earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Products: RP-C, RP-C-EXT-BL-SMI-4-HV-PD
Functionalities: Hardware
Product version: 3.2
9/1/2020

RP-C-EXT-BL-SMI-4-HV-PD

The RP-C-EXT-BL-SMI-4-HV-PD SMI blind module connects to the RP-C room controllers and provides I/O expansion for control of AC mains-supplied motors (drives) with SMI (Standard Motor Interface for AC applications).

The SMI high-voltage blind module enables control and power supply (230 VAC) of motorized venetian blinds, roller shutters, awnings, and other shade products (typically for exterior use).

The SMI blind module is part of the RP Series expansion modules for connected room solution and can be combined with other modules from this product range.

 
action_zoom_plus_stroke RP-C-EXT-BL-SMI-4-HV-PD – SMI high-voltage blind module
Figure: RP-C-EXT-BL-SMI-4-HV-PD – SMI high-voltage blind module

SMI Blind Outputs

The SMI high-voltage blind modules have four Blind outputs for control of motorized window blinds (drives) that are powered by AC mains voltage (230 VAC). The Standard Motor Interface (SMI), AC version for AC mains-supplied drives, is used to control the blind motors.

For more information, see SMI Blind Outputs .

RP Series Expansion Module Digital Inputs

The RP Series expansion modules have four digital inputs, which can be used for sensing of dry contact digital inputs in applications such as interfacing with light switches and window contacts.

For more information, see RP Series Expansion Module Digital Inputs .

RP Series Expansion Module Built-in Power Supply

The RP Series expansion light modules with power distribution capability, low-voltage blind modules, and SMI blind modules have a built-in power supply that can accommodate a nominal input voltage of 230 VAC at 50/60 Hz. Light modules without power distribution capability can accommodate a nominal input voltage of 100 to 277 VAC at 50/60 Hz.

For more information, see RP Series Expansion Module Built-in Power Supply .

RP Series Expansion Module and Multi-sensor Memory

RP Series expansion modules and multi-sensor have two types of memory, flash memory and RAM.

For more information, see RP Series Expansion Module and Multi-sensor Memory .

SMI Blind Modules Supported Building Standards

The SMI blind modules comply to version 3.0 of the SMI specification.

For more information, see SMI Blind Modules Supported Building Standards .

RP Series Expansion Module and Multi-sensor Communication Ports

The RP Series expansion modules and multi-sensors have two room bus ports (RJ45 receptacles), which enable connection to the RP-C controller and other expansion modules and multi-sensors on the room bus through a daisy-chain configuration.

For more information, see RP-C Room Bus .

RP Series Expansion Module and Multi-sensor Address Switch

Each RP Series expansion module and multi-sensor has a rotary switch, which is used to give the device a unique address on the room bus.

For more information, see RP-C Room Bus .

RP-C Room Bus

The RP-C room bus allows RP Series expansion modules and multi-sensors to be connected to the controller for motion detection, luminosity measurements, communication with remote control (RP-C-RC-BLE), and control of electric lights and window blinds.

For more information, see RP-C Room Bus .

RP Series Expansion Module Pluggable Connectors

The RP Series expansion modules have PCB mounted connectors for the power input, outputs and digital inputs. The connectors are mechanically keyed and color-coded, which allows the matching external connectors to be plugged in on site quickly and easily.

For more information, see RP Series Expansion Module Pluggable Connectors .

RP Series Expansion Module LEDs

There is one or more LEDs on the front panel of the RP Series expansion modules.

For more information, see RP Series Expansion Module LEDs .

RP Series Expansion Module Set Button

All RP Series expansion modules have a Set button on the front. The Set button is reserved for future use.

For more information, see RP Series Expansion Module Set Button .

RP Series Expansion Module Device Installation

The RP Series expansion module can be installed on a DIN rail or flat surface.

For more information, see RP Series Expansion Module Device Installation .

Wiring

The wiring recommendations provide guidance regarding wiring of the I/O modules, SmartX servers, SmartX IP Controller devices, and RP Series expansion modules and multi-sensors.

For more information, see Wiring .

RP Series Expansion Module and Multi-sensor Maintenance Modes

The RP Series expansion modules and multi-sensors support different modes that can be used for maintenance purposes.

For more information, see RP Series Expansion Module and Multi-sensor Maintenance Modes .

SmartX IP Controller Device Firmware Management

Using WorkStation, you can update the firmware of multiple SmartX IP Controller devices and their attached SmartX Sensors, RP Series expansion modules, and multi-sensors at the same time with minimum downtime. In particular, the universal upgrade package simplifies the update process and requires minimal user involvement and coordination.

Tip:

SmartX Sensors, RP Series expansion modules, and multi-sensors are supported by the SmartX IP Controller - RP Series.

For more information, see SmartX IP Controller Device Firmware Management .

RP Series Expansion Module Regulatory Compliance and Approvals

This section provides information on regulatory compliance and approvals for the RP Series expansion modules.

For more information, see RP Series Expansion Modules Regulatory Compliance and Approvals .

Specifications

Electrical
Nominal voltage
230 VAC
Operating voltage range
+/-10 %
Frequency
50/60 Hz
Maximum current consumption
8 A
Room bus power consumption
0.3 W (24 VDC)
Protection
Maximum 16 A external fuse (circuit breaker) is needed
Overvoltage category
III
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Humidity
20 to 90 % RH non-condensing
Pollution degree
2
Material
Plastic flame rating
UL94 V-0
Ingress protection rating
IP 20
Mechanical
Dimensions
198 W x 110 H x 64 D mm (7.8 W x 4.3 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight
0.405 kg (0.893 lb)
Installation
DIN rail or flat surface
Connectors
Power input: 1 x 3-pin Wieland GST15i3 connector
  
Blind outputs: 4 x 5-pin Wieland GST15i5 connector
  
Digital inputs: 4 x 2-pin Wieland GST15i2 connector
Communication ports
Room bus
RS-485
  
Dual RJ45 ports for daisy-chain configurations
  
Use a Cat 5 (or higher) cable
  
Maximum total length of the room bus: 72 m (236 ft)
Room bus protection
Transient voltage suppressors on communication and power signals
Hardware
CPU type
ARM Cortex-M4 single-core
Frequency
80 MHz
SRAM (embedded)
320 KB
Flash memory (embedded)
512 KB
NOR flash memory
16 MB
Status indicator
LED (green and red) that shows the status of the device
Blind status indicator
One status LED (green) for each output
Address switch
Rotary switch 0 to 9
Set button
Push-button switch
Blind outputs
SMI motor control outputs for 230 VAC powered blind motors.
Outputs
4, Blind 1 to Blind 4
Output terminals
N, PE, L, I+, and I-
SMI version
3.0
Number of SMI channels
1
Maximum total number of blind motors (drives)
16
Power distribution
230 VAC (same voltage as power supply)
  
Maximum 2 A load per output
  
Maximum 8 A total load for the 4 outputs
Digital inputs
Inputs
4, DI1 to DI4
Range
Dry contact, 0 to 5.0 VDC, 2.2 mA

Internal Configuration

The RP-C-EXT-BL-SMI-4-HV-PD internal configuration with regards to the signal ground is shown in the following figure.

 
action_zoom_plus_stroke RP-C-EXT-BL-SMI-4-HV-PD internal configuration
Figure: RP-C-EXT-BL-SMI-4-HV-PD internal configuration
  • Hardware Overview
  • RP Series Expansion Modules and Multi-sensors
  • Blind Modules
  • SMI Blind Outputs
  • RP Series Expansion Module Digital Inputs
  • RP Series Expansion Module Built-in Power Supply
  • RP Series Expansion Module and Multi-sensor Memory
  • SMI Blind Modules Supported Building Standards
  • RP-C Room Bus
  • RP Series Expansion Module Pluggable Connectors
  • RP Series Expansion Module LEDs
  • RP Series Expansion Module Set Button
  • RP Series Expansion Module Device Installation
  • Wiring
  • RP Series Expansion Module and Multi-sensor Maintenance Modes
  • SmartX IP Controller Device Firmware Management
  • RP Series Expansion Modules Regulatory Compliance and Approvals