earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Products: RP-C, RP-C-EXT-0-10V-4, RP-C-EXT-0-10V-4-PD, RP-C-EXT-BL-2-LV-PD, RP-C-EXT-BL-4-HV-PD, RP-C-EXT-BL-SMI-2-LV-PD, RP-C-EXT-BL-SMI-4-HV-PD, RP-C-EXT-DALI, RP-C-EXT-DALI-M-PD, RP-C-EXT-MS-BLE, RP-C-EXT-REL-4
Functionalities: Hardware
Product version: 3.2
1/19/2021

RP-C Room Bus

The RP-C room bus allows RP Series expansion modules and multi-sensors to be connected to the controller for motion detection, luminosity measurements, communication with remote control (RP-C-RC-BLE), and control of electric lights and window blinds.

The room bus is a proprietary RS-485 bus, which is designed to provide both 24 VDC power supply and communications for the connected modules and multi-sensors.

The maximum total length of the room bus is 72 m (236 ft). The room bus uses a Cat 5 (or higher) unshielded, straight-through wired cable with eight conductors (four twisted pairs) and RJ45 connectors. The wire size (cross-sectional area) should be 22 to 26 AWG (0.34 to 0.14 mm²). When the RP-C controller is installed in a space that handles conditioned air or return air, the room bus cables and IP network cables frequently must be plenum-rated to meet applicable building codes. For more information, see Wiring

Notice

LOSS OF COMMUNICATION

  • Ensure that the total length of the room bus does not exceed 72 m (236 ft).

  • Use a Cat 5 or higher unshielded twisted pair cable with eight conductors (four twisted pairs), a cross-sectional area of 22 to 26 AWG (0.34 to 0.14 mm 2 ), and a rating that meets the requirements of the target environment.

Failure to follow these instructions can result in loss of communication.

By default, the RP-C controller's Room Bus port (RS-485 Com B) is configured and allocated for the room bus. For more information, see RP-C Communication Ports .

 
action_zoom_plus_stroke Location of the Room Bus ports and address switches on the RP-C controllers and RP Series expansion modules and multi-sensors
Figure: Location of the Room Bus ports and address switches on the RP-C controllers and RP Series expansion modules and multi-sensors

You can connect a single RP Series expansion module or multi-sensor to the room bus, or you can connect up to six devices in a daisy-chain configuration.

Note:

When connecting devices to the RP-C room bus through a daisy-chain configuration, it does not matter if the incoming and outgoing cables are connected to one or the other room bus port on the device.

The RP-C room bus supports up to six connected RP Series expansion modules and multi-sensors with the following restrictions:

  • Maximum of two DALI light modules

  • Maximum of two SMI blind modules

  • Maximum of four multi-sensors

 
action_zoom_plus_stroke Example of supported combination of RP Series expansion modules and multi-sensors on the RP-C room bus
Figure: Example of supported combination of RP Series expansion modules and multi-sensors on the RP-C room bus

Each RP Series expansion module and multi-sensor has a rotary switch, which is used to give the device a unique address on the room bus. An RP Series expansion module or multi-sensor can be given any address in the range of 1 to 6. Configuring the address 0 means that the device enters maintenance mode and goes offline. Configuring an address in the range of 7 to 9 also means that the device goes offline. For more information, see RP Series Expansion Module Room Bus Addressing . An incorrectly configured switch can cause two devices to have the same address on the room bus, which means that both devices will be offline.

Notice

LOSS OF COMMUNICATION

Ensure that the rotary switch on the RP Series expansion module or multi-sensor is configured to give the device a unique room bus address in the range of 1 to 6.

Failure to follow these instructions can result in loss of communication.

Table: Room Bus Addresses

Address

Description

0

Maintenance mode. Device offline.

1 to 6

Valid addresses supported by the EcoStruxure Building Operation software.

7 to 9

Reserved for future use. Addresses not supported by the EcoStruxure Building Operation software. Device offline.

Note:

Devices connected to the RP-C room bus through a daisy-chain configuration can be assigned addresses regardless of the order in which the devices appear in the daisy chain. For example, device number 1 can have the address 6, device number 2 can have the address 4, and so on.

Note:

An RP Series expansion module and multi-sensor can be put into different maintenance modes in which the device is either offline or online. For more information, see RP Series Expansion Module and Multi-sensor Maintenance Modes .

  • Hardware Overview
  • RP-Cs
  • Wiring
  • RP-C
  • RP Series Expansion Modules and Multi-sensors
  • Light Modules
  • Blind Modules
  • RP-C-EXT-DALI-M-PD
  • RP-C-EXT-0-10V-4-PD
  • RP-C-EXT-BL-4-HV-PD
  • RP-C-EXT-BL-2-LV-PD
  • RP-C-EXT-DALI
  • RP-C-EXT-0-10V-4
  • RP-C-EXT-BL-SMI-4-HV-PD
  • RP-C-EXT-BL-SMI-2-LV-PD
  • RP-C-EXT-REL-4
  • RP-C-EXT-MS-BLE
  • RP-C Communication Ports
  • Connecting RP Series Expansion Modules and Multi-sensors to RP-C
  • Configuring the Room Bus Address for an RP Series Expansion Module
  • Configuring the Room Bus Address for an RP Series Expansion Multi-sensor
  • RP Series Expansion Module Room Bus Addressing
  • RP Series Expansion Module and Multi-sensor Maintenance Modes