | 
| 
 RS-485 Com A  | 
 
  | 
 
  | 
| 
 4  | 
 TX/RX +  | 
 RS-485 communication  | 
| 
 5  | 
 TX/RX –  | 
 RS-485 communication  | 
| 
 6  | 
 RET  | 
 Internally connected to terminal 3 (functional earth ground)  | 
| 
 7  | 
 Bias +  | 
 5.0 VDC, RS-485 bias supply, current limited 40 mA  | 
| 
 RS-485 Com B  | 
 
  | 
 
  | 
| 
 8  | 
 TX/RX +  | 
 RS-485 communication  | 
| 
 9  | 
 TX/RX –  | 
 RS-485 communication  | 
| 
 10  | 
 RET  | 
 Internally connected to terminal 3 (functional earth ground)  | 
| 
 LON TP/FT  | 
 
  | 
 
  | 
| 
 11  | 
 LON-2  | 
 TP/FT-10 Free topology LonWorks network, 78 kbps  | 
| 
 12  | 
 LON-1  | 
 TP/FT-10 Free topology LonWorks network, 78 kbps  | 
| 
 13  | 
 RET  | 
 Internally connected to terminal 3 (functional earth ground)  | 
The screw terminals 4 to 10, intended for RS-485 communication, act as connectors to the automation server and are easily inserted/removed without disrupting the network. Doing so may help in isolating possible RS-485 communication problems.