Specifikationer

Specifikationer


Produkter: RP-C-EXT-0-10V-4
Funktionaliteter: Maskinteknik, Maskinvara
Produktversion: 3.3
2023-08-02

RP-C-EXT-0-10V-4

arrow1_rotationIntroduction arrow1_rotationFeatures arrow1_rotationSpecifikationer arrow1_rotationConnections
 
action_zoom_plus_stroke RP-C-EXT-0-10V-4 – 0-10V light module
Figur: RP-C-EXT-0-10V-4 – 0-10V light module

Introduction

SpaceLogic* RP-C-EXT-0-10V-4 light module connects to the SpaceLogic RP room controllers and provides I/O expansion for 0-10V lighting control.

The 0-10V light module enables control of lights equipped with 0-10V ballasts.

Lighting can be controlled by the RP-C through motion detection and light intensity measurement provided by the Multi-sensor or by SpaceLogic Sensors connected to the RP-C.

The 0-10V light module is part of the RP controller expansion modules for connected room solution and can be combined with other modules from this product range.

* Formerly known as SmartX.

Features

The 0-10V light module has the following features:

  • Power and communications through the room bus

  • Four light control outputs

  • Four digital inputs for connection of light switches and window contacts. The digital inputs are SELV (Safety Extra-Low Voltage).

  • Suitable for mounting in ceilings

  • Wieland connectors for quick and easy installation

  • Engage mobile application for room comfort settings

  • Status LED for the device

  • Rotary switch for address configuration

0-10V lighting control

The analog interface has the following features:

  • Independent control of each of the four outputs.

  • The lights on each output belong to the same group and are thus controlled simultaneously (same ON / OFF / Dimming setpoint).

Room bus

The RP-C room bus allows RP controller expansion modules and multi-sensors to be connected to the controller for motion detection, luminosity measurements, communication with remote control (RP-C-RC-BLE), and control of electric lights and window blinds.

The RP-C room bus supports up to six connected RP controller expansion modules with the following restrictions:

  • Maximum of two DALI light modules

  • Maximum of two SMI blind modules

  • Maximum of four multi-sensors

Maximum total length of the room bus is 72 m (236 ft).

Engage mobile application

The Engage mobile application enables control of room temperature, fan speed, lights, and blinds/shades directly from a smartphone. A user can manage these settings when the application is connected to the RP-C controller.

The Engage mobile application is free and available for download from Google Play and Apple App Store.

For more information, see the Engage Specification Sheet.

Tabell: Part Numbers

Product

Part number

RP-C-EXT-0-10V-4
SXWRE010410001
DIN-RAIL-CLIP, DIN-rail end clip
package of 25 pieces
SXWDINEND10001

Specifikationer

Electrical
Nominal voltage
100 to 277 VAC
Operating voltage range
+/-10 %
Frequency
50/60 Hz
Power consumption
10 VA
Room bus power consumption
0.3 W (24 VDC)
Overvoltage category
III
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Humidity
20 to 90 % RH non-condensing
Pollution degree
2
Material
Plastic flame rating
UL94 V-0
Ingress protection rating
IP 20
Mechanical
Dimensions
198 W x 110 H x 64 D mm (7.8 W x 4.3 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight
0.438 kg (0.965 lb)
Installation
DIN rail or flat surface
Connectors
Power input: 1 x 3-pin Wieland GST15i3 connector
  
Light outputs: 4 x 2-pin Wieland GST15i2 connector
  
Digital inputs: 4 x 2-pin Wieland GST15i2 connector
Software compatibility
EcoStruxure Building Operation software
version 3.2 and later
Agency compliances
Emission
RCM; BS/EN 61000-6-3; BS/EN 50491-5-2; FCC Part 15, Sub-part B, Class B
Immunity
BS/EN 61000-6-2; BS/EN 50491-5-3
Safety standards
BS/EN 60730-1; BS/EN 60730-2-11; BS/EN 50491-3; UL 916 C-UL US Listed
Fire performance in air-handling spaces a
UL 2043
a) The RP-C-EXT-0-10V-4 light module is approved for plenum applications.
Communication ports
Room bus
RS-485
  
Dual RJ45 ports for daisy-chain configurations
  
Use a Cat 5 (or higher) cable
  
Maximum total length of the room bus: 72 m (236 ft)
Room bus protection
Transient voltage suppressors on communication and power signals
Hardware
CPU type
ARM Cortex-M4 single-core
Frequency
80 MHz
SRAM (embedded)
320 KB
Flash memory (embedded)
512 KB
NOR flash memory
16 MB
Status indicator
LED (green and red) that shows the status of the device
Address switch
Rotary switch 0 to 9
Set button
Push-button switch
0-10V light outputs
Outputs
4, Light 1 to Light 4
Output terminals
AOn (n: 1 to 4) and COM
Analog output voltage
0 to 10 VDC
Maximum source/sink current
10 mA per output
Digital inputs
Inputs
4, DI1 to DI4
Range
Dry contact, 0 to 5.0 VDC, 2.2 mA, SELV (Safety Extra-Low Voltage)

Connections

Follow proper installation wiring diagrams and instructions. For more information on wiring, see the SpaceLogic Hardware Reference Guide.

 
action_zoom_plus_stroke RP-C-EXT-0-10V-4
Figur: RP-C-EXT-0-10V-4

Tabell: Required External Connectors

Use

Part number

Reference

Connector type

Suitable for cable diameters

mm (inches)

Marking

Color of coding

/ housing

Minimum order quantity

Power supply input

SXWRPCCONWWPOW

91.931.4053.1

Female

5.6–11

(0.22–0.43)

L, PE, N

Black

/Black

100

Light outputs

SXWRPCCONWWLIGHT2

91.922.3353.0

Male

6–7.7

(0.24–0.30)

2, 1

2: AO1..4

1: COM

Light blue

/White

100

Digital inputs

SXWRPCCONWDI

91.921.2353.0

Female

3.4–5.5

(0.14–0.21)

1, 2

1: DI1..4

2: RET

Light blue

/White

100

The external connectors need to be ordered separately. The connectors can be ordered in quantities of 50 or 100 from Schneider Electric using the above part numbers. The connectors can also be ordered directly from Wieland using the above reference numbers. For more information, see the Wieland Electric web site.

  • RP-C
  • RP-C-EXT-MS-BLE
  • RP-C-EXT-DALI
  • RP-C-EXT-REL-4
  • RP-C-EXT-DALI-M-PD
  • RP-C-EXT-0-10 V-4-PD
  • RP-C-EXT-BL-2-LV-PD
  • RP-C-EXT-BL-4-HV-PD
  • RP-C-EXT-BL-SMI-2-LV-PD
  • RP-C-EXT-BL-SMI-4-HV-PD
  • Driftsättning
  • Engage