earth_america
user_standard Iniciar sesión
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concepto

Concepto


Productos MP-V
Funcionalidades: Hardware
Versión del producto: 3.0, 3.1, 3.2
11/03/2021

MP-Vs

SmartX IP Controller – MP-V is a multi-purpose, fully programmable, IP based field controller dedicated for VAV applications. MP-V integrates a controller, a damper actuator, and an air flow sensor in a single package for ease of installation. MP-V is a native SmartX device, which can either be used as a standalone BACnet/IP field controller or as part of an EcoStruxure BMS with a SmartX AS-P or AS-B server, or an Enterprise Server, as the parent server.

MP-V allows for flexible control solutions due to the dual Ethernet ports, the interface to SmartX Sensors, and the mix of universal inputs, triac outputs, and analog outputs.

When MP-Vs are part of an EcoStruxure BMS, you can take full advantage of the existing EcoStruxure Building Operation engineering tools.

 
action_zoom_plus_stroke MP-V
Figura: MP-V

MP-V Models

The MP-V comes in two models with a different I/O point count and different I/O point mix.

Para obtener más información, consulte MP-V Models .

MP-V Onboard I/O

The MP-V models offer a versatile mix of I/O point types that match a wide variety of VAV applications.

Para obtener más información, consulte MP-V Onboard I/O .

MP-V Damper Actuator

The MP-V has an integrated damper actuator, which allows for simplified installation of MP-V directly over the damper shaft.

Para obtener más información, consulte MP-V Damper Actuator .

MP-V Air Flow Sensor

The MP-V uses a digital pressure sensor to measure the air velocity pressure signal from the velocity probe in the inlet of the VAV box. The measured value is used by the controller to position the VAV damper actuator for the required air flow.

Para obtener más información, consulte MP-V Air Flow Sensor .

MP-V Built-in Power Supply

The MP-V has a built-in power supply designed to accommodate 24 VAC at 50/60 Hz input power.

Para obtener más información, consulte MP-V Built-in Power Supply .

SmartX IP Controller Device Memory

SmartX IP Controller devices have three types of memory:

  • Flash memory: for boot loader, operating system, application software, and configuration storage

  • RAM: for runtime operation

  • FRAM non-volatile memory: for data retention in the case of power outage

Para obtener más información, consulte SmartX IP Controller Device Memory .

SmartX IP Controller Supported Building Standards

One of the cornerstones of the EcoStruxure BMS is support for open standards. As a result, the SmartX IP controller complies with the BACnet open standard, one of the most popular standards for buildings.

Para obtener más información, consulte SmartX IP Controller Supported Building Standards .

MP Series Controller Communication Ports

The MP Series controller contains a combination of Ethernet, USB, and SmartX Sensor communication ports.

Para obtener más información, consulte MP Series Controller Communication Ports .

SmartX IP Controller Sensor Bus

The SmartX IP controller provides a sensor bus, which allows SmartX Sensors to be connected to the controller.

Para obtener más información, consulte SmartX IP Controller Sensor Bus .

MP-V Screw Terminals

The MP-V is delivered with terminal blocks installed on the device. The MP-V uses pluggable terminal blocks, which are easy to install and remove from the device.

Para obtener más información, consulte MP-V Screw Terminals .

MP Series Controller LEDs

There are five LEDs on the front panel of the MP Series controller.

Para obtener más información, consulte MP Series Controller LEDs .

MP Series Controller Reset Modes

You can reset and restart the MP Series controllers in different ways depending on how long you press the reset button. The resets and restarts can affect the retention of values after restart based on the retain levels configured for the variables.

Para obtener más información, consulte MP Series Controller Reset Modes .

MP-V Device Installation

The MP-V incorporates an integral actuator and the device is designed for over-the-shaft damper installation.

Para obtener más información, consulte MP-V Device Installation .

Wiring

The wiring recommendations provide guidance regarding wiring of the I/O modules, SmartX servers, and SmartX IP Controller devices.

Para obtener más información, consulte Wiring .

SmartX IP Controller Device Firmware Management

Using WorkStation, you can update the firmware of multiple SmartX IP Controller devices and their attached SmartX Sensors at the same time with minimum downtime. In particular, the universal upgrade package simplifies the update process and requires minimal user involvement and coordination.

Aviso

SmartX Sensors are supported by the SmartX IP Controller - MP and RP Series.

Para obtener más información, consulte SmartX IP Controller Device Firmware Management .

Especificaciones

AC input
Nominal voltage
24 VAC
Operating voltage range
+/- 20 %
Frequency
50/60 Hz
Maximum power consumption (MP-V-7A)
21 VA
Maximum power consumption (MP-V-9A)
22 VA
Power input protection
MOV suppression and internal fuse
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-40 to +70 °C (-40 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic flame rating
UL94 V-0
Ingress protection rating
IP 20
Mechanical
Dimensions
161 W x 198 H x 63 D mm (6.3 W x 7.8 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight
1.13 kg (2.5 lb)
Installation
Over the damper shaft
Terminal blocks
Removable
Real-time clock
Accuracy, at 25 °C (77 °F)
+/-1 minute per month
Backup time, at 25 °C (77 °F)
7 days minimum
Communication ports
Ethernet
Dual 10/100BASE-TX (RJ45)
USB
1 USB 2.0 device port (mini-B)
  
1 USB 2.0 host port (type-A), 5 VDC, 2.5 W
Sensor bus
24 VDC, 2 W, RS-485 (RJ45)
Sensor bus protection
Transient voltage suppressors on communication and power signals
Communications
BACnet
BACnet/IP, port configurable, default 47808
  
BTL B-AAC (BACnet Advanced Application Controller) a
a) See the BTL Product Catalog for up-to-date details on BTL listed firmware revisions on BACnet International's home page.
CPU
Frequency
500 MHz
Type
ARM Cortex-A7 dual-core
DDR3 SDRAM
128 MB
NOR flash memory
32 MB
Memory backup
128 kB, FRAM, non-volatile
Damper actuator
Torque rating
6 Nm (53 lbf.in)
Stroke
0° to 90°, fully adjustable
Timing
Approximately 2 seconds/degree at 60 Hz and 2.4 seconds/degree at 50 Hz for 90° rotation at 24 VAC
Position indication
Visual indication
Damper position feedback
Yes
Manual override
Push-button clutch release
Damper shaft diameter
12.7 mm (0.5 inch) or 9.5 mm (0.375 inch)
  
Adapter kit AM-135 is required for 9.5 mm (0.375 inch) diameter shafts.
Damper shaft minimum length (from VAV box)
22.2 mm (0.875 inch)
Air flow sensor
Range
0 to 249 Pa (0 to 1 inH 2 O)
Resolution
0.33 Pa (0.001 inH 2 O) at 25°C (77°F)
Accuracy
±5% of 249 Pa (1.00 inH 2 O) span at 25°C (77°F)

Internal Configuration

The MP-V internal configuration with regards to the signal ground is shown in the following figure.

 
action_zoom_plus_stroke  MP-V internal configuration
Figura: MP-V internal configuration
  • Hardware Overview
  • MP-V Models
  • MP-V Onboard I/O
  • MP-V Damper Actuator
  • MP-V Air Flow Sensor
  • MP-V Built-in Power Supply
  • SmartX IP Controller Device Memory
  • SmartX IP Controller Supported Building Standards
  • MP Series Controller Communication Ports
  • SmartX IP Controller Sensor Bus
  • MP-V Screw Terminals
  • MP Series Controller LEDs
  • MP Series Controller Reset Modes
  • MP-V Device Installation
  • Wiring
  • SmartX IP Controller Device Firmware Management