earth_america
user_standard Iniciar sesión
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Explicación de procesos

Explicación de procesos


Productos AS-B, Enterprise Central, Enterprise Server, AS-P, WorkStation, Project Configuration Tool
Funcionalidades: Programaciones
Versión del producto: 3.2, 3.3, 2022
15/10/2020

Creating an Analog Schedule

You create an analog schedule to control the state of an analog value.

Mostrar más
action_close

An analog schedule controls a device that gauges the output in real numbers. The real numbers include positive or negative numbers, fractions, and decimal values.

For example, you can create an analog schedule to regulate a thermostat setpoint in an office area. To control the temperature from 08:00 to 17:00, you can set the value to 22 °C (72 °F) when the schedule is active and 16 °C (62 °F) when the schedule is inactive.

 
action_zoom_plus_stroke Analog Schedule
Figura: Analog Schedule

To create an analog schedule
  1. In WorkStation, in the System Tree pane, select the EcoStruxure BMS server or the folder.

  2. On the File menu, point to New and then click Schedule .

  3. In the Create Object wizard, in the object type list, select Analog Schedule .

  4. In the Name box, type a name for the schedule.

  5. In the Description box, type a description for the schedule.

  6. Click Create .

Now you can add events to the analog schedule and bind the schedule to an analog value.

  • Schedule Types
  • Analog Schedules
  • Binding an Analog Value to an Analog Schedule
  • Adding a Weekly Event
  • Adding a Calendar Exception Event
  • Cómo añadir un evento de excepción de calendario
  • Adding a Date Range Exception Event
  • Adding a Calculated Exception Event
  • Create Object Dialog – Naming the Object Page