earth_america
user_standard Accedi
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Specifiche

Specifiche


Prodotti: RP-C-EXT-BL-SMI-4-HV-PD
Funzionalità: Ingegneria, Hardware
Versione del prodotto: 2023, 2024, 7.0
13/08/2024
Clicca per visualizzare la versione aggiornata non ancora tradotta

SpaceLogic RP-C-EXT-BL-SMI-4-HV-PD

arrow1_rotationIntroduzione arrow1_rotationFunzionalità arrow1_rotationSpecifiche arrow1_rotationCollegamenti
 
action_zoom_plus_stroke RP-C-EXT-BL-SMI-4-HV-PD – Modulo oscuranti ad alta tensione SMI
Figura: RP-C-EXT-BL-SMI-4-HV-PD – Modulo oscuranti ad alta tensione SMI

Introduzione

SpaceLogic™ RP-C-EXT-BL-SMI-4-HV-PD SMI blind module connects to the SpaceLogic RP room controllers and provides I/O expansion for control of AC mains-supplied motors (drives) with SMI (Standard Motor Interface for AC applications).

The SMI blind module is an SMI certified and registered actuator (controller) that complies to SMI version 3.0. SMI 3.0 offers simplified maintenance, new functions, improved robustness, and high compatibility. The module can be used with products of SMI version 2.0 because the interface is backward compatible.

The SMI high-voltage blind module enables control and power supply (230 VAC) of motorized venetian blinds, roller shutters, awnings, and other shade products (typically for exterior use).

The SMI blind module is part of the RP controller expansion modules for connected room solution and can be combined with other modules from this product range.

Funzionalità

Il modulo oscuranti ad alta tensione SMI ha le seguenti funzionalità:

  • Alimentazione e comunicazione attraverso il room bus

  • Un canale SMI, suddiviso in quattro uscite, per il controllo SMI di oscuranti alimentati a 230 V CA (apertura, chiusura, posizionamento)

  • Quattro ingressi digitali per il collegamento di interruttori oscuranti e contatti finestra. Gli ingressi digitali sono SELV (Safety Extra-Low Voltage, bassissima tensione di sicurezza).

  • Misura del consumo energetico per modulo

  • Connettori Wieland per un'installazione semplice e veloce

  • App Mobile Engage per le impostazioni di comfort dell'ambiente

  • LED di stato per il dispositivo

  • Un LED di stato per ogni uscita oscurante

  • Interruttore girevole per configurazione indirizzo

Controllo oscurante SMI

The SMI interface has the following features:

  • Up to 16 blind motors or drives can be controlled electrically in parallel (provided the load limits are not exceeded)

  • High-precision intermediate positioning

  • Motor feedback with diagnostic information

Room bus

The RP controller room bus allows RP controller expansion modules to be connected to the controller for people counting, motion detection, luminosity and sound pressure level measurements, Bluetooth Low Energy based applications, and control of electric lights and window blinds.

The RP-C Pro and RP-C Pro Plus controller room bus supports up to nine connected RP controller expansion modules with the following restrictions:

  • Maximum of two DALI light modules

  • Maximum of two SMI blind modules

  • Maximum of seven Multi-sensor or Insight-Sensor devices

The RP-C Advanced controller room bus supports up to six connected RP controller expansion modules with the following restrictions:

  • Maximum of two DALI light modules

  • Maximum of two SMI blind modules

  • Maximum of four Multi-sensor or Insight-Sensor devices

The RP-V Advanced controller room bus supports up to four connected RP controller expansion modules with the following restrictions:

  • Maximum of one DALI light module

  • Maximum of one SMI blind module

  • Maximum of two Multi-sensor or Insight-Sensor devices

Maximum total length of the room bus is 72 m (236 ft).

Applicazione mobile Engage

The Engage mobile application enables control of room temperature, fan speed, lights, and blinds/shades directly from a smartphone. A user can manage these settings when the application is connected to the RP controller.

The Engage mobile application is free and available for download from Google Play and Apple App Store.

For more information, see the Engage Specification Sheet.

Tabella: Codici d'ordine

Prodotto

Codice d'ordine

RP-C-EXT-BL-SMI-4-HV-PD
SXWRESMI4HVPD10001
DIN-RAIL-CLIP, DIN-rail end clip
package of 25 pieces
SXWDINEND10001
Mounting plate - RP controller expansion modules
package of 5 pieces
SXWREMPK510001

Specifiche

Electrical
Nominal voltage
230 VAC
Operating voltage range
+/-10 %
Frequency
50/60 Hz
Maximum current consumption
8 A
Room bus power consumption
0.3 W (24 VDC)
Protection
Maximum 16 A external fuse (circuit breaker) is needed
Overvoltage category
III
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Humidity
20 to 90 % RH non-condensing
Pollution degree
2
Material
Plastic flame rating
UL94 V-0
Ingress protection rating
IP 20
Mechanical
Dimensions
198 W x 110 H x 64 D mm (7.8 W x 4.3 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight
0.405 kg (0.893 lb)
Recommended installation
DIN rail or flat surface in a cabinet a
Connectors
Power input: 1 x 3-pin Wieland GST15i3 connector
  
Blind outputs: 4 x 5-pin Wieland GST15i5 connector
  
Digital inputs: 4 x 2-pin Wieland GST15i2 connector
Optional mounting plate
The mounting plate is used to facilitate mounting and cable management for the RP controller expansion module as well as to provide strain relief for the connectors.
Dimensions
202 W x 268.3 H x 17.8 D mm (8.0 W x 10.6 H x 0.7 D in.)
 
action_zoom_plus_stroke
Weight
0.306 kg (0.675 lb)
Compatibility
EcoStruxure BMS server communication
EcoStruxure Building Operation
version 3.2.1 and later
Energy metering support
EcoStruxure Building Operation
version 3.3.1 and later
Agency compliances
Emission
RCM; BS/EN 61000-6-3; BS/EN IEC 63044-5-2; FCC Part 15, Sub-part B, Class B
Immunity
BS/EN 61000-6-2; BS/EN IEC 63044-5-3
Safety standards
BS/EN 60730-1; BS/EN 60730-2-11; BS/EN IEC 63044-3
Communication ports
Room bus
RS-485
  
Dual RJ45 ports for daisy-chain configurations
  
Use a Cat 5 (or higher) cable
  
Maximum total length of the room bus: 72 m (236 ft)
Room bus protection
Transient voltage suppressors on communication and power signals
Hardware
CPU type
ARM Cortex-M4 single-core
Frequency
80 MHz
SRAM (embedded)
320 KB
Flash memory (embedded)
512 KB
NOR flash memory
16 MB
Status indicator
LED (green and red) that shows the status of the device
Blind status indicator
One status LED (green) for each output
Address switch
Rotary switch 0 to 9
Set button
Push-button switch
Energy metering
Misura del consumo energetico
The energy consumption is measured in Wh, shared by the four outputs.
Accuracy class (according to IEC 61557-12)
Active energy measurement: Class 1
Typical measurement accuracy at room temperature
20 to 100 W: 5%
  
100 to 3000 W: 1%
Uscite oscuranti
SMI motor control outputs for 230 VAC powered blind motors.
Outputs
4, Blind 1 to Blind 4
Output terminals
N, PE, L, I+, and I-
SMI version
3.0
Number of SMI channels
1
Maximum total number of blind motors (drives)
16
Power distribution
230 VAC (same voltage as power supply)
  
Maximum 2 A load per output
  
Maximum 8 A total load for the 4 outputs
Digital inputs
Inputs
4, DI1 to DI4
Range
Dry contact, 0 to 5.0 VDC, 2.2 mA, SELV (Safety Extra-Low Voltage)

Collegamenti

Follow proper installation wiring diagrams and instructions. For more information on wiring, see the SpaceLogic Hardware Reference Guide.

 
action_zoom_plus_stroke RP-C-EXT-BL-SMI-4-HV-PD
Figura: RP-C-EXT-BL-SMI-4-HV-PD

Tabella: Required External Connectors

Use

Part number

Reference

Connector type

Suitable for cable diameters

mm (inches)

Marking

Color of coding

/housing

Minimum order quantity

Power supply input

SXWRPCCONWWPOW

91.931.4053.1

Female

5.6–11

(0.22–0.43)

L, PE, N

Black

/Black

100

Blind outputs

SXWRPCCONWBLSMI

91.952.4053.1

Male

8.5–12.5

(0.34–0.49)

N, PE, 1, 2, 3

1: L

2: I+

3: I-

Black

/Black

50

Digital inputs

SXWRPCCONWDI

91.921.2353.0

Female

3.4–5.5

(0.14–0.21)

1, 2

1: DI1..4

2: RET

Light blue

/White

100

The external connectors need to be ordered separately. The connectors can be ordered in quantities of 50 or 100 from Schneider Electric using the above part numbers. The connectors can also be ordered directly from Wieland using the above reference numbers. For more information, see the Wieland Electric web site.

Compatibility with the type and characteristics of the blind motors should be verified at an early stage in your project. In case of uncertainty, additional testing may be required.

  • SpaceLogic RP-C Advanced
  • SpaceLogic RP-C-EXT-MS-BLE
  • SpaceLogic RP-C-EXT-DALI-M-PD
  • SpaceLogic RP-C-EXT-0-10V-4-PD
  • SpaceLogic RP-C-EXT-BL-2-LV-PD
  • SpaceLogic RP-C-EXT-BL-4-HV-PD
  • SpaceLogic RP-C-EXT-BL-SMI-2-LV-PD
  • SpaceLogic RP-C-EXT-DALI
  • SpaceLogic RP-C-EXT-0-10V-4
  • SpaceLogic RP-C-EXT-REL-4
  • Commission
  • Engage