SpaceLogic TM 无线适配器 -Advanced 是一款基于 USB 的无线适配器,可为您的 SpaceLogic BACnet/IP 控制器或自动化服务器实现 Zigbee TM 无线连接,从而扩展其点数并为您的改装应用带来灵活性。该适配器可与 BACnet/IP 控制器(如 RP 控制器)以及自动化服务器(如 AS-P 和 AS-B 服务器)一起使用。
An automation server equipped with the adapter can communicate over the Zigbee wireless protocol with up to 164 wireless devices, depending on the type of Zigbee device and the radio bandwidth usage of the device. An RP controller equipped with the adapter can communicate with up to 30 wireless devices.
有关受支持无线设备的信息,请参阅“受支持的无线设备”一节。
该适配器允许在调试后选择 2.4GHz 频带中的 16 个工作信道之一,以改善信号传输和接收。
The adapter works seamlessly within EcoStruxure Building Management systems so that Zigbee objects become easily available to the user.
The adapter’s compact design allows it to plug in to RP controllers or automation servers in tight spaces and the optional mounting cradle, wall plate, and USB cable extension allow for the choice of a wall, ceiling, or exterior of the enclosure mount to maximize the transmission and reception of signals from distributed Zigbee devices.
In WorkStation, the firmware of the adapter will be automatically updated when you update the RP controller or automation server to which it is connected.
适配器具有以下特点:
Zigbee 认证产品(带RP控制器、AS-P 和 AS-B 服务器)
Zigbee 3.0
设计紧凑、安装简便
多种安装选项
集成 2.4 GHz 天线
无线通信距离:
视线范围:最大 50 m (164 ft)
允许网络的调试后信道更改
通过 EcoStruxure Building Operation 软件进行配置和固件更新
产品 |
物料号 |
SpaceLogic Wireless Adapter - Advanced
|
SXWZBAUSB10001
|
USB Adapter Cradle Kit Includes plastic mounting cradle and wall plate |
SXWUSBCRA10001
|
USB Extension Cable 1 m (3 ft) Includes USB extension cable of length 1 m (3 ft) |
SXWUSBCBL10001
|
Plenum Rated USB Extension Cable 3 m (10 ft) Includes plenum rated USB extension cable of length 3 m (10 ft) |
SXWUSBCBL10002
|
Electrical | |
DC input supply voltage
|
5 伏直流 (USB)
a
|
a) 通过 RP 控制器或自动化服务器上的 USB 2.0 主机端口连接和供电。 | |
Maximum power consumption
|
0.3 W
|
Wireless connectivity | |
Communication protocol
|
Zigbee 3.0
|
Frequency band
|
2.4 GHz (ISM band), compliant with IEEE Standard 802.15.4
|
Maximum output power
|
+10 dBm
|
Maximum communication distance
|
Line-of-sight: 50 m (164 ft)
|
Antenna
|
Integrated antenna
|
Maximum total number of hops allowed in the wireless network
|
5
|
Wireless device limits for an RP controller | |
Maximum total number of wireless devices connected to the wireless network
|
Up to 30
a
|
a) The maximum number depends on the type of Zigbee device and the radio bandwidth usage of the Zigbee device. | |
Maximum total number of SE8000 and VT8000 room controllers
|
4
|
Maximum total number of Zigbee end devices paired with an RP controller
|
20
|
Maximum total number of ASSA ABLOY VingCard electronic locks
|
1
|
Wireless device limits for an automation server | |
Maximum total number of wireless devices connected to the wireless network
|
Up to 164
a
|
a) The maximum number depends on the type of Zigbee device and the radio bandwidth usage of the Zigbee device. | |
Maximum total number of Zigbee routers and Zigbee end devices
|
64
|
Maximum total number of Zigbee Green Power devices
|
100
|
Maximum total number of Zigbee end devices paired with an automation server
|
20
|
Environment | |
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
Ambient temperature, storage
|
-40 to +70 °C (-40 to +158 °F)
|
Humidity
|
Maximum 95 % RH non-condensing
|
Material | |
Plastic flame rating
|
UL94 HB
|
Plenum rating
|
UL 2043
|
Ingress protection rating
|
IP 20
|
Mechanical | |
尺寸,适配器
|
见下图
|
![]() |
|
尺寸,安装架和壁板
|
见下图
|
![]() |
|
Weight
|
Adapter: 7.57 g (0.267 oz)
|
Cradle and nut: 21.35 g (0.753 oz)
|
|
Cradle, nut, and wall plate: 33.40 g (1.178 oz)
|
|
Installation
|
Connection to USB host port on RP controller or automation server
|
Indoor use only
|
|
Installation options
|
Enclosure exterior
|
Drop ceiling with mounting cradle (optional)
|
|
Wall with wall plate (optional)
|
|
Maximum USB 2.0 cable length
|
3 m (10 ft)
|
Software requirements | |
EcoStruxure Building Operation software
|
version 3.2 and later
|
EcoStruxure Building Commission mobile application software
|
version 4.0 and later
|
RP-C controller firmware
|
版本 3.02.xx 或更高
|
AS-P server firmware
|
EcoStruxure Building Operation software version 3.2 and later
|
AS-B server firmware
|
EcoStruxure Building Operation software version 3.3 and later
|
Agency compliances | |
EMC
|
EN 301 489-1 V2.2.3; EN 301 489-17 V3.2.2; BS/EN 55032:2015; BS/EN 55035:2017; FCC Part 15, Sub-part C, Class B; ICES-003, Class B
|
Radio
|
ETSI EN 300 328 V2.2.2
|
Safety standards
|
BS/EN 62368-1:2014; BS/EN 62311:2008; BS/EN 62479:2010
|
FCC ID
|
QOQ13
|
ISED certification number
|
IC: 5123A-13
|
Hardware | |
CPU type
|
ARM Cortex-M4 with Floating Point Unit (FPU)
|
Frequency
|
38.4 MHz
|
SRAM (embedded)
|
64 KB
|
Flash memory (embedded)
|
512 KB
|
Connectors
|
USB 2.0, type-A connector
|
For information on the wireless devices that are supported by the wireless network, see the document SpaceLogic Wireless Connectivity – Advanced; Supported Devices.
The import files for supported wireless devices can be found in the Schneider Electric BMS Applications web portal ( bms-applications.schneider-electric.com ).
In EcoStruxure Building Operation software version 4.0 and later, additional Zigbee 3.0 wireless devices can be supported using the Zigbee Wireless Device Support Service. For information on how support for Zigbee 3.0 devices can be added in the EcoStruxure Building Operation software through this service, see the document PA-00842 - New Service for Zigbee Device Support in EBO.