产品: RP-C, RP-C-EXT-BL-SMI-2-LV-PD
功能: 硬件
产品版本: 2022, 2023, 2024, 7.0
2023/10/6

RP-C-EXT-BL-SMI-2-LV-PD

The RP-C-EXT-BL-SMI-2-LV-PD SMI blind module connects to the RP-C room controllers and provides I/O expansion for control of DC low-voltage motors (drives) with SMI LoVo (Standard Motor Interface for low-voltage applications).

The SMI low-voltage blind module enables control and power supply (24 VDC) of motorized venetian blinds, roller blinds, pleated blinds, and other shade products (typically for interior use).

The SMI blind module is part of the RP controller expansion modules for connected room solution and can be combined with other modules from this product range.

 
action_zoom_plus_stroke RP-C-EXT-BL-SMI-2-LV-PD – SMI low-voltage blind module
图: RP-C-EXT-BL-SMI-2-LV-PD – SMI low-voltage blind module

SMI LoVo Blind Outputs

The SMI low-voltage blind modules have two Blind outputs for control of motorized window blinds (drives) that are powered by 24 VDC. The Standard Motor Interface (SMI), LoVo version for DC low-voltage drives, is used to control the blind motors.

有关更多信息,请参阅 SMI LoVo Blind Outputs .

RP Controller Expansion Module Digital Inputs

The RP controller expansion modules have digital inputs that can be used for sensing of dry contacts:

  • The light modules, blind modules, and the RP-C-EXT-REL-4 relay module have four digital inputs, which can be used in applications such as interfacing with light switches and window contacts.

  • The CRS-HH-REL-10 relay module has 12 digital inputs suitable for dry contact monitoring of switches and push buttons used for lighting control, window and door positions, and other functions in the hotel room.

有关更多信息,请参阅 RP Controller Expansion Module Digital Inputs .

RP Controller Expansion Module Built-in Power Supply

The RP controller expansion light modules with power distribution capability, low-voltage blind modules, and SMI blind modules have a built-in power supply that can accommodate a nominal input voltage of 230 VAC at 50/60 Hz. Light modules without power distribution capability can accommodate a nominal input voltage of 100 to 277 VAC at 50/60 Hz.

有关更多信息,请参阅 RP Controller Expansion Module Built-in Power Supply .

RP Controller Expansion Module Energy Metering

RP controller expansion modules with power distribution capability support energy metering, which means that the module can measure the electrical energy consumption and power demand for the equipment connected to and supplied by the module.

有关更多信息,请参阅 RP Controller Expansion Module Energy Metering .

RP Controller Expansion Module Memory

RP controller expansion modules have two types of memory, flash memory and RAM.

有关更多信息,请参阅 RP Controller Expansion Module Memory .

SMI Blind Modules Supported Building Standards

The SMI blind modules comply to version 3.0 of the SMI specification.

有关更多信息,请参阅 SMI Blind Modules Supported Building Standards .

RP Controller Expansion Module Communication Ports

The RP controller expansion modules have two room bus ports (RJ45 receptacles), which enable connection to the RP-C controller and other expansion modules on the room bus through a daisy-chain configuration.

有关更多信息,请参阅 RP-C Room Bus .

RP Controller Expansion Module Address Switch

Each RP controller expansion module has a rotary switch, which is used to give the device a unique address on the room bus.

有关更多信息,请参阅 RP-C Room Bus .

RP-C Room Bus

The RP controller room bus allows RP controller expansion modules to be connected to the controller for people counting, motion detection, luminosity and sound pressure level measurements, Bluetooth Low Energy based applications, and control of electric lights and window blinds.

有关更多信息,请参阅 RP-C Room Bus .

RP Controller Expansion Module Pluggable Connectors

The RP controller expansion modules have PCB mounted connectors for the power input, outputs, and digital inputs. The PCB mounted connectors mate with pluggable connectors:

  • The light modules, blind modules, and the RP-C-EXT-REL-4 relay module have mechanically keyed and color-coded connectors, which allows the matching external connectors to be plugged in on site quickly and easily.

  • The CRS-HH-REL-10 relay module has PCB header connectors for pluggable screw terminal blocks, which are easy to install and remove from the device.

有关更多信息,请参阅 RP Controller Expansion Module Pluggable Connectors .

RP Controller Expansion Module LEDs

There is one or more LEDs on the front panel of the RP controller expansion modules.

有关更多信息,请参阅 RP Controller Expansion Module LEDs .

RP Controller Expansion Module Set Button

All RP controller expansion modules have a Set button on the front. The Set button is reserved for future use.

有关更多信息,请参阅 RP Controller Expansion Module Set Button .

RP Controller Expansion Module Device Installation

The RP controller expansion module can be installed on a DIN rail or other flat surface inside a cabinet. The device is recommended to be installed in a cabinet, unless local regulations allow an exception.

有关更多信息,请参阅 RP Controller Expansion Module Device Installation .

Wiring

The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, BACnet/IP devices, RP controller expansion modules, and Operator Display.

有关更多信息,请参阅 Wiring .

RP Controller Expansion Module Maintenance Modes

The RP controller expansion modules support different modes that can be used for maintenance purposes.

有关更多信息,请参阅 RP Controller Expansion Module Maintenance Modes .

BACnet/IP Device Firmware Management

Using WorkStation, you can update the firmware of multiple BACnet/IP devices and their attached SpaceLogic Sensor devices and RP controller expansion modules at the same time with minimum downtime. In particular, the universal upgrade package simplifies the update process and requires minimal user involvement and coordination.

提示:

SpaceLogic Sensor devices and RP controller expansion modules are supported by the RP controller.

有关更多信息,请参阅 BACnet/IP Device Firmware Management .

RP Controller Expansion Module Regulatory Compliance and Approvals

This section provides information on regulatory compliance and approvals for the RP controller expansion modules.

有关更多信息,请参阅 RP Controller Expansion Light, Blind, and Relay Modules Regulatory Compliance and Approvals .

规格

Electrical
Nominal voltage
230 VAC
Operating voltage range
+/-10 %
Frequency
50/60 Hz
Power consumption
75 VA
Room bus power consumption
0.3 W (24 VDC)
Protection
Maximum 16 A external fuse (circuit breaker) is needed
Overvoltage category
III
Onboard 24 VDC power supply
RP-C-EXT-BL-SMI-2-LV-PD has an onboard 24 VDC power supply that is used to power the blind outputs.
Nominal voltage
24 VDC
Maximum supply current
1.3 A
Protection
Short-circuit protection
Environment
Ambient temperature, operating
0 to 40 °C (32 to 104 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Humidity
20 to 90 % RH non-condensing
Pollution degree
2
Material
Plastic flame rating
UL94 V-0
Ingress protection rating
IP 20
Mechanical
Dimensions
198 W x 110 H x 64 D mm (7.8 W x 4.3 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight
0.439 kg (0.968 lb)
Recommended installation
DIN rail or flat surface in a cabinet a
Connectors
Power input: 1 x 3-pin Wieland GST15i3 connector
  
Blind outputs: 2 x 5-pin Wieland GST15i5 connector
  
Digital inputs: 4 x 2-pin Wieland GST15i2 connector
Communication ports
Room bus
RS-485
  
Dual RJ45 ports for daisy-chain configurations
  
Use a Cat 5 (or higher) cable
  
Maximum total length of the room bus: 72 m (236 ft)
Room bus protection
Transient voltage suppressors on communication and power signals
Hardware
CPU type
ARM Cortex-M4 single-core
Frequency
80 MHz
SRAM (embedded)
320 KB
Flash memory (embedded)
512 KB
NOR flash memory
16 MB
Status indicator
LED (green and red) that shows the status of the device
Blind status indicator
One status LED (green) for each output
Address switch
Rotary switch 0 to 9
Set button
Push-button switch
Energy metering
Energy consumption measurement
The energy consumption is measured in Wh, shared by the two outputs.
Accuracy class (according to IEC 61557-12)
Active energy measurement: Class 1
Typical measurement accuracy at room temperature
0.5 to 2 W: 5%
  
2 to 30 W: 1%
Blind outputs
SMI LoVo motor control outputs for 24 VDC powered blinds motors.
Outputs
2, Blind 1 to Blind 2
Output terminals
I+, I-, 0 V, and 24 V
SMI version
3.0
Number of SMI channels
1
Maximum total number of blind motors (drives)
16
Power distribution
24 VDC
  
Maximum 1 A load per output
  
Maximum 1.3 A total load for the 2 outputs
  
Maximum 2 A starting current (<100 ms) per output
Digital inputs
Inputs
4, DI1 to DI4
Range
Dry contact, 0 to 5.0 VDC, 2.2 mA, SELV (Safety Extra-Low Voltage)

Internal Configuration

The RP-C-EXT-BL-SMI-2-LV-PD internal configuration with regards to the signal ground is shown in the following figure.

 
action_zoom_plus_stroke RP-C-EXT-BL-SMI-2-LV-PD internal configuration
图: RP-C-EXT-BL-SMI-2-LV-PD internal configuration
  • Hardware Overview
  • RP Controller Expansion Modules
  • Blind Modules
  • SMI LoVo Blind Outputs
  • RP Controller Expansion Module Digital Inputs
  • RP Controller Expansion Module Built-in Power Supply
  • RP Controller Expansion Module Energy Metering
  • RP Controller Expansion Module Memory
  • SMI Blind Modules Supported Building Standards
  • RP-C Room Bus
  • RP Controller Expansion Module Pluggable Connectors
  • RP Controller Expansion Module LEDs
  • RP Controller Expansion Module Set Button
  • RP Controller Expansion Module Device Installation
  • Wiring
  • RP Controller Expansion Module Maintenance Modes
  • BACnet/IP Device Firmware Management
  • RP Controller Expansion Light, Blind, and Relay Modules Regulatory Compliance and Approvals