SpaceLogic RP-C Advanced

 
action_zoom_plus_stroke RP-C-12C-F-24V
图: RP-C-12C-F-24V

简介

SpaceLogic™ RP-C Advanced is a room-purpose, fully programmable, IP based field controller that suits a wide range of HVAC applications and offers a room connectivity hub for Connected Room Solutions.

RP-C Advanced comes either as a 24 VAC/DC controller with 12 I/O points or as a 230 VAC controller with 16 I/O points.

The controller is integrated into Connected Room Solutions and EcoStruxure Building Operation and is positioned for room control as well as well-being, comfort of occupants in an energy-efficient way.

The RP-C Advanced controller can also be reconfigured through the EcoStruxure Building Operation software to support BACnet MS/TP, instead of BACnet/IP.

The controller can either be used as a standalone BACnet/IP field controller, BACnet/SC node, or as part of an EcoStruxure BMS with a SpaceLogic AS-P or AS-B server or an Enterprise Server as the parent server.

The controller features a wireless chip, which enables commissioning of the controller with the Commission mobile application and allows tenants to change the room comfort settings using their smartphones with the Engage mobile application.

Web services enable web access directly to the controller, making the controller an open IoT hub in the room or space area.

RP-C Advanced 具有下述特点:

  • 板载双网口交换机

  • BACnet/SC 节点

  • 全系列的控制器型号

  • 通用板载 I/O 点组合

  • 可选盖板

  • 无线连接

  • 高级监控

  • 两个可配置 RS-485 端口

  • 提供可连接 SmartX Sensor 的总线

  • 连接房间的房间总线解决方案

  • Modbus RTU 子网

  • KNX 支持(需要 KNX Modbus 网关)

  • BACnet MS/TP 支持(需要适配器)

  • 通过 Engage 移动应用程序进行房间舒适度设置

  • 在 BMS 就位之前,Commission 移动应用程序以调试控制器

  • 全面的 EcoStruxure Building Operation 软件支持,提供高效的工程工具

  • 通过 RESTful API 的 Web 服务

IP 连接、灵活的网络拓扑以及对 ACnet/SC 应用程序的支持

The BACnet/IP controllers are based on open protocols that simplify interoperability, IP configuration, and device management, and can be enabled as BACnet/SC nodes for increased cybersecurity:

  • IP addressing

  • BACnet/IP or BACnet/SC communications

  • DHCP for easy network configuration

The BACnet/IP controllers have a dual-port Ethernet switch, which enables flexible network topologies:

  • Star

  • Daisy chain

  • Rapid Spanning Tree Protocol (RSTP) ring

In a star topology, the controller and the parent EcoStruxure BMS server are individually connected to an Ethernet switch. Daisy-chain multiple controllers together to reduce installation time and cost. When using a ring network topology, in the event of a broken IP network or a non-operational controller, RSTP will enable rapid identification of the location of the detected error while maintaining communication with the controllers on either side of the break.

BACnet/SC (Secure Connect) 支持

The BACnet/IP controllers support BACnet/SC applications as a BACnet/SC node. This allows the controllers to be used in a BACnet/SC network, which allows secure transport of BACnet traffic and information between BACnet/SC devices over private and public networks without the need for BBMDs, VLANs, and VPNs, because the BACnet/SC protocol uses WebSocket technology and TLS 1.3 encryption. In addition, BACnet/SC uses certificate management to help ensure only those devices authorized to be on a BACnet/SC network can operate on that network.

全系列的控制器型号

RP-C Advanced 系列有四个不同的型号,提供四个不同的 I/O 点类型组,分别名为 12A、12B、12C 和 16A。RP-C-12A、-12B 和 -12C 型号支持 24 VAC/DC 电源,而 RP-C-16A 型号为 230 VAC 供电。

 
action_zoom_plus_stroke

可自由编程

可自由编程的 RP-C 型号同时支持脚本和功能块编程选择,非常灵活。RP-C 可借助标准控制器应用程序提高效率和标准化。

多种 I/O 点组合型号

RP-C-12A、-12B、-12C 和 -16A 型号提供 12 或 16 I/O 点,包括四个不同的 I/O 点类型组。I/O 点类型的通用组合可匹配众多 HVAC 应用类型。通用输入/输出极其灵活度,既可配置为输入也可配置为输出。

表格: I/O Point Types by RP-C Models

I/O Point Types

RP-C-12A model

RP-C-12B model

RP-C-12C model

RP-C-16A model

Universal I/O

Type Ub

8

8

4

8

Solid-state relay outputs

(MOSFET)

4

-

4

4

Relay outputs

Form A

-

3

3

3

High power relay outputs

Form C

-

1

1

1

表格: Configurations by I/O Point Types

Configurations

Universal I/O

Type Ub

Solid-state Relay Outputs

(MOSFET)

Relay Outputs

Form A

High Power Relay Outputs

Form C

Digital inputs

yes

-

-

-

Counter inputs

yes

-

-

-

Supervised inputs

yes

-

-

-

Voltage inputs

(0 to 10 VDC)

yes

-

-

-

Current inputs

(0 to 20 mA)

yes

-

-

-

Temperature inputs

yes

-

-

-

Resistive inputs

yes

-

-

-

2-wire RTD temperature inputs

yes

-

-

-

Voltage outputs

(0 to 10 VDC)

yes

-

-

-

Digital outputs

-

yes

yes

yes

Digital pulsed outputs

-

yes

yes

yes

PWM outputs

-

yes

yes

yes

Tristate outputs

-

yes

yes

-

Tristate pulsed outputs

-

yes

yes

-

通用输入/输出

The universal inputs/outputs are ideal for any mix of temperature, pressure, flow, status points, and similar point types in a building control system.

As counter inputs, the universal inputs/outputs are commonly used in energy metering applications. As RTD inputs, they are ideal for temperature points in a building control system. As supervised inputs, they are used for security applications where it is critical to know whether or not a wire has been cut or shorted. These events provide a separate indication of alarms and events in the system.

For all analog inputs, maximum and minimum levels can be defined to automatically detect over-range and under-range values.

The universal inputs/outputs are capable of supporting analog outputs of type voltage outputs. Therefore, the universal inputs/outputs support a wide range of devices, such as actuators.

Only devices with safe extra low voltage equipment (SELV/PELV) inputs/outputs should be connected to the universal inputs/outputs.

固态继电器输出

The solid-state relay (SSR) outputs can be used in many applications to switch 24 VAC or 24 VDC on or off for external loads such as actuators, relays, or indicators. SSRs are silent and are not adversely affected by relay contact wear.

继电器输出

The relay outputs support digital Form A point types. The Form A relays are designed for direct load applications.

高功率继电器输出

The high power relay output is of type Form C. The normally-open (NO) contact is ideal for switching resistive loads of up to 12 A, such as electrical heating elements. The normally-closed (NC) contact can be used to switch inductive loads of up to 3 A.

可选盖板

所有 RP-C 型号可配备可选的盖板以减少对于螺钉端子和线的触及。

 
action_zoom_plus_stroke 配备可选盖板的 RP-C
图: 配备可选盖板的 RP-C

无线连接

RP-C 是启用了低功耗蓝牙 (BLE) 的产品。您可以使用此无线连接选项将运行 Commission 移动应用程序或用于房间舒适度设置的 Engage 移动应用程序的智能手机或平板电脑连接到 RP-C。

Through Wireless Adapter - Advanced connected to the host USB port, Zigbee TM wireless connectivity can be enabled for the RP controller. The controller can extend its point count through the Zigbee wireless network and bring flexibility in your applications. The RP controller equipped with the adapter is a Zigbee Certified Product that is compliant with Zigbee 3.0. For more information on the adapter and supported wireless devices, see the Wireless Adapter - Advanced Specification Sheet.

高级监控

The BACnet/IP controllers support local trends, schedules, and alarms, enabling local operation when the controller is offline or used in standalone applications.

The battery-free power backup of the memory and real-time clock helps prevent data loss and allows seamless and quick recovery after a power disruption.

In WorkStation, you update the firmware of multiple BACnet/IP controllers at the same time and with minimum down time. The EcoStruxure BMS server keeps track of the installed firmware to support backup, restore, and replacement of the controllers and sensors. The server can host controllers of different firmware versions.

两个可配置 RS-485 端口

RP-C 控制器有两个可配置 RS-485 端口,可以针对支持三种不同类型的网络进行配置:

  • 传感器总线

  • 房间总线

  • Modbus 网络

The controller can host two networks, but only one of each network type.

One of the RS-485 ports can alternatively be configured to support BACnet MS/TP network communication with the automation server, instead of BACnet/IP. For more information, see section “BACnet MS/TP support”. The other RS-485 port can then be configured to support either sensor bus, room bus, or Modbus network.

提供可连接 SmartX Sensor 的总线

The BACnet/IP controllers provide an interface designed for the SpaceLogic Sensor family of living space sensors. The SpaceLogic Sensor devices offer an efficient way to sense the temperature, humidity, CO 2 , and occupancy in a room. The SpaceLogic Sensor devices are available with different combinations of sensor types and various covers and user interface options, such as touchscreen, setpoint and override buttons, and blank covers.

 
action_zoom_plus_stroke SpaceLogic 传感器设备
图: SpaceLogic 传感器设备

The RP controller sensor bus provides both power and communications for up to four sensors that are daisy-chained using standard Cat 5 (or higher) cables. This maximum number of sensors that can be connected to a controller is regardless of the sensor model and the combination of cover and sensor base type:

  • Blank covers: Up to four sensors of any combination of sensor base types

  • 3-button and touchscreen covers: Up to four sensors of any combination of sensor base types

  • SpaceLogic LCD temperature sensors: Up to four sensors are supported

The maximum total length of the sensor bus is 61 m (200 ft). For more information, see the SpaceLogic Sensors - SXWS Sensors for MP and RP IP Controllers - Specification Sheet.

The RS-485 Power Adapter can be used for injecting 24 VDC from an external 24 VDC power supply to the bus. For more information, see the RS-485 Adapters Specification Sheet.

连接房间的房间总线解决方案

The RP controller room bus allows RP controller expansion modules to be connected to the controller for people counting, motion detection, luminosity and sound pressure level measurements, Bluetooth Low Energy based applications, and control of electric lights and window blinds.

The RP-C Advanced controller room bus supports up to six connected RP controller expansion modules with the following restrictions:

  • Maximum of two DALI light modules

  • Maximum of two SMI blind modules

  • Maximum of four Multi-sensor or Insight-Sensor devices

Maximum total length of the room bus is 72 m (236 ft).

The RS-485 Power Adapter can be used for injecting 24 VDC from an external 24 VDC power supply to the bus. For more information, see the RS-485 Adapters Specification Sheet.

更多信息,请参阅 RP 控制器扩展模块的规格表。

Modbus RTU 子网

The RP controller Modbus network allows standard Modbus devices and the KNX Modbus gateway (RP-C-EXT-KNX) to be connected to the controller.

The Modbus RTU protocol is used for the communication. The RP controller acts as the Modbus client and the connected devices act as servers.

For connection to Modbus devices, it is recommended to use the non-isolated RS-485 adapter to provide screw termination. The adapter converts an RS-485 RJ45 interface to screw terminals. The adapter can be ordered from Schneider Electric. For more information, see the RS-485 Adapters Specification Sheet.

To connect the adapter, it is recommended that you use a Cat 5 (or higher) UTP cable with eight conductors and RJ45 connectors. The cable should be rated for the target environment and have a maximum length of 0.3 m (12 in.). The cable is not included and needs to be purchased separately.

The maximum number of Modbus devices that can be connected to an RP controller depends on the type of Modbus device and the number of Modbus registers.

The RP-C Advanced controller Modbus network supports up to 10 connected Modbus devices with the following restrictions:

  • Maximum of one KNX Modbus gateway (RP-C-EXT-KNX)

  • Maximum of 250 Modbus registers per network

64-bit Modbus registers are supported, which can be used in energy metering.

Modbus 设备类型

Modbus device types are pre-configured Modbus applications for quick and easy Modbus device integration in EcoStruxure Building Operation solutions. For information on the Modbus devices supported using Modbus device types, see the document EcoStruxure Building - Modbus Device Integration - Supported Device Brochure.

支持 KNX

Through the KNX Modbus gateway (RP-C-EXT-KNX), the RP controller can communicate with KNX devices such as push-buttons and sensors.

The KNX Modbus gateway provides a KNX to Modbus interface that connects to one of the RP controller's configurable RS-485 ports.

For more information, see the RP-C-EXT-KNX Specification Sheet.

BACnet MS/TP 支持

The RP controllers support both BACnet IP and MS/TP protocols. The controller can be configured to use either protocol. This feature enables both retrofitting of MNB and b3 BACnet devices while reusing parts of the existing cabling and equipment, as well as a later transition from the BACnet MS/TP (RS-485) network to an IP based network.

An RJ45 to screw terminal block adapter is required to connect the RP controller to the BACnet MS/TP network of the AS-P or AS-B server. The adapter can be ordered from Schneider Electric. The adapter is available in two models, with an isolated or non-isolated RS-485 interface. For more information, see the RS-485 Adapters Specification Sheet.

To connect the adapter, it is recommended that you use a Cat 5 (or higher) UTP cable with eight conductors and RJ45 connectors. The cable should be rated for the target environment and have a maximum length of 0.3 m (12 in.). The cable is not included and needs to be purchased separately.

In retrofit projects with MNB devices, the RP controllers can be mixed with MNB devices on the BACnet MS/TP network. The isolated adapter is used for connection of a controller. The adapter is connected to the RS-485 Com B port on the controller.

In retrofit projects with b3 BACnet devices, the RP controllers can be mixed with b3 BACnet devices on the BACnet MS/TP network. The non-isolated adapter is used for connection of a controller. The adapter can be connected to either the RS-485 Com A or Com B port on the controller.

In retrofit projects with only RP controllers on the BACnet MS/TP network, the non-isolated adapter is used for connection of a controller. The adapter can be connected to either the RS-485 Com A or Com B port on the controller.

Engage 移动应用程序

The Engage mobile application enables control of room temperature, fan speed, lights, and blinds/shades directly from a smartphone. A user can manage these settings when the application is connected to the RP controller.

The Engage mobile application is free and available for download from Google Play and Apple App Store.

For more information, see the Engage Specification Sheet.

Commission 移动应用程序

Commission 移动应用程序设计用于 BACnet/IP 控制器的本地配置、现场部署和调试。该移动应用程序可缩短调试时间,便于灵活地实施项目,最小化网络基础设施的依赖性。

The mobile application is designed for use with Android, Apple (iOS), and Microsoft Windows 10 and Windows 11 devices. For more information, see the EcoStruxure Building Commission Specification Sheet.

 
action_zoom_plus_stroke Commission 移动应用程序
图: Commission 移动应用程序

Using the Commission mobile application, you can connect to one or many RP controllers. You can connect to a single RP controller using the controller's built-in Bluetooth connectivity or using the SpaceLogic Bluetooth Adapter connected to a SpaceLogic Sensor. Using a wireless access point or a network switch, you can connect to a network of RP controllers on the local IP network.

设备配置

With the Commission mobile application, you can easily discover BACnet/IP controllers on the IP network. You can change the configuration of each controller, including the BACnet and IP network settings, location, and parent server. To save engineering time, you can save common device settings and then reuse them for controllers of the same model.

现场部署和 I/O 检验

The Commission mobile application does not require an EcoStruxure BMS server or a network infrastructure to be in place. You can use the mobile application to load the controller application directly into the local BACnet/IP controller and deploy the controller. The controller application can be created offline using Project Configuration Tool or WorkStation. You can use the mobile application to change the behavior of an installed standard controller application, such as configuring temperature setpoints. You can also perform an I/O checkout to verify that the controller's I/O points are configured, wired, and operating correctly.

You can perform I/O checkout on the RP controller room bus to verify proper communication over the room bus between the RP controller and the associated RP controller expansion modules. Module type mismatches or address mismatches can then be resolved. After wiring the physical inputs and outputs of the RP controller expansion modules, you can perform the following tasks on the different modules:

  • DALI light modules: discover, wink, and associate DALI lights with the logical software points, and test individual lights

  • 0-10V light modules: test individual lights

  • Blind modules: calibrate and test blinds

  • Relay module: test outputs

全面的 EcoStruxure Building Operation 软件支持

The power of the RP controller is fully realized when it is part of an EcoStruxure BMS, which provides the following benefits:

  • WorkStation/WebStation interface

  • Script and Function Block programming options

  • Device discovery

  • Engineering efficiency

  • Preconfigured BMS applications for HVAC and Connected Room Solutions

  • Zoning option

WorkStation/WebStation 界面

WorkStation and WebStation provide a consistent user experience regardless of which EcoStruxure BMS server the user is logged on to. The user can log on to the parent EcoStruxure BMS server to engineer, commission, supervise, and monitor the BACnet/IP controller and its I/O as well as its attached SpaceLogic Sensor devices. For more information, see the WorkStation and WebStation specification sheets.

脚本和功能块编程选项

The fully programmable RP and MP controller models have both Script and Function Block programming options. Existing programs can easily be reused between the EcoStruxure BMS server and the controller.

设备发现

The enhanced Device Discovery in WorkStation enables you to easily identify BACnet/IP controllers on a BACnet network and to associate the controllers with their parent server.

工程效率

The engineering and maintenance of BACnet/IP controllers can be done very efficiently using the EcoStruxure Building Operation reusability features. With these features, you can create library items (Custom Types) for a complete controller application that contains programs and all necessary objects such as trends, alarms, and schedules. The controller application in the Custom Types library is reusable across all controllers of the same model. You can use the controller application as a base for creating new controllers intended for similar applications. You can then edit the controller application, and the changes are automatically replicated to all controllers, while each controller keeps its local values.

WorkStation supports both online and offline engineering of BACnet/IP controllers. You can make the configuration changes online or use database mode to make the changes offline. In database mode, the changes are saved to the EcoStruxure Building Operation database so that you can apply the changes to the controllers later.

Project Configuration Tool enables you to perform all the engineering off site, without the need for physical hardware, which minimizes the time you need to spend on site. You can run the EcoStruxure BMS servers virtually and engineer the BACnet/IP controllers before you deploy your server and controller applications to the servers and controllers on site. For more information, see the Project Configuration Tool specification sheet.

暖通空调和连通房间解决方案的预配置 BMS 应用程序

To improve engineering efficiency and standardize engineering practices, fully designed and tested controller applications are available at bms-applications.schneider-electric.com for use with the RP controllers. This library contains applications for different RP controller models and application types, such as fan coil units, ceiling solutions, lights and blinds. These preconfigured controller applications are packages that include all software programs, and for example graphics, alarms, and documentation such as functional specifications and I/O wiring schedules, that are needed for your projects. The online repository can be accessed using common web browsers on Windows PCs as well as mobile devices running Apple iOS 11.3 (or later) and Android 6.0 Marshmallow (or later).

 
action_zoom_plus_stroke 预配置 BMS 应用程序的下载页面
图: 预配置 BMS 应用程序的下载页面
分区选项

The Zoning option for WorkStation and WebStation provides access to an interactive zoning tool that enables easy reconfiguration of Connected Room Solutions and flexibility when switching between zones. The WebStation zoning tool provides a graphical interface that enables quick editing of zones from any web browser device.

The RP-C-12A, -12B, -12C, and -16A models support up to four segments, which can be used to support rezoning in a building.

Web 服务

The RP controller uses the RESTful API, which allows IT web services to easily interact with software applications. The flexibility of the RESTful API allows the RP controller to handle multiple types of input and return different data formats. With Web services, clients can read/write data (BACnet values) directly from/to the controller. Web services use resource methods GET, PUT, POST, and DELETE to access and use the data. HTTPS is used for communication between the client and the controller.

The Web services function is disabled by default. When enabled, it requires approximately 200 kB of RP controller memory.

表格: RP-C Advanced 零件编号

产品

部件号

RP-C-12A-F-24V
SXWRCF12A10002

RP-C-12A-F-24V:符合 TAA 变体 a

SXWRCF12A10T02
RP-C-12B-F-24V
SXWRCF12B10002

RP-C-12B-F-24V:符合 TAA 的变体 a

SXWRCF12B10T02
RP-C-12C-F-24V
SXWRCF12C10002

RP-C-12C-F-24V:符合 TAA 的变体 a

SXWRCF12C10T02
RP-C-16A-F-230V
SXWRCF16A10003
  1. RP-C-12A-F-24V、RP-C-12B-F-24V 和 RP-C-12C-F-24V 可在符合《贸易协议法》(TAA) 的变体中获得。 符合 TAA 的变体在硬件和功能方面没有区别。 符合 TAA 的变体在其零件号中有一个“T”。

表格: RP-C 配件的零件号

产品

部件号

Optional covers
SXWRPCCOV10001
DIN-RAIL-CLIP, DIN-rail end clip
package of 25 pieces
SXWDINEND10001

隔离 RS-485 适配器 a

SXWISORS48510001

非隔离 RS-485 适配器 a

SXWNISORS48510001

RS-485 电源适配器 a

SXWNISORS485P10001
SpaceLogic Wireless Adapter - Advanced
SXWZBAUSB10001
SpaceLogic Bluetooth Adapter
SXWBTAECXX10001
  1. RS-485 适配器在符合《贸易协议法》(TAA) 的变体中不可用。

For more information on part numbers for Network Connectivity Accessories, see the 有关更多信息,请参阅 Product Selection Guide - EcoStruxure Building ..

规格

AC input
RP-C-12A-F-24V, RP-C-12B-F-24V, and RP-C-12C-F-24V
Nominal voltage
24 VAC
Operating voltage range
+/-15 %
Frequency
50/60 Hz
Maximum power consumption
23 VA
Power input protection
MOV suppression and internal fuse
RP-C-16A-F-230V
Nominal voltage
230 VAC
Operating voltage range
+/-10 %
Frequency
50/60 Hz
Maximum power consumption
65 VA
Power consumption without load
5 W
Power input protection
MOV suppression and internal fuse
  
Separate PTC thermistor used as a resettable fuse for 24 VAC Out only
Overvoltage category
III
Pollution degree
2
DC input
RP-C-12A-F-24V, RP-C-12B-F-24V, and RP-C-12C-F-24V
Nominal voltage
24 to 30 VDC
Operating voltage range
23.5 to 33 VDC
Maximum power consumption
14 W
Power input protection
MOV suppression and internal fuse
AC output
RP-C-16A-F-230V
Type
Isolated Class 2 output
Nominal voltage
24.0 VAC a
Minimum voltage
19.8 VAC a
Maximum voltage
30.8 VAC a
Frequency
Same frequency as the power supply (50/60 Hz)
Output power rating
19 VA
Environment
RP-C-12A-F-24V, RP-C-12B-F-24V, and RP-C-12C-F-24V
Ambient temperature, operating
0 to 50 °C (32 to 122 °F) at normal operation
  
-40 to +60 °C (-40 to +140 °F) for rooftop applications, horizontal installation only
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Maximum humidity
95 % RH non-condensing
RP-C-16A-F-230V
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic flame rating
UL94-5VB
Ingress protection rating
IP 20
Mechanical
Dimensions
180 W x 110 H x 64 D mm (7.1 W x 4.3 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight, RP-C-12A-F-24V
0.370 kg (0.816 lb)
Weight, RP-C-12B-F-24V and RP-C-12C-F-24V
0.390 kg (0.860 lb)
Weight, RP-C-16A-F-230V
0.720 kg (1.587 lb)
Recommended installation
DIN rail or flat surface in a cabinet a
Terminal blocks
Fixed
Optional covers
Dimensions
181 W x 164 H x 64 D mm (7.1 W x 6.5 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight, optional covers
0.070 kg (0.154 lb)
Compatibility
EcoStruxure BMS server communication
EcoStruxure Building Operation
version 3.0.1 and later
BACnet MS/TP network support
EcoStruxure Building Operation
version 4.0.2 and later
Modbus 64-bit register support
EcoStruxure Building Operation
version 5.0.1 and later
BACnet/SC network support
EcoStruxure Building Operation
version 6.0.1 and later
Agency compliances
RP-C-12A-F-24V, RP-C-12B-F-24V, and RP-C-12C-F-24V
Emission
RCM; BS/EN 61000-6-3; BS/EN IEC 63044-5-2; FCC Part 15, Subparts B and C, Class B
Immunity
BS/EN 61000-6-2; BS/EN IEC 63044-5-3
Radio
ETSI EN 300 328 V2.2.2
Safety standards
BS/EN 60730-1; BS/EN 60730-2-11; BS/EN IEC 63044-3; UL 916 C-UL US Listed a
FCC ID
DVE-RPC24
ISED certification number
IC: 24775-RPC24
Fire performance in air-handling spaces a
UL 2043
RP-C-16A-F-230V
Emission
RCM; BS/EN 61000-6-3; BS/EN IEC 63044-5-2
Immunity
BS/EN 61000-6-2; BS/EN IEC 63044-5-3
Radio
ETSI EN 300 328 V2.2.2
Safety standards
BS/EN 60730-1; BS/EN 60730-2-11; BS/EN IEC 63044-3
Energy
eu.bac Certified Product (Licence No. 219832); BS/EN 15500-1
Real-time clock
Accuracy, at 25 °C (77 °F)
+/-1 minute per month
Backup time, at 25 °C (77 °F)
7 days minimum
Communication ports
Ethernet
Dual 10/100BASE-TX (RJ45)
USB
1 USB 2.0 device port (mini-B)
  
1 USB 2.0 host port (type-A), 5 VDC, 2.5 W
RS-485 port Com A
24 VDC, 3 W, RS-485 (RJ45)
  
Transient voltage suppressors on communication and power signals
RS-485 port Com B
24 VDC, 3 W, RS-485 (RJ45)
  
Transient voltage suppressors on communication and power signals
RS-485 transceiver characteristics
Transceiver type
Failsafe
  
Non-isolated
External biasing
None required
Total Unit Load (UL) per device
Maximum 0.5 UL
Communications
BACnet
BACnet/IP, port configurable, default 47808
  
BACnet/SC, port configurable, no default port
  
BACnet MS/TP, maximum bus length: 1200 m (4000 ft), maximum baud rate: 76800
  
BTL B-AAC (BACnet Advanced Application Controller) a
Wireless connectivity
Bluetooth Low Energy
Communication protocol
Bluetooth ® 5.1 Low Energy compliant
Frequency
2.402 to 2.480 GHz
Maximum output power
10 dBm
Maximum communication distance
Line-of-sight: 100 m (328 ft)
Antenna
Integrated antenna
RF connector for optional external antenna
SMA connector
External antenna (optional)
Restricted to the approved antenna type listed below (used in certification)

Manufacturer

Model (Part number)

Gain

Type

Impedance

Linx Technologies

ANT-2.4-WRT-MON-SMA

0.8 dBi

Monopole

50 ohm

CPU
Frequency
500 MHz
Type
ARM Cortex-A7 single-core
Internal SRAM
6 MB
NOR flash memory
48 MB
Memory backup
128 kB, FRAM, non-volatile
Universal inputs/outputs
Channels, RP-C-12A-F-24V
8 Ub, Ub1 to Ub8
Channels, RP-C-12B-F-24V
8 Ub, Ub1 to Ub8
Channels, RP-C-12C-F-24V
4 Ub, Ub1 to Ub4
Channels, RP-C-16A-F-230V
8 Ub, Ub1 to Ub8
Absolute maximum ratings
-0.5 to +24 VDC
A/D converter resolution
16 bits
Universal input/output protection
Transient voltage suppressor on each universal input/output
Digital inputs
Range
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
Minimum pulse width
150 ms
Counter inputs
Range
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
Minimum pulse width
20 ms
Maximum frequency
25 Hz
Supervised inputs
5 V circuit, 1 or 2 resistors
Monitored switch combinations
Series only, parallel only, and series and parallel
Resistor range
1 to 10 kohm
For a 2-resistor configuration, each resistor must have the same value +/- 5 %
Voltage inputs
Range
0 to 10 VDC
Accuracy
+/-(7 mV + 0.2 % of reading)
Resolution
1.0 mV
Impedance
1 Mohm
Current inputs
Range
0 to 20 mA
Accuracy
+/-(0.01 mA + 0.4 % of reading)
Resolution
1 μA
Impedance
47 ohm
Resistive inputs
10 ohm to 10 kohm accuracy
+/-(7 + 4 x 10 -3 x R) ohm
R = Resistance in ohm
10 kohm to 60 kohm accuracy
+/-(4 x 10 -3 x R + 7 x 10 -8 x R 2 ) ohm
R = Resistance in ohm
Temperature inputs (thermistors)
Range
-50 to +150 °C (-58 to +302 °F)
Supported thermistors
Honeywell
20 kohm
Type I (Continuum)
10 kohm
Type II (I/NET)
10 kohm
Type III (Satchwell)
10 kohm
Type IV (FD)
10 kohm
Type V (FD w/ 11k shunt)
Linearized 10 kohm
Satchwell D?T
Linearized 10 kohm
Johnson Controls
2.2 kohm
Xenta
1.8 kohm
Balco
1 kohm
Measurement accuracy
20 kohm
-50 to -30 °C: +/-1.5 °C (-58 to -22 °F: +/-2.7 °F)
  
-30 to 0 °C: +/-0.5 °C (-22 to +32 °F: +/-0.9 °F)
  
0 to 100 °C: +/-0.2 °C (32 to 212 °F: +/-0.4 °F)
  
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F)
10 kohm, 2.2 kohm, and 1.8 kohm
-50 to -30 °C: +/-0.75 °C (-58 to -22 °F: +/-1.35 °F)
  
-30 to +100 °C: +/-0.2 °C (-22 to +212 °F: +/-0.4 °F)
  
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F)
Linearized 10 kohm
-50 to -30 °C: +/-2.0 °C (-58 to -22 °F: +/-3.6 °F)
  
-30 to 0 °C: +/-0.75 °C (-22 to +32 °F: +/-1.35 °F)
  
0 to 100 °C: +/-0.2 °C (32 to 212 °F: +/-0.4 °F)
  
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F)
1 kohm
-50 to +150 °C: +/-1.0 °C (-58 to +302° F: +/-1.8 °F)
RTD temperature inputs
Supported RTDs
Pt1000, Ni1000, and LG-Ni1000
Pt1000
Sensor range
-50 to +150 °C (-58 to +302 °F)

BACnet/IP device environment

Sensor range

Measurement accuracy

0 to 50 °C (32 to 122 °F)

-50 to +70 °C (-58 to +158 °F)

+/-0.5 °C (+/-0.9 °F)

0 to 50 °C (32 to 122 °F)

70 to 150 °C (158 to 302 °F)

+/-0.7 °C (+/-1.3 °F)

-40 to +60 °C (-40 to +140 °F)

-50 to +150 °C (-58 to +302 °F)

+/-1.0 °C (+/-1.8 °F)

Ni1000
Sensor range
-50 to +150 °C (-58 to +302 °F)

BACnet/IP device environment

Sensor range

Measurement accuracy

0 to 50 °C (32 to 122 °F)

-50 to +150 °C (-58 to +302 °F)

+/-0.5 °C (+/-0.9 °F)

-40 to +60 °C (-40 to +140 °F)

-50 to +150 °C (-58 to +302 °F)

+/-0.5 °C (+/-0.9 °F)

LG-Ni1000
Sensor range
-50 to +150 °C (-58 to +302 °F)

BACnet/IP device environment

Sensor range

Measurement accuracy

0 to 50 °C (32 to 122 °F)

-50 to +150 °C (-58 to +302 °F)

+/-0.5 °C (+/-0.9 °F)

-40 to +60 °C (-40 to +140 °F)

-50 to +150 °C (-58 to +302 °F)

+/-0.5 °C (+/-0.9 °F)

RTD temperature wiring
Maximum wire resistance
20 ohm/wire (40 ohm total)
Maximum wire capacitance
60 nF
The wire resistance and capacitance typically corresponds to a 200 m wire.
Voltage outputs
Range
0 to 10 VDC
Accuracy
+/-60 mV
Resolution
10 mV
Minimum load resistance
2.4 kohm
Source current
+4.2 mA
Sink current
-1 mA (0 to 0.4 VDC)
  
-4.2 mA (0.4 to 10 VDC)
Relay outputs, DO
Channels, RP-C-12A-F-24V
0
Channels, RP-C-12B-F-24V
3, DO1 to DO3
Channels, RP-C-12C-F-24V
3, DO5 to DO7
Channels, RP-C-16A-F-230V
3, DO5 to DO7
Contact rating
Pilot Duty (C300)
  
Resistive load: 250 VAC/30 VDC, 4 A (cos phi = 1)
  
Inductive load: 250 VAC/30 VDC, 4 A (cos phi = 0.4)
Switch type
Form A Relay
  
Single Pole Single Throw
  
Normally Open
Commons
COM1 for DO1, DO2, and DO3 (on RP-C-12B model)
  
COM3 for DO5, DO6, and DO7 (on RP-C-12C and RP-C-16A models)
Isolation contact to system ground
3,000 VAC
Cycle life
At least 100,000 cycles
Minimum pulse width
100 ms
High power relay outputs, DO
Channels, RP-C-12A-F-24V
0
Channels, RP-C-12B-F-24V
1, DO4
Channels, RP-C-12C-F-24V
1, DO8
Channels, RP-C-16A-F-230V
1, DO8
Contact rating
Pilot Duty (B300)
  
Minimum current: 100 mA (5 VDC)
  
Normally Open contact, resistive load: 250 VAC/24 VDC, 12 A (cos phi = 1)
  
Normally Closed contact, inductive load: 250 VAC/24 VDC, 3 A (cos phi = 0.4)
Switch type
Form C Relay
  
Single Pole Double Throw
  
Normally Open and Normally Closed
Isolation contact to system ground
5,000 VAC
Cycle life
At least 100,000 cycles
Minimum pulse width
100 ms
Solid-state relay outputs, DO
Channels, RP-C-12A-F-24V
4, DO1 to DO4
Channels, RP-C-12B-F-24V
0
Channels, RP-C-12C-F-24V
4, DO1 to DO4
Channels, RP-C-16A-F-230V
4, DO1 to DO4
Output rating
Maximum 2 A load per output
  
Maximum 4 A total load for the 4 outputs
AC voltage range
Maximum 30 VAC
DC voltage range
Maximum 30 VDC
Commons
COM1 for DO1 and DO2 (on RP-C-12A, -12C, and -16A models)
  
COM2 for DO3 and DO4 (on RP-C-12A, -12C, and -16A models)
When the SSR outputs are used to switch AC, the common terminals can be connected to 0 to 30 VAC. When the SSR outputs are used to switch DC, the common terminals can be connected to -30 VDC to +30 VDC.
Common voltage range (AC)
0 to 30 VAC
Common voltage range (DC)
-30 to +30 VDC
Minimum pulse width
100 ms
Solid-state relay output protection
Transient voltage suppressor across each solid-state relay (SSR) output

端子

For more information on wiring, see Hardware Reference Guide.

 
action_zoom_plus_stroke RP-C-12A 型号 (24 VAC/DC)
图: RP-C-12A 型号 (24 VAC/DC)
 
action_zoom_plus_stroke RP-C-12B 型号 (24 VAC/DC)
图: RP-C-12B 型号 (24 VAC/DC)
 
action_zoom_plus_stroke RP-C-12C 型号 (24 VAC/DC)
图: RP-C-12C 型号 (24 VAC/DC)
 
action_zoom_plus_stroke RP-C-16A 型号 (230 VAC)
图: RP-C-16A 型号 (230 VAC)

表格: Part Numbers for SpaceLogic Sensor Devices, Sensor Bases

Product

Part number

Sensor base with temperature sensor

SXWSBTXXXSXX

Sensor base with temperature and humidity sensors

SXWSBTHXXSXX

Sensor base with temperature and CO 2 sensors

SXWSBTXCXSXX

Sensor base with temperature, humidity, and CO 2 sensors

SXWSBTHCXSXX

表格: Part Numbers for SpaceLogic Sensor Devices, Covers

Product

Housing

Part number

Blank cover

Medium matte white

SXWSCBXSELXX

Blank cover

Optimum glass white

SXWSCBXSELXW

Blank cover

Optimum glass black

SXWSCBXSELXB

Blank cover with occupancy sensor

Medium matte white

SXWSCBPSELXX

Blank cover with occupancy sensor

Optimum glass white

SXWSCBPSELXW

Blank cover with occupancy sensor

Optimum glass black

SXWSCBPSELXB

3-button cover

Medium matte white

SXWSC3XSELXX

3-button cover

Optimum glass white

SXWSC3XSELXW

3-button cover

Optimum glass black

SXWSC3XSELXB

3-button cover with occupancy sensor

Medium matte white

SXWSC3PSELXX

3-button cover with occupancy sensor

Optimum glass white

SXWSC3PSELXW

3-button cover with occupancy sensor

Optimum glass black

SXWSC3PSELXB

Touchscreen display cover

Medium matte white

SXWSCDXSELXX

Touchscreen display cover

Optimum glass white

SXWSCDXSELXW

Touchscreen display cover

Optimum glass black

SXWSCDXSELXB

Touchscreen display cover with occupancy sensor

Medium matte white

SXWSCDPSELXX

Touchscreen display cover with occupancy sensor

Optimum glass white

SXWSCDPSELXW

Touchscreen display cover with occupancy sensor

Optimum glass black

SXWSCDPSELXB

Touchscreen display cover with light control buttons

Optimum glass white

SXWSC2XSELXW

Touchscreen display cover with light control buttons

Optimum glass black

SXWSC2XSELXB

Touchscreen display cover with light control buttons and occupancy sensor

Optimum glass white

SXWSC2PSELXW

Touchscreen display cover with light control buttons and occupancy sensor

Optimum glass black

SXWSC2PSELXB

Touchscreen display cover with light and blind control buttons

Optimum glass white

SXWSC4XSELXW

Touchscreen display cover with light and blind control buttons

Optimum glass black

SXWSC4XSELXB

Touchscreen display cover with light and blind control buttons and occupancy sensor

Optimum glass white

SXWSC4PSELXW

Touchscreen display cover with light and blind control buttons and occupancy sensor

Optimum glass black

SXWSC4PSELXB

表格: Part Numbers for SpaceLogic Sensor Devices, Combination Models

Product

Housing

Part number

Complete SpaceLogic Sensor model with temperature sensor, buttons for override and setpoint control, and LCD display cover

Medium matte white

SXWSATXXXSLX

Complete SpaceLogic Sensor model with temperature sensor, buttons for override and setpoint control, and LCD display cover

Optimum glass white

SXWSATXXXSLW

Complete SpaceLogic Sensor model with temperature sensor, buttons for override and setpoint control, and LCD display cover

Optimum glass black

SXWSATXXXSLB

Complete non-communicating a SpaceLogic Sensor model with resistive temperature sensor (10 kohm type 3 thermistor) and blank cover

Medium matte white

SLASXXX

Complete non-communicating a SpaceLogic Sensor model with resistive temperature sensor (10 kohm type 3 thermistor) and blank cover

Optimum glass white

SLAWXXX

Complete non-communicating a SpaceLogic Sensor model with resistive temperature sensor (10 kohm type 3 thermistor) and blank cover

Optimum glass black

SLABXXX

  1. The SpaceLogic resistive temperature sensor (SLA...) is designed to be connected to I/O points/terminals on RP or MP controllers, or I/O modules. The sensor requires an analog input (temperature input).
  • Enterprise Server
  • SpaceLogic AS-P
  • SpaceLogic AS-B
  • WorkStation
  • WebStation
  • SpaceLogic RP-C-EXT-MS-BLE
  • SpaceLogic RP-C-EXT-IS-BLE
  • SpaceLogic RP-C-EXT-DALI-M-PD
  • SpaceLogic RP-C-EXT-DALI
  • SpaceLogic RP-C-EXT-0-10V-4-PD
  • SpaceLogic RP-C-EXT-0-10V-4
  • SpaceLogic RP-C-EXT-BL-4-HV-PD
  • SpaceLogic RP-C-EXT-BL-2-LV-PD
  • SpaceLogic RP-C-EXT-BL-SMI-4-HV-PD
  • SpaceLogic RP-C-EXT-BL-SMI-2-LV-PD
  • SpaceLogic RP-C-EXT-REL-4
  • CRS-HH-REL-10
  • RP-C-EXT-KNX
  • SpaceLogic 无线适配器 - 高级
  • RP-C-RC-BLE
  • 调试
  • Engage
  • 项目配置工具 - 版本 2
  • Automated Engineering Tool