SpaceLogic™ RP-C-EXT-DALI-M-PD light module connects to the SpaceLogic RP room controllers and provides I/O expansion for lighting control with DALI (Digital Addressable Lighting Interface).
DALI 灯控模块可为配备 DALI 电子镇流器(DALI 控制装置)的灯具供电和进行控制。
The DALI light module is a DALI-2 certified control device (application controller) with multi-master capability. DALI-2 compliance means benefits such as improved interoperability and easier installation and maintenance. The DALI light module can be used with DALI version-1 products because DALI-2 is designed to be backward compatible with DALI version-1. The multi-master capability of the DALI light module allows the module to function as a DALI master in a DALI network and can thus work together with DALI-2 sensors and push-buttons.
Lighting can be controlled by the RP controller through motion detection and light intensity measurement provided by the Multi-sensor or Insight-Sensor, or by SpaceLogic Sensors connected to the RP controller.
The DALI light module is part of the RP controller expansion modules for connected room solution and can be combined with other modules from this product range.
DALI 灯控模块具有下述特点:
通过房间总线供电和通信
通过 DALI-2 认证的控制设备(应用控制器)
DALI 多主功能,用于与 DALI 总线上的 DALI 传感器和按钮进行通信,最大限度地降低布线和安装成本
DALI 控制装置的组和单独寻址(灯)
一个 DALI 信道,分为四个输入/输出(端子),用于 DALI 总线电源和多达 32 个灯和 16 个输入设备的控制(每个输入/输出的灯和输入设备的最大数量由最大涌入电流确定)
最多 16 个 DALI 组用于一般灯具控制
总共多达 16 个 DALI 输入设备。每个输入设备最多支持四个传感器或按钮。
简化了连接到同一端子的 DALI 灯的调试支持
当同一终端上的所有灯都熄灭时,自动断开 DALI 驱动器/镇流器的电源,从而节省能源
支持非 DALI 照明控制终端上非 DALI 灯的开/关(继电器)控制
用于连接灯开关和窗户触点的四个数字输入。数字输入为 SELV(安全的弱电信号)
测量每个模块的能耗
适合安装在天花板中
用于快捷安装的 Wieland l连接器
用于房间舒适度设置的 Engage 移动应用程序
显示设备的状态 LED
每个 DALI 输入/输出一个状态 LED
用于地址配置的旋转开关
DALI 输入/输出通过 DALI 灯控模块连接到电源网络。对于 DALI 总线,您可以使用 ELV(超低电压)装置允许的标准安装设备。DALI 总线符合 SELV(安全超低电压)要求。
The DALI-2 interface has the following features:
DALI groups can combine lights regardless of which outputs the lights belong to.
Lights that belong to the same DALI group are controlled simultaneously for switching on/off, dimming, and color temperature (tunable white) adjustment
Management of ballast and lamp alarms
Automatic addressing of lights
通过使用 DALI 通道组,您可以将连接到同一输入/输出(端子)的所有 DALI 灯作为一个逻辑灯控制,这简化并加快了调试过程。
The RP controller room bus allows RP controller expansion modules to be connected to the controller for people counting, motion detection, luminosity and sound pressure level measurements, Bluetooth Low Energy based applications, and control of electric lights and window blinds.
The RP-C Pro and RP-C Pro Plus controller room bus supports up to nine connected RP controller expansion modules with the following restrictions:
Maximum of two DALI light modules
Maximum of two SMI blind modules
Maximum of seven Multi-sensor or Insight-Sensor devices
The RP-C Advanced controller room bus supports up to six connected RP controller expansion modules with the following restrictions:
Maximum of two DALI light modules
Maximum of two SMI blind modules
Maximum of four Multi-sensor or Insight-Sensor devices
The RP-V Advanced controller room bus supports up to four connected RP controller expansion modules with the following restrictions:
Maximum of one DALI light module
Maximum of one SMI blind module
Maximum of two Multi-sensor or Insight-Sensor devices
Maximum total length of the room bus is 72 m (236 ft).
The Engage mobile application enables control of room temperature, fan speed, lights, and blinds/shades directly from a smartphone. A user can manage these settings when the application is connected to the RP controller.
The Engage mobile application is free and available for download from Google Play and Apple App Store.
For more information, see the Engage Specification Sheet.
产品 |
物料号 |
RP-C-EXT-DALI-M-PD
|
SXWREDAMPD10001
|
DIN-RAIL-CLIP, DIN-rail end clip
package of 25 pieces
|
SXWDINEND10001
|
Mounting plate - RP controller expansion modules
package of 5 pieces
|
SXWREMPK510001
|
Electrical | ||||||||||||||||||||||
Nominal voltage
|
230 VAC
|
|||||||||||||||||||||
Operating voltage range
|
+/-10 %
|
|||||||||||||||||||||
Frequency
|
50/60 Hz
|
|||||||||||||||||||||
Maximum current consumption
|
10 A
|
|||||||||||||||||||||
Room bus power consumption
|
0.3 W (24 VDC)
|
|||||||||||||||||||||
Protection
|
Maximum 16 A external fuse (circuit breaker) is needed
|
|||||||||||||||||||||
Overvoltage category
|
III
|
|||||||||||||||||||||
Environment | ||||||||||||||||||||||
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
|||||||||||||||||||||
Ambient temperature, storage
|
-20 to +70 °C (-4 to +158 °F)
|
|||||||||||||||||||||
Humidity
|
20 to 90 % RH non-condensing
|
|||||||||||||||||||||
Pollution degree
|
2
|
|||||||||||||||||||||
Material | ||||||||||||||||||||||
Plastic flame rating
|
UL94 V-0
|
|||||||||||||||||||||
Ingress protection rating
|
IP 20
|
|||||||||||||||||||||
Mechanical | ||||||||||||||||||||||
Dimensions
|
198 W x 110 H x 64 D mm (7.8 W x 4.3 H x 2.5 D in.)
|
|||||||||||||||||||||
|
||||||||||||||||||||||
Weight
|
0.433 kg (0.955 lb)
|
|||||||||||||||||||||
Recommended installation
|
DIN rail or flat surface in a cabinet
a
|
|||||||||||||||||||||
a) It is recommended to install the device in an enclosure (cabinet), unless local regulations allow an exception. | ||||||||||||||||||||||
Connectors
|
Power input: 1 x 3-pin Wieland GST15i3 connector
|
|||||||||||||||||||||
DALI inputs/outputs: 4 x 5-pin Wieland GST15i5 connector
|
||||||||||||||||||||||
Digital inputs: 4 x 2-pin Wieland GST15i2 connector
|
||||||||||||||||||||||
Optional mounting plate | ||||||||||||||||||||||
The mounting plate is used to facilitate mounting and cable management for the RP controller expansion module as well as to provide strain relief for the connectors. | ||||||||||||||||||||||
Dimensions
|
202 W x 268.3 H x 17.8 D mm (8.0 W x 10.6 H x 0.7 D in.)
|
|||||||||||||||||||||
|
||||||||||||||||||||||
Weight
|
0.306 kg (0.675 lb)
|
|||||||||||||||||||||
Compatibility | ||||||||||||||||||||||
EcoStruxure BMS server communication
|
||||||||||||||||||||||
EcoStruxure Building Operation
|
version 3.1.1 and later
|
|||||||||||||||||||||
Energy metering support
|
||||||||||||||||||||||
EcoStruxure Building Operation
|
version 3.3.1 and later
|
|||||||||||||||||||||
DALI multi-master support
|
||||||||||||||||||||||
EcoStruxure Building Operation
|
version 4.0.1 and later
|
|||||||||||||||||||||
Support for simplified commissioning and energy saving for DALI lights, and relay control of non-DALI lights
|
||||||||||||||||||||||
EcoStruxure Building Operation
|
version 5.0.3 and later
|
|||||||||||||||||||||
Agency compliances | ||||||||||||||||||||||
Emission
|
RCM; BS/EN 61000-6-3; BS/EN IEC 63044-5-2; FCC Part 15, Sub-part B, Class B
|
|||||||||||||||||||||
Immunity
|
BS/EN 61000-6-2; BS/EN IEC 63044-5-3
|
|||||||||||||||||||||
Safety standards
|
BS/EN 60730-1; BS/EN 60730-2-11; BS/EN IEC 63044-3
|
|||||||||||||||||||||
Digital addressable lighting interface
|
IEC 62386-101; IEC 62386-103
|
|||||||||||||||||||||
Communication ports | ||||||||||||||||||||||
Room bus
|
RS-485
|
|||||||||||||||||||||
Dual RJ45 ports for daisy-chain configurations
|
||||||||||||||||||||||
Use a Cat 5 (or higher) cable
|
||||||||||||||||||||||
Maximum total length of the room bus: 72 m (236 ft)
|
||||||||||||||||||||||
Room bus protection
|
Transient voltage suppressors on communication and power signals
|
|||||||||||||||||||||
Hardware | ||||||||||||||||||||||
Main microcontroller | ||||||||||||||||||||||
CPU type
|
ARM Cortex-M4 single-core
|
|||||||||||||||||||||
Frequency
|
80 MHz
|
|||||||||||||||||||||
SRAM (embedded)
|
320 KB
|
|||||||||||||||||||||
Flash memory (embedded)
|
1024 KB
|
|||||||||||||||||||||
Memory | ||||||||||||||||||||||
NOR flash memory
|
16 MB
|
|||||||||||||||||||||
DALI microcontroller | ||||||||||||||||||||||
CPU type
|
ARM Cortex-M0 single-core
|
|||||||||||||||||||||
Frequency
|
32 MHz
|
|||||||||||||||||||||
SRAM (embedded)
|
8 KB
|
|||||||||||||||||||||
Flash memory (embedded)
|
64 KB
|
|||||||||||||||||||||
Additional hardware | ||||||||||||||||||||||
Status indicator
|
LED (green and red) that shows the status of the device
|
|||||||||||||||||||||
Light status indicator
|
One status LED (green) for each DALI input/output
|
|||||||||||||||||||||
Address switch
|
Rotary switch 0 to 9
|
|||||||||||||||||||||
Set button
|
Push-button switch
|
|||||||||||||||||||||
Energy metering | ||||||||||||||||||||||
能耗测量 | ||||||||||||||||||||||
The energy consumption is measured in Wh, shared by the four outputs. | ||||||||||||||||||||||
Accuracy class (according to IEC 61557-12)
|
Active energy measurement: Class 1
|
|||||||||||||||||||||
Typical measurement accuracy at room temperature
|
20 to 100 W: 5%
|
|||||||||||||||||||||
100 to 3000 W: 1%
|
||||||||||||||||||||||
DALI inputs/outputs | ||||||||||||||||||||||
Inputs/outputs
|
4, Light 1 to Light 4
|
|||||||||||||||||||||
The four inputs/outputs share one DALI channel. | ||||||||||||||||||||||
Input/output terminals
|
N, PE, L, DA+, and DA-
|
|||||||||||||||||||||
DALI bus voltage
|
18 VDC
|
|||||||||||||||||||||
Maximum supply current
|
250 mA
|
|||||||||||||||||||||
Guaranteed supply current
|
64 mA
|
|||||||||||||||||||||
Maximum cable length
|
See the SpaceLogic Hardware Reference Guide
|
|||||||||||||||||||||
Power distribution
|
230 VAC (same voltage as power supply)
|
|||||||||||||||||||||
Maximum 5 A load per output
|
||||||||||||||||||||||
Maximum 10 A total load for the 4 outputs
|
||||||||||||||||||||||
Maximum 165 A inrush current (<20 ms) per output
|
||||||||||||||||||||||
Maximum 800 A inrush current (<200 µs) per output
|
||||||||||||||||||||||
DALI devices | ||||||||||||||||||||||
Supported control gear
|
See table below.
|
|||||||||||||||||||||
|
||||||||||||||||||||||
a) Color type Tc (Color temperature) of Part 209 of the IEC 62386 standard is supported. | ||||||||||||||||||||||
Supported input device types
|
See table below.
|
|||||||||||||||||||||
|
||||||||||||||||||||||
a) Parts of the IEC 62386 standard. | ||||||||||||||||||||||
b) For a list of supported input devices, see the Product Database on the DiiA website, www.dali-alliance.org | ||||||||||||||||||||||
c) It is recommended to always test an input device at an early stage in a project. | ||||||||||||||||||||||
Digital inputs | ||||||||||||||||||||||
Inputs
|
4, DI1 to DI4
|
|||||||||||||||||||||
Range
|
Dry contact, 0 to 5.0 VDC, 2.2 mA, SELV (Safety Extra-Low Voltage)
|
Follow proper installation wiring diagrams and instructions. For more information on wiring, see the SpaceLogic Hardware Reference Guide.
Use |
Part number |
Reference |
Connector type |
Suitable for cable diameters mm (inches) |
Marking |
Color of coding /housing |
Minimum order quantity |
Power supply input |
SXWRPCCONWWPOW |
91.931.4053.1 |
Female |
5.6–11 (0.22–0.43) |
L, PE, N |
Black /Black |
100 |
DALI inputs/outputs |
SXWRPCCONWWLIGHTPD |
91.952.4453.0 |
Male |
8.5–12.5 (0.34–0.49) |
N, PE, L, D2, D1 D2: DA+ D1: DA- |
Pastel blue /White |
50 |
Digital inputs |
SXWRPCCONWDI |
91.921.2353.0 |
Female |
3.4–5.5 (0.14–0.21) |
1, 2 1: DI1..4 2: RET |
Light blue /White |
100 |
The external connectors need to be ordered separately. The connectors can be ordered in quantities of 50 or 100 from Schneider Electric using the above part numbers. The connectors can also be ordered directly from Wieland using the above reference numbers. For more information, see the Wieland Electric web site.