earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Specifications

Specifications


Products: RP-C
Functionalities: Engineering, Hardware
Product version: 2024
12/18/2024

SpaceLogic RP-C Pro Plus

 
action_zoom_plus_stroke RP-C-16C-F-230V
Figure: RP-C-16C-F-230V

Introduction

SpaceLogic™ RP-C Pro Plus is a high-power, fully programmable, IP based field controller that offers a multi-room connectivity hub for Connected Room Solutions.

The controller comes with pluggable connectors, with ability to distribute 24 VAC/DC power, as well as greater memory space for large room and luxury suite applications.

RP-C Pro Plus is a 230 VAC controller with 16 I/O points and can be mounted directly on ceilings without the need for an enclosure.

The controller is integrated into Connected Room Solutions and EcoStruxure Building Operation and is positioned for room control as well as well-being, comfort of occupants in an energy-efficient way.

The controller can either be used as a standalone BACnet/IP field controller, BACnet/SC node, or as part of an EcoStruxure BMS with a SpaceLogic AS-P or AS-B server or an Enterprise Server as the parent server.

The controller features a wireless chip, which enables commissioning of the controller with the Commission mobile application and allows tenants to change the room comfort settings using their smartphones with the Engage mobile application.

Web services enable web access directly to the controller, making the controller an open IoT hub in the room or space area.

RP-C Pro Plus has the following features:

  • IP enabled with dual-port Ethernet switch

  • BACnet/SC node

  • Controller model for 230 VAC with 16 I/O points

  • Versatile onboard I/O point mix

  • Option to use external or internal power supply for power distribution

  • Pluggable connectors for quick and easy installation in suspended ceilings

  • Wireless connectivity

  • Advanced monitoring

  • Three configurable RS-485 ports

  • Sensor bus for living space sensors

  • Room bus for Connected Room Solutions

  • Modbus RTU subnetwork

  • KNX support (KNX Modbus gateway required)

  • Engage mobile application for room comfort settings

  • Commission mobile application for commissioning of the controller before the BMS is in place

  • Full EcoStruxure Building Operation software support, providing efficient engineering tools

  • Web services through RESTful API

IP connectivity, flexible network topologies, and support for BACnet/SC applications

The BACnet/IP controllers are based on open protocols that simplify interoperability, IP configuration, and device management, and can be enabled as BACnet/SC nodes for increased cybersecurity:

  • IP addressing

  • BACnet/IP or BACnet/SC communications

  • DHCP for easy network configuration

The BACnet/IP controllers have a dual-port Ethernet switch, which enables flexible network topologies:

  • Star

  • Daisy chain

  • Rapid Spanning Tree Protocol (RSTP) ring

In a star topology, the controller and the parent EcoStruxure BMS server are individually connected to an Ethernet switch. Daisy-chain multiple controllers together to reduce installation time and cost. When using a ring network topology, in the event of a broken IP network or a non-operational controller, RSTP will enable rapid identification of the location of the detected error while maintaining communication with the controllers on either side of the break.

BACnet/SC (Secure Connect) support

The BACnet/IP controllers support BACnet/SC applications as a BACnet/SC node. This allows the controllers to be used in a BACnet/SC network, which allows secure transport of BACnet traffic and information between BACnet/SC devices over private and public networks without the need for BBMDs, VLANs, and VPNs, because the BACnet/SC protocol uses WebSocket technology and TLS 1.3 encryption. In addition, BACnet/SC uses certificate management to help ensure only those devices authorized to be on a BACnet/SC network can operate on that network.

Controller model for 230 VAC with 16 I/O points

The RP-C Pro Plus range includes one RP controller model, RP-C-16C-F-230V, which offers a set of I/O point types named 16C, and supports 230 VAC power supply.

 
action_zoom_plus_stroke

Fully programmable

The fully programmable RP controller provides flexibility through support of both Script and Function Block programming options. The controller promotes efficiency and standardization through the use of standard controller applications.

Versatile mix of I/O points

RP-C-16C-F-230V provides 16 I/O points, consisting of four different sets of I/O point types. The versatile mix of I/O point types match a wide variety of applications. The universal inputs/outputs are highly flexible and can be configured as either inputs or outputs.

Table: I/O Point Types

I/O Point Types

RP-C-16C-F-230V

Universal I/O (Type Ub)

4

Solid-state relay (SSR) outputs (MOSFET)

4 a

Universal I/O (Type Ub) or SSR outputs (MOSFET) b

8 b

  1. With 24 VAC/DC power distribution
  2. Configurable I/O point type that can be configured either as Universal I/O (Type Ub) or SSR output. When a configurable I/O point is configured as an Universal I/O (Type Ub), the SSR output is enabled and feeds 24 VAC/VDC power, but the SSR output can not be configured or used according to table “Configurations by I/O Point Types”.

Table: Configurations by I/O Point Types

Configurations

Universal I/O

Type Ub

Solid-state Relay Outputs

(MOSFET)

Digital inputs

yes

-

Counter inputs

yes

-

Supervised inputs

yes

-

Voltage inputs

(0 to 10 VDC)

yes

-

Current inputs

(0 to 20 mA)

yes

-

Temperature inputs

yes

-

Resistive inputs

yes

-

2-wire RTD temperature inputs

yes

-

Voltage outputs

(0 to 10 VDC)

yes

-

Digital outputs

-

yes

Digital pulsed outputs

-

yes

PWM outputs

-

yes

Tristate outputs

-

yes

Tristate pulsed outputs

-

yes

Universal inputs/outputs

The universal inputs/outputs are ideal for any mix of temperature, pressure, flow, status points, and similar point types in a building control system.

As counter inputs, the universal inputs/outputs are commonly used in energy metering applications. As RTD inputs, they are ideal for temperature points in a building control system. As supervised inputs, they are used for security applications where it is critical to know whether or not a wire has been cut or shorted. These events provide a separate indication of alarms and events in the system.

For all analog inputs, maximum and minimum levels can be defined to automatically detect over-range and under-range values.

The universal inputs/outputs are capable of supporting analog outputs of type voltage outputs. Therefore, the universal inputs/outputs support a wide range of devices, such as actuators.

Only devices with safe extra low voltage equipment (SELV/PELV) inputs/outputs should be connected to the universal inputs/outputs.

Solid-state relay outputs

The solid-state relay (SSR) outputs can be used in many applications to switch 24 VAC or 24 VDC on or off for external loads such as actuators, relays, or indicators. SSRs are silent and are not adversely affected by relay contact wear.

Option to use external or internal power supply for power distribution

The controller offers the ability to chose between an external power supply (24 VAC/DC, 8 A) or the internal transformer (24 VAC, 19 VA) for power distribution to the solid-state relay outputs. The choice is easily made by placing a jumper on a pin header.

Pluggable connectors

The controller is equipped with PCB mounted connectors for the 230 VAC power input, the I/Os, and the power input for an external power supply. The PCB mounted connectors mate with pluggable connectors. This means time savings and cost reductions for the installation, compared to wiring terminal blocks on site. The connectors can quickly and easily be plugged together on site. The pluggable connectors can be installed without strain relief and touch protection. As there is no need for an enclosure, the controller is suitable for retrofit applications and installation in suspended ceilings or underfloor spaces.

Wireless connectivity

The RP controller is a Bluetooth Low Energy (BLE) enabled product. You can use this wireless connectivity option to connect the controller with a smartphone or tablet running the Commission mobile application or the Engage mobile application for room comfort settings.

Through Wireless Adapter - Advanced connected to the host USB port, Zigbee TM wireless connectivity can be enabled for the RP controller. The controller can extend its point count through the Zigbee wireless network and bring flexibility in your applications. The RP controller equipped with the adapter is a Zigbee Certified Product that is compliant with Zigbee 3.0. For more information on the adapter and supported wireless devices, see the Wireless Adapter - Advanced Specification Sheet.

Advanced monitoring

The BACnet/IP controllers support local trends, schedules, and alarms, enabling local operation when the controller is offline or used in standalone applications.

The battery-free power backup of the memory and real-time clock helps prevent data loss and allows seamless and quick recovery after a power disruption.

In WorkStation, you update the firmware of multiple BACnet/IP controllers at the same time and with minimum down time. The EcoStruxure BMS server keeps track of the installed firmware to support backup, restore, and replacement of the controllers and sensors. The server can host controllers of different firmware versions.

Three configurable RS-485 ports

The controller has three configurable RS-485 ports, which can be configured to support three different types of networks:

  • Sensor bus

  • Room bus

  • Modbus network

The controller can host three networks, but only one of each network type.

Sensor bus for living space sensors

The BACnet/IP controllers provide an interface designed for the SpaceLogic Sensor family of living space sensors. The SpaceLogic Sensor devices offer an efficient way to sense the temperature, humidity, CO 2 , and occupancy in a room. The SpaceLogic Sensor devices are available with different combinations of sensor types and various covers and user interface options, such as touchscreen, setpoint and override buttons, and blank covers.

 
action_zoom_plus_stroke SpaceLogic Sensor devices
Figure: SpaceLogic Sensor devices

The RP controller sensor bus provides both power and communications for up to four sensors that are daisy-chained using standard Cat 5 (or higher) cables. This maximum number of sensors that can be connected to a controller is regardless of the sensor model and the combination of cover and sensor base type:

  • Blank covers: Up to four sensors of any combination of sensor base types

  • 3-button and touchscreen covers: Up to four sensors of any combination of sensor base types

  • SpaceLogic LCD temperature sensors: Up to four sensors are supported

The maximum total length of the sensor bus is 61 m (200 ft). For more information, see the SpaceLogic Sensors - SXWS Sensors for MP and RP IP Controllers - Specification Sheet.

The RS-485 Power Adapter can be used for injecting 24 VDC from an external 24 VDC power supply to the bus. For more information, see the RS-485 Adapters Specification Sheet.

Room bus for Connected Room Solutions

The RP controller room bus allows RP controller expansion modules to be connected to the controller for people counting, motion detection, luminosity and sound pressure level measurements, Bluetooth Low Energy based applications, and control of electric lights and window blinds.

The RP-C Pro and RP-C Pro Plus controller room bus supports up to nine connected RP controller expansion modules with the following restrictions:

  • Maximum of two DALI light modules

  • Maximum of two SMI blind modules

  • Maximum of seven Multi-sensor or Insight-Sensor devices

Maximum total length of the room bus is 72 m (236 ft).

The RS-485 Power Adapter can be used for injecting 24 VDC from an external 24 VDC power supply to the bus. For more information, see the RS-485 Adapters Specification Sheet.

For more information, see the Specification Sheets for the RP controller expansion modules.

Modbus RTU subnetwork

The RP controller Modbus network allows standard Modbus devices and the KNX Modbus gateway (RP-C-EXT-KNX) to be connected to the controller.

The Modbus RTU protocol is used for the communication. The RP controller acts as the Modbus client and the connected devices act as servers.

For connection to Modbus devices, it is recommended to use the non-isolated RS-485 adapter to provide screw termination. The adapter converts an RS-485 RJ45 interface to screw terminals. The adapter can be ordered from Schneider Electric. For more information, see the RS-485 Adapters Specification Sheet.

To connect the adapter, it is recommended that you use a Cat 5 (or higher) UTP cable with eight conductors and RJ45 connectors. The cable should be rated for the target environment and have a maximum length of 0.3 m (12 in.). The cable is not included and needs to be purchased separately.

The maximum number of Modbus devices that can be connected to an RP controller depends on the type of Modbus device and the number of Modbus registers.

The RP-C Pro Plus controller Modbus network supports up to 20 connected Modbus devices with the following restrictions:

  • Maximum of one KNX Modbus gateway (RP-C-EXT-KNX)

  • Maximum of 1,000 Modbus registers per network

64-bit Modbus registers are supported, which can be used in energy metering.

Modbus device types

Modbus device types are pre-configured Modbus applications for quick and easy Modbus device integration in EcoStruxure Building Operation solutions. For information on the Modbus devices supported using Modbus device types, see the document EcoStruxure Building - Modbus Device Integration - Supported Device Brochure.

KNX support

Through the KNX Modbus gateway (RP-C-EXT-KNX), the RP controller can communicate with KNX devices such as push-buttons and sensors.

The KNX Modbus gateway provides a KNX to Modbus interface that connects to one of the RP controller's configurable RS-485 ports.

For more information, see the RP-C-EXT-KNX Specification Sheet.

Engage mobile application

The Engage mobile application enables control of room temperature, fan speed, lights, and blinds/shades directly from a smartphone. A user can manage these settings when the application is connected to the RP controller.

The Engage mobile application is free and available for download from Google Play and Apple App Store.

For more information, see the Engage Specification Sheet.

Commission mobile application

The Commission mobile application is designed for local configuration, field deployment, and commissioning of BACnet/IP controllers. The mobile application reduces the commissioning time, allows flexibility in project execution, and minimizes dependencies on network infrastructure.

The mobile application is designed for use with Android, Apple (iOS), and Microsoft Windows 10 and Windows 11 devices. For more information, see the EcoStruxure Building Commission Specification Sheet.

 
action_zoom_plus_stroke Commission mobile application
Figure: Commission mobile application

Using the Commission mobile application, you can connect to one or many RP controllers. You can connect to a single RP controller using the controller's built-in Bluetooth connectivity or using the SpaceLogic Bluetooth Adapter connected to a SpaceLogic Sensor. Using a wireless access point or a network switch, you can connect to a network of RP controllers on the local IP network.

Device configuration

With the Commission mobile application, you can easily discover BACnet/IP controllers on the IP network. You can change the configuration of each controller, including the BACnet and IP network settings, location, and parent server. To save engineering time, you can save common device settings and then reuse them for controllers of the same model.

Field deployment and I/O checkout

The Commission mobile application does not require an EcoStruxure BMS server or a network infrastructure to be in place. You can use the mobile application to load the controller application directly into the local BACnet/IP controller and deploy the controller. The controller application can be created offline using Project Configuration Tool or WorkStation. You can use the mobile application to change the behavior of an installed standard controller application, such as configuring temperature setpoints. You can also perform an I/O checkout to verify that the controller's I/O points are configured, wired, and operating correctly.

You can perform I/O checkout on the RP controller room bus to verify proper communication over the room bus between the RP controller and the associated RP controller expansion modules. Module type mismatches or address mismatches can then be resolved. After wiring the physical inputs and outputs of the RP controller expansion modules, you can perform the following tasks on the different modules:

  • DALI light modules: discover, wink, and associate DALI lights with the logical software points, and test individual lights

  • 0-10V light modules: test individual lights

  • Blind modules: calibrate and test blinds

  • Relay module: test outputs

Full EcoStruxure Building Operation software support

The power of the RP controller is fully realized when it is part of an EcoStruxure BMS, which provides the following benefits:

  • WorkStation/WebStation interface

  • Script and Function Block programming options

  • Device discovery

  • Engineering efficiency

  • Preconfigured BMS applications for HVAC and Connected Room Solutions

  • Zoning option

WorkStation/WebStation interface

WorkStation and WebStation provide a consistent user experience regardless of which EcoStruxure BMS server the user is logged on to. The user can log on to the parent EcoStruxure BMS server to engineer, commission, supervise, and monitor the BACnet/IP controller and its I/O as well as its attached SpaceLogic Sensor devices. For more information, see the WorkStation and WebStation specification sheets.

Script and Function Block programming options

The fully programmable RP and MP controller models have both Script and Function Block programming options. Existing programs can easily be reused between the EcoStruxure BMS server and the controller.

Device discovery

The enhanced Device Discovery in WorkStation enables you to easily identify BACnet/IP controllers on a BACnet network and to associate the controllers with their parent server.

Engineering efficiency

The engineering and maintenance of BACnet/IP controllers can be done very efficiently using the EcoStruxure Building Operation reusability features. With these features, you can create library items (Custom Types) for a complete controller application that contains programs and all necessary objects such as trends, alarms, and schedules. The controller application in the Custom Types library is reusable across all controllers of the same model. You can use the controller application as a base for creating new controllers intended for similar applications. You can then edit the controller application, and the changes are automatically replicated to all controllers, while each controller keeps its local values.

WorkStation supports both online and offline engineering of BACnet/IP controllers. You can make the configuration changes online or use database mode to make the changes offline. In database mode, the changes are saved to the EcoStruxure Building Operation database so that you can apply the changes to the controllers later.

Project Configuration Tool enables you to perform all the engineering off site, without the need for physical hardware, which minimizes the time you need to spend on site. You can run the EcoStruxure BMS servers virtually and engineer the BACnet/IP controllers before you deploy your server and controller applications to the servers and controllers on site. For more information, see the Project Configuration Tool specification sheet.

Preconfigured BMS applications for HVAC and Connected Room Solutions

To improve engineering efficiency and standardize engineering practices, fully designed and tested controller applications are available at bms-applications.schneider-electric.com for use with the RP controllers. This library contains applications for different RP controller models and application types, such as fan coil units, ceiling solutions, lights and blinds. These preconfigured controller applications are packages that include all software programs, and for example graphics, alarms, and documentation such as functional specifications and I/O wiring schedules, that are needed for your projects. The online repository can be accessed using common web browsers on Windows PCs as well as mobile devices running Apple iOS 11.3 (or later) and Android 6.0 Marshmallow (or later).

 
action_zoom_plus_stroke Download page for preconfigured BMS applications
Figure: Download page for preconfigured BMS applications
Zoning option

The Zoning option for WorkStation and WebStation provides access to an interactive zoning tool that enables easy reconfiguration of Connected Room Solutions and flexibility when switching between zones. The WebStation zoning tool provides a graphical interface that enables quick editing of zones from any web browser device.

The RP-C-16C-F-230V model supports up to eight segments, which can be used to support rezoning in a building.

Web services

The RP controller uses the RESTful API, which allows IT web services to easily interact with software applications. The flexibility of the RESTful API allows the RP controller to handle multiple types of input and return different data formats. With Web services, clients can read/write data (BACnet values) directly from/to the controller. Web services use resource methods GET, PUT, POST, and DELETE to access and use the data. HTTPS is used for communication between the client and the controller.

The Web services function is disabled by default. When enabled, it requires approximately 200 kB of RP controller memory.

Table: Part Number for RP-C Pro Plus

Product

Part number

RP-C-16C-F-230V
SXWRCF16C10001

Table: Part Numbers for RP-C Accessories

Product

Part number

DIN-RAIL-CLIP, DIN-rail end clip
package of 25 pieces
SXWDINEND10001
Mounting plate - RP-C Pro Plus
package of 5 pieces
SXWRCMPK510001
Non-isolated RS-485 adapter
SXWNISORS48510001
RS-485 power adapter
SXWNISORS485P10001
SpaceLogic Wireless Adapter - Advanced
SXWZBAUSB10001
SpaceLogic Bluetooth Adapter
SXWBTAECXX10001
Spare jumper
Samtec SNT-100-BK-G-H

For more information on part numbers for Network Connectivity Accessories, see the For more information, see Product Selection Guide - EcoStruxure Building ..

Specifications

AC input
Nominal voltage
230 VAC
Operating voltage range
+/-10 %
Frequency
50/60 Hz
Maximum power consumption
65 VA
Power consumption without load
5 W
Power input protection
MOV suppression and internal fuse
  
Separate PTC thermistor used as a resettable fuse for the SSR outputs (DO1 to DO12) only
Overvoltage category
III
Pollution degree
2
24 VAC/VDC input (EXT Input) for external power supply to SSR outputs
AC voltage range
Maximum 30 VAC
DC voltage range
Maximum 30 VDC
EXT Input negative terminal (–), AC voltage range
0 to 30 VAC
EXT Input negative terminal (–), DC voltage range
-30 to +30 VDC
Maximum current consumption
8 A
Internal transformer for power supply to SSR outputs
Type
Isolated Class 2 output
Nominal voltage
24 VAC
Frequency
Same frequency as the power supply (50/60 Hz)
Output power rating
19 VA
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F) at normal operation
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic flame rating
UL94 V-0
Ingress protection rating
IP 20
Mechanical
Dimensions
306 W x 110 H x 64 D mm (12.0 W x 4.3 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight
0.968 kg (2.134 lb)
Recommended installation
DIN rail or flat surface
Connectors
Power input: 1 x 3-pin Wieland GST15i3 connector
  
External input, 24 VAC/VDC: 1 x 2-pin Wieland GST15i2 connector
  
SSR outputs: 4 x 2-pin Wieland GST15i2 connector
  
Universal I/Os: 4 x 2-pin Wieland GST15i2 connector
  
SSR outputs or Universal IOs: 8 x 4-pin Wieland GST15i4 connector
Optional mounting plate
The mounting plate is used to facilitate mounting and cable management for the RP-C Pro Plus controller as well as to provide strain relief for the connectors.
Dimensions
310 W x 268.3 H x 17.8 D mm (12.2 W x 10.6 H x 0.7 D in.)
 
action_zoom_plus_stroke
Weight
0.458 kg (1.01 lb)
Compatibility
EcoStruxure BMS server communication
EcoStruxure Building Operation
version 5.0.1 and later
BACnet/SC network support
EcoStruxure Building Operation
version 6.0.1 and later
Agency compliances
Emission
RCM; BS/EN 61000-6-3; BS/EN IEC 63044-5-2
Immunity
BS/EN 61000-6-2; BS/EN IEC 63044-5-3
Radio
ETSI EN 300 328 V2.2.2
Safety standards
BS/EN 60730-1; BS/EN 60730-2-11; BS/EN IEC 63044-3
Real-time clock
Accuracy, at 25 °C (77 °F)
+/-1 minute per month
Backup time, at 25 °C (77 °F)
7 days minimum
Communication ports
Ethernet
Dual 10/100BASE-TX (RJ45), IEEE 802.3 compliant
USB
1 USB 2.0 host port (type-A), 5 VDC, 2.5 W
RS-485 port Com A
24 VDC, 3 W, RS-485 (RJ45)
  
Transient voltage suppressors on communication and power signals
RS-485 port Com B
24 VDC, 3 W, RS-485 (RJ45)
  
Transient voltage suppressors on communication and power signals
RS-485 port Com C
24 VDC, 3 W, RS-485 (RJ45)
  
Transient voltage suppressors on communication and power signals
RS-485 transceiver characteristics
Transceiver type
Failsafe
  
Non-isolated
External biasing
None required
Total Unit Load (UL) per device
Maximum 0.5 UL
Communications
BACnet
BACnet/IP, port configurable, default 47808
  
BACnet/SC, port configurable, no default port
  
BTL B-AAC (BACnet Advanced Application Controller), B-GW (BACnet Gateway) a
Wireless connectivity
Bluetooth Low Energy
Communication protocol
Bluetooth ® 5.1 Low Energy compliant
Frequency
2.402 to 2.480 GHz
Maximum output power
10 dBm
Maximum communication distance
Line-of-sight: 100 m (328 ft)
Antenna
Integrated antenna
RF connector for optional external antenna
SMA connector
External antenna (optional)
Restricted to the approved antenna type listed below (used in certification)

Manufacturer

Model (Part number)

Gain

Type

Impedance

Linx Technologies

ANT-2.4-WRT-MON-SMA

0.8 dBi

Monopole

50 ohm

CPU
Frequency
500 MHz
Type
ARM Cortex-A7 dual-core
DDR3 SDRAM
128 MB
NOR flash memory
64 MB
Memory backup
128 kB, FRAM, non-volatile
Universal inputs/outputs
Channels
4, Ub9 to Ub12
Absolute maximum ratings
-0.5 to +24 VDC
A/D converter resolution
16 bits
Universal input/output protection
Transient voltage suppressor on each universal input/output
Digital inputs
Range
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
Minimum pulse width
150 ms
Counter inputs
Range
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
Minimum pulse width
20 ms
Maximum frequency
25 Hz
Supervised inputs
5 V circuit, 1 or 2 resistors
Monitored switch combinations
Series only, parallel only, and series and parallel
Resistor range
1 to 10 kohm
For a 2-resistor configuration, each resistor must have the same value +/- 5 %
Voltage inputs
Range
0 to 10 VDC
Accuracy
+/-(7 mV + 0.2 % of reading)
Resolution
1.0 mV
Impedance
1 Mohm
Current inputs
Range
0 to 20 mA
Accuracy
+/-(0.01 mA + 0.4 % of reading)
Resolution
1 μA
Impedance
47 ohm
Resistive inputs
10 ohm to 10 kohm accuracy
+/-(7 + 4 x 10 -3 x R) ohm
R = Resistance in ohm
10 kohm to 60 kohm accuracy
+/-(4 x 10 -3 x R + 7 x 10 -8 x R 2 ) ohm
R = Resistance in ohm
Temperature inputs (thermistors)
Range
-50 to +150 °C (-58 to +302 °F)
Supported thermistors
Honeywell
20 kohm
Type I (Continuum)
10 kohm
Type II (I/NET)
10 kohm
Type III (Satchwell)
10 kohm
Type IV (FD)
10 kohm
Type V (FD w/ 11k shunt)
Linearized 10 kohm
Satchwell D?T
Linearized 10 kohm
Johnson Controls
2.2 kohm
Xenta
1.8 kohm
Balco
1 kohm
Measurement accuracy
20 kohm
-50 to -30 °C: +/-1.5 °C (-58 to -22 °F: +/-2.7 °F)
  
-30 to 0 °C: +/-0.5 °C (-22 to +32 °F: +/-0.9 °F)
  
0 to 100 °C: +/-0.2 °C (32 to 212 °F: +/-0.4 °F)
  
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F)
10 kohm, 2.2 kohm, and 1.8 kohm
-50 to -30 °C: +/-0.75 °C (-58 to -22 °F: +/-1.35 °F)
  
-30 to +100 °C: +/-0.2 °C (-22 to +212 °F: +/-0.4 °F)
  
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F)
Linearized 10 kohm
-50 to -30 °C: +/-2.0 °C (-58 to -22 °F: +/-3.6 °F)
  
-30 to 0 °C: +/-0.75 °C (-22 to +32 °F: +/-1.35 °F)
  
0 to 100 °C: +/-0.2 °C (32 to 212 °F: +/-0.4 °F)
  
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F)
1 kohm
-50 to +150 °C: +/-1.0 °C (-58 to +302° F: +/-1.8 °F)
RTD temperature inputs
Supported RTDs
Pt1000, Ni1000, and LG-Ni1000
Pt1000
Sensor range
-50 to +150 °C (-58 to +302 °F)

BACnet/IP device environment

Sensor range

Measurement accuracy

0 to 50 °C (32 to 122 °F)

-50 to +70 °C (-58 to +158 °F)

+/-0.5 °C (+/-0.9 °F)

0 to 50 °C (32 to 122 °F)

70 to 150 °C (158 to 302 °F)

+/-0.7 °C (+/-1.3 °F)

-40 to +60 °C (-40 to +140 °F)

-50 to +150 °C (-58 to +302 °F)

+/-1.0 °C (+/-1.8 °F)

Ni1000
Sensor range
-50 to +150 °C (-58 to +302 °F)

BACnet/IP device environment

Sensor range

Measurement accuracy

0 to 50 °C (32 to 122 °F)

-50 to +150 °C (-58 to +302 °F)

+/-0.5 °C (+/-0.9 °F)

-40 to +60 °C (-40 to +140 °F)

-50 to +150 °C (-58 to +302 °F)

+/-0.5 °C (+/-0.9 °F)

LG-Ni1000
Sensor range
-50 to +150 °C (-58 to +302 °F)

BACnet/IP device environment

Sensor range

Measurement accuracy

0 to 50 °C (32 to 122 °F)

-50 to +150 °C (-58 to +302 °F)

+/-0.5 °C (+/-0.9 °F)

-40 to +60 °C (-40 to +140 °F)

-50 to +150 °C (-58 to +302 °F)

+/-0.5 °C (+/-0.9 °F)

RTD temperature wiring
Maximum wire resistance
20 ohm/wire (40 ohm total)
Maximum wire capacitance
60 nF
The wire resistance and capacitance typically corresponds to a 200 m wire.
Voltage outputs
Range
0 to 10 VDC
Accuracy
+/-60 mV
Resolution
10 mV
Minimum load resistance
2.4 kohm
Source current
+4.2 mA
Sink current
-1 mA (0 to 0.4 VDC)
  
-4.2 mA (0.4 to 10 VDC)
Solid-state relay outputs, DO
Channels
4, DO9 to DO12
Output rating
Maximum 2 A load for the “C” group of 2 outputs
  
Maximum 2 A load for the “D” group of 2 outputs
Minimum pulse width
100 ms
Solid-state relay output protection
Transient voltage suppressor across each solid-state relay (SSR) output
Configurable solid-state relay outputs or universal inputs/outputs
Channels
8 configurable SSR outputs (DO) or universal inputs/outputs (Ub)
Universal inputs/outputs
The specifications for the configurable universal inputs/outputs Ub1 to Ub8 are the same as for Ub9 to Ub12, with the exception for the number of channels. For information on the common specifications, see section “Universal inputs/outputs” above.
Channels
8, Ub1 to Ub8
Solid-state relay outputs
The specifications for the configurable solid-state relay outputs DO1 to DO8 are the same as for DO9 to DO12, with the exception for the number of channels and the output rating. For information on the common specifications, see section “Solid-state relay outputs, DO” above.
Channels
8, DO1 to DO8
Output rating
Maximum 2 A load for the “A” group of 4 outputs
  
Maximum 2 A load for the “B” group of 4 outputs

Connections

For more information on wiring, see the SpaceLogic Hardware Reference Guide.

 
action_zoom_plus_stroke RP-C-16C-F-230V
Figure: RP-C-16C-F-230V

Table: Required External Connectors

Use

Part number

Reference

Connector type

Suitable for cable diameters

mm (inches)

Marking

Color of coding

/housing

Minimum order quantity

Power supply input

SXWRPCCONWWPOW

91.931.4053.1

Female, 3-pole

5.6–11

(0.22–0.43)

L, PE, N

Black

/Black

100

External input, 24 VAC / VDC

SXWRPCCONPOWIP

91.921.3053.0

Female, 2-pole

6–7.7

(0.24–0.30)

L, N

White

/White

100

SSR outputs (DO), 24 VAC / VDC

SXWRPCCONDCOP

91.922.3053.0

Male, 2-pole

6–7.7

(0.24–0.30)

L, N

White

/White

100

Universal I/O (Ub)

SXWRPCCONWWLIGHT2

91.922.3353.0

Male, 2-pole

6–7.7

(0.24–0.30)

2, 1

Light blue

/White

100

Configurable SSR outputs (DO) or Universal I/O (Ub)

SXWRPCCONUIO

91.942.4650.0

Male, 4-pole

6.5–12

(0.26–0.47)

1, 2, 3, 4/N

Turquoise blue

/White

100

The external connectors need to be ordered separately. The connectors can be ordered in quantities of 100 from Schneider Electric using the above part numbers. The connectors can also be ordered directly from Wieland using the above reference numbers. For more information, see the Wieland Electric web site.

Table: Part Numbers for SpaceLogic Sensor Devices, Sensor Bases

Product

Part number

Sensor base with temperature sensor

SXWSBTXXXSXX

Sensor base with temperature and humidity sensors

SXWSBTHXXSXX

Sensor base with temperature and CO 2 sensors

SXWSBTXCXSXX

Sensor base with temperature, humidity, and CO 2 sensors

SXWSBTHCXSXX

Table: Part Numbers for SpaceLogic Sensor Devices, Covers

Product

Housing

Part number

Blank cover

Medium matte white

SXWSCBXSELXX

Blank cover

Optimum glass white

SXWSCBXSELXW

Blank cover

Optimum glass black

SXWSCBXSELXB

Blank cover with occupancy sensor

Medium matte white

SXWSCBPSELXX

Blank cover with occupancy sensor

Optimum glass white

SXWSCBPSELXW

Blank cover with occupancy sensor

Optimum glass black

SXWSCBPSELXB

3-button cover

Medium matte white

SXWSC3XSELXX

3-button cover

Optimum glass white

SXWSC3XSELXW

3-button cover

Optimum glass black

SXWSC3XSELXB

3-button cover with occupancy sensor

Medium matte white

SXWSC3PSELXX

3-button cover with occupancy sensor

Optimum glass white

SXWSC3PSELXW

3-button cover with occupancy sensor

Optimum glass black

SXWSC3PSELXB

Touchscreen display cover

Medium matte white

SXWSCDXSELXX

Touchscreen display cover

Optimum glass white

SXWSCDXSELXW

Touchscreen display cover

Optimum glass black

SXWSCDXSELXB

Touchscreen display cover with occupancy sensor

Medium matte white

SXWSCDPSELXX

Touchscreen display cover with occupancy sensor

Optimum glass white

SXWSCDPSELXW

Touchscreen display cover with occupancy sensor

Optimum glass black

SXWSCDPSELXB

Touchscreen display cover with light control buttons

Optimum glass white

SXWSC2XSELXW

Touchscreen display cover with light control buttons

Optimum glass black

SXWSC2XSELXB

Touchscreen display cover with light control buttons and occupancy sensor

Optimum glass white

SXWSC2PSELXW

Touchscreen display cover with light control buttons and occupancy sensor

Optimum glass black

SXWSC2PSELXB

Touchscreen display cover with light and blind control buttons

Optimum glass white

SXWSC4XSELXW

Touchscreen display cover with light and blind control buttons

Optimum glass black

SXWSC4XSELXB

Touchscreen display cover with light and blind control buttons and occupancy sensor

Optimum glass white

SXWSC4PSELXW

Touchscreen display cover with light and blind control buttons and occupancy sensor

Optimum glass black

SXWSC4PSELXB

Table: Part Numbers for SpaceLogic Sensor Devices, Combination Models

Product

Housing

Part number

Complete SpaceLogic Sensor model with temperature sensor, buttons for override and setpoint control, and LCD display cover

Medium matte white

SXWSATXXXSLX

Complete SpaceLogic Sensor model with temperature sensor, buttons for override and setpoint control, and LCD display cover

Optimum glass white

SXWSATXXXSLW

Complete SpaceLogic Sensor model with temperature sensor, buttons for override and setpoint control, and LCD display cover

Optimum glass black

SXWSATXXXSLB

Complete non-communicating a SpaceLogic Sensor model with resistive temperature sensor (10 kohm type 3 thermistor) and blank cover

Medium matte white

SLASXXX

Complete non-communicating a SpaceLogic Sensor model with resistive temperature sensor (10 kohm type 3 thermistor) and blank cover

Optimum glass white

SLAWXXX

Complete non-communicating a SpaceLogic Sensor model with resistive temperature sensor (10 kohm type 3 thermistor) and blank cover

Optimum glass black

SLABXXX

  1. The SpaceLogic resistive temperature sensor (SLA...) is designed to be connected to I/O points/terminals on RP or MP controllers, or I/O modules. The sensor requires an analog input (temperature input).
  • Enterprise Server
  • SpaceLogic AS-P
  • SpaceLogic AS-B
  • WorkStation
  • WebStation
  • SpaceLogic RP-C-EXT-MS-BLE
  • SpaceLogic RP-C-EXT-IS-BLE
  • SpaceLogic RP-C-EXT-DALI-M-PD
  • SpaceLogic RP-C-EXT-DALI
  • SpaceLogic RP-C-EXT-0-10V-4-PD
  • SpaceLogic RP-C-EXT-0-10V-4
  • SpaceLogic RP-C-EXT-BL-4-HV-PD
  • SpaceLogic RP-C-EXT-BL-2-LV-PD
  • SpaceLogic RP-C-EXT-BL-SMI-4-HV-PD
  • SpaceLogic RP-C-EXT-BL-SMI-2-LV-PD
  • SpaceLogic RP-C-EXT-REL-4
  • SpaceLogic CRS-HH-REL-10
  • Spacelogic RP-C-EXT-KNX
  • SpaceLogic Wireless Adapter - Advanced
  • RP-C-RC-BLE
  • Commission
  • Engage
  • Project Configuration Tool – Version 2
  • Automated Engineering Tool