Concept

Concept


Products: DI-16
Functionalities: Hardware
Product version: 3.3, 2022, 2023, 2024, 7.0, 7.1
12/18/2025

DI-16 Central IO Module

arrow1_rotation Digital inputs arrow1_rotation Specifications

This Central IO module is a digital input, 16-channel I/O module. You can use the digital inputs for sensing of multiple dry contact digital inputs in applications such as equipment status monitoring or alarm point monitoring. As counter inputs, digital inputs are commonly used in energy metering applications.

The following input types are supported:

  • Digital (dry contact, open collector, or open drain)

  • Counter (dry contact, open collector, or open drain)

Each channel has a dedicated two-color (red and green) status LED that provides local monitoring of the input. You can configure the channel status LED for a digital or counter input to display either red or green for each input state. The front panel contains both the I/O channel and module status LEDs.

 
action_zoom_plus_stroke DI-16 Central IO module
Figure: DI-16 Central IO module

Digital inputs

The digital inputs (DI) are designed to read two different types of inputs:

  • Digital

  • Counter

 
action_zoom_plus_stroke Internal configuration
Figure: Internal configuration

Applied voltages beyond the absolute maximum ratings cause over current in the protection component DZ.

The I/O bus in the terminal base provides the Central IO module with power and an address.

The address value in the I/O bus is increased by one for each terminal base. The I/O bus also enables RS-485 communication between the Central IO module and the automation server.

Digital inputs

The external connection of a digital input is shown in the following figure:

 
action_zoom_plus_stroke Digital input external connection
Figure: Digital input external connection

K is the monitored external switch.

VS = 24 V

RPU = 10 kohm

Counter inputs

A counter input uses the same hardware configuration as the digital input that is shown in the figure above.

Specifications

Input channels
16
DC input supply power
1.6 W
DC input supply voltage
24 VDC
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic flame rating
UL94-5VB
Enclosure
PC/ABS
Ingress protection rating
IP 20
Mechanical
Dimensions including terminal base
90 W x 114 H x 64 D mm (3.6 W x 4.5 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight including terminal base TB-IO-W1
0.255 kg (0.56 lb)
Weight including terminal base TB-IO-W1-2
0.284 kg (0.63 lb)
Weight excluding terminal base
0.131 kg (0.29 lb)
Terminal base
TB-IO-W1
  
TB-IO-W1-2
Terminals
 
action_zoom_plus_stroke
All inputs
Range
Dry contact switch closure or open collector/open drain, 24 VDC, 2.4 mA
Absolute maximum ratings
-0.5 to +24 VDC
LED polarity
Software selectable, if the LED is activated when the input is high or low
LED color
Red or green, software selectable
Digital
Minimum pulse width
120 ms
Counter
Minimum pulse width
20 ms
Maximum frequency
25 Hz
  • I/O Modules
  • Input Modules